Steam boiler replacement
hi guys.
Quoting a steam boiler replacement I’ve measured all the radiations and determined I have 425 sq ft or steam and 426 edr. My question is that on this boiler the supply is 2” but the existing boiler currently has 2 3 1/2 supply’s. Should I be worried sizing the boiler to the radiators and leaving the current supply piping?
    pecmsg Member Posts: 7,311
    Are you a contractor or homeowner?
    Steamhead Member Posts: 18,735
    What model boiler?
    Consulting
    ethicalpaul Member Posts: 8,933
    Your question is somewhat strange to read but I'll answer it how I read it without comment as to any other concerns:
    You can use your existing 3-1/2" supply (near boiler) piping with your new boiler.
    But send some pictures of it because we like to look at pictures.
    mattmia2 Member Posts: 17,562
    each main should connect separately to the header for the new boiler. if there is a header from a previous boiler still there you need to remove it and bring the mains individually down to the new header. the connections to the header should be ordered as: all the supply risers from the boiler, all the risers to the steam mains, the equalizer. you may need to make the header a loop or rotate the boiler or other creative arangements to accomplish this.
    EBEBRATT-Ed Member Posts: 20,545
    Just follow the new boiler piping diagram in the manual and you will be fine. Larger piping than the manual shows will be no issue. Small may be a small or big problem.
    Mad Dog_2
  • KC_Jones
    KC_Jones Member Posts: 5,939
    If there really is 3 1/2" piping that will all have to come out as the fittings basically aren't available so you can't really work with it. Some boilers only list a single tapping as being needed, but have a second available if you want to use it, depends on boiler brand
    2014 Weil Mclain EG-40
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,690
    They still make Bushings to adapt to
    3 1/2" Thank God! Mad Dog
    STEAM DOCTORmattmia2
    you can even get 3.5" pvc threaded plugs(not for steam use but 3.5" stuff is out there just maybe not sitting on the shelf locally or inexpensive)
