hi guys.
Quoting a steam boiler replacement I’ve measured all the radiations and determined I have 425 sq ft or steam and 426 edr. My question is that on this boiler the supply is 2” but the existing boiler currently has 2 3 1/2 supply’s. Should I be worried sizing the boiler to the radiators and leaving the current supply piping?

Comments

  • pecmsg
    pecmsg Member Posts: 7,270

    Are you a contractor or homeowner?

  • Steamhead
    Steamhead Member Posts: 18,693

    What model boiler?

    All Steamed Up, Inc.

    Baltimore, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting

  • ethicalpaul
    ethicalpaul Member Posts: 8,928

    Your question is somewhat strange to read but I'll answer it how I read it without comment as to any other concerns:

    You can use your existing 3-1/2" supply (near boiler) piping with your new boiler.

    But send some pictures of it because we like to look at pictures.

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • mattmia2
    mattmia2 Member Posts: 17,428

    each main should connect separately to the header for the new boiler. if there is a header from a previous boiler still there you need to remove it and bring the mains individually down to the new header. the connections to the header should be ordered as: all the supply risers from the boiler, all the risers to the steam mains, the equalizer. you may need to make the header a loop or rotate the boiler or other creative arangements to accomplish this.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,465

    Just follow the new boiler piping diagram in the manual and you will be fine. Larger piping than the manual shows will be no issue. Small may be a small or big problem.