3/8 pex lines for tiny zones
GW
GW Posts: 5,259
I haven't done 'new work' in forever, mostly chop-swap. As recall, the 3/8 pex/plastic lines will carry a good amount, 1 gpm under normal circumstances? Up to 10000 btu if we use traditional numbers? I have a guy that want's micro-zones (yes we have a buffer tank)
Thanks for any input.
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
    edited June 26
    With 3/8" PEX, you could flow as much as 1.3gpm. At a 20°Δ, that's a max of 13,000 BTU's.
    GW
    hot_rod Posts: 28,699
    depends on the loop length.
    The PPI online calculator is good to run examples
    https://plasticpipecalculator.com/PressureDropHeadLoss.aspx
    100’ of 3/8 pex at 1 gpm
    14, head will take a high head circ
    GWGroundUp
  • GW
    GW Posts: 5,259
    Just 6600 btu on the largest zone- should be good
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    edited June 27
    i would figure .5-.75 gpm for 3/8" pex which gives you ~7000 btu/hr at 20f delta t. that is a pretty good sized radiator. if you're trying to do something low temp you might need to think about what flow you need.
    GW
  • GW
    GW Posts: 5,259
    Yes just regular temps- 180.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    50' of 3/8 with a .6 gpm flow
    edited June 28
    Sorry, this is wrong and .6 - 1.1gpm is correct. I was figuring ½” PEX.
  • GroundUp
    GroundUp Posts: 2,573
    The biggest question is why? What's stopping you from using 1/2" that's available everywhere?
    Alan (California Radiant) Forbespecmsg
  • Dave H_2
    Dave H_2 Posts: 627
    I would second this, going to 3/8" makes it harder to locate fittings, manifold connections and pipe as there are not that many manufacturers extruding 3/8".
    When I do underfloor radiant, i try to always work with 3/8" for ease of install but in tyhis case of supply/return piping to high temp radiation, 1/2" is the way to go
    Dave Holdorf
    Taco, Inc
  • GW
    GW Posts: 5,259
    Why- there were some tricky routes to weave in and out of the framing.
    The HO wanted insulation the whole route(s), and drilling holes to accommodate the OD of the armaflex. I simply wanted to keep the holes to a minimum.
    3/8 fittings availability are not an issue
    We started this job yesterday. I chickened out and went 1/2”
    Yet the sociology is evident- we all mostly oversize to avoid questions.
    I remember 20 or 25 years ago this local vendor/heating designer proposed a design to a certain homeowner. I cannot recall specifics, but the gist was there was a little remodel going on the heating area (condominium) was going to double or triple. There was an existing 5/16 inch pex line. I grabbed the 5/16 and created a little manifold and did what I’m guessing was 200 or 300 ft.² of radiant. By human standards, this should not have worked. I recall the guy waiting two or three months to pay me because he didn’t think it would work. I eventually got the check in the mail. The lesson stayed with me, the fact that BTUs can do more work than we generally think they can.
    (Those were the old days, business doesn’t work like that anymore)
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    Dave H_2PC7060
    my concern about the small tubing is more that if some sludge gets in there for some reason it may plug up.
    GW
