How rich is too rich
Battling the HTP phoenix lite that I've named "tuba". Foghorns like a sonofa for the first 30 seconds or so after ignition. I tried all the usual suggestions and the only thing that works is throttling a little rich. It's out of spec though. Manual calls for 8-10% for low and high fire. I keep low around 8.5 for some excess air to keep the burner cool but high is closer to 11 if I want silence. Maybe a little more. CO stays well under 60 so I don't know if I should even care as it's more efficient combustion the higher that CO2 goes. I've searched and searched and nobody ever has a real answer to all the modcons that howl besides richen it up.
Comments
-
co of 60ppm seems kinda high, you are probably on the low excess air side of the curve.
0 -
I'm not sure where you operate out of, but in New York, the Natural Gas Utilities want CO flue #s under 50 PPM as a rule. Mad Dog
0 -
-
You probably aren't confused, but I've seen it enough times to feel a need for a caution: CO and CO2 are not the same thing. And in combustion work in general, CO will increase with a richer mixture, while CO2 will increase with a leaner mixture.
Another sort of useless general comment: sometimes you can get a resonant sound — like a tuba maybe! — from unstable combustion, but other times you can get a similar sort of sound by simply varying the air flow — and it may change as less air or more flows through. This can be altered by draught, for instance. Or of course any air shutters.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
This is certainly not Too Rich
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
Only the 6" piece HTP uses inside their control panel. Completely hard piped.
0 -
I agree but also hear comments like "anything below 100 is fine". What else can I do besides have the noise? And why does it only happen for that short time at ignition? You'll find 100s of these type of threads with a quick Google search but none of them ever seem to have a detailed, proven explanation. Some say pipe, some say vent, some say regulator, but when those items are changed it never seems to solve anything.
1 -
Yes I'm on the right side 100%. I thought of that. The readings verify based on my gas adjustments. I'm between 3 and 4% O2 currently.
0 -
Just a thought — but have you tried going way lean? Just enough fuel in the air to fire up? and then adjusting back richer? Until the CO2 peaks and the CO maybe beings to show an increase?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Not sure what you mean. just to verify I'm on the right side of the curve?
0 -
I thought for a minute there you were talking about the 15+billionaires in the cargill and mcvey families😀
0 -
How many years before you can't plant corn in your garden without kicking up to them?
0 -
-
yup
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 127 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements