Steam Boiler Replacement: Don't Make These Expensive Mistakes
This weeks video talks about the common mistakes I have seen on steam boiler replacement projects. I would love to know your thoughts.
Boiler Lessons
Comments
-
-
Not a pro, but how about a comment on reusing a faulty flue without inspecting?
Trying to keep Bernie burning!
0 -
You covered all bases, Ray Ray. If you're going to overlook any of the aforementioned tasks, do not even take steam boiler replacement work. You will be doing everyone a great disservice.
Last winter we replaced two, 12 year old Weil Mc Clain LGB-8s in an historic Hudson Valley Church ⛪️. The Boilers had unnecessary F&T Traps that clogged over the years and helped cause dry-firing of both boilers, Zero Combustion Air provisions which lead to both boilers carbonizing as well.
On Top of all of this, The Church had been paying for an expensive maintenance contract but the automatic and Manual reset LWCOs were clogged and failed to prevent total boiler failures.
If you're going to tackle Steam work and want to be successful, going All-In is the only path to Victory. Mad Dog
0 -
-
@Mad Dog_2 it baffles me why we don’t more boiler accidents Lots of poorly maintained boilers
Ray Wohlfarth
Boiler Lessons1 -
They were extremely lucky and had The Lord looking over them. All the electronic controls and wiring were fried too! We make sure ALL of our boiler installations from a Small residental job on up get a Carbon Monoxide/Smoke Boiler Interlock for added safety and protection of Life and Property. Mad Dog
0 -
What did you replace them with?
Baltimore, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
One LGB -10 and One LGB-5. The Sanctuary (LGB-10) and upper level of the Church gets used only 3 hours every Sunday, so we seperated the systems and ran the first floor on its own new mains 3" and 2 1/2" and Returns. The First Floor is used 7 Days a week for Meals-on-Wheels, Bingo, Et Cetera.
We expect to see a healthy drop in fuel usage. We now have both systems humming along on 12 ounces and 8 ounces, respectively,of Steam Vapor. Mad Dog
1 -
-
-
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 125 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 121 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements