Options
arcticman
arcticman Member, Email Confirmation Posts: 35

We're researching the EK1 as an option for a new boiler.
I have an existing ~30 foot 7 inch double walled SS vertical flue with no elbows.
Can a 4 inch flue be inserted through the existing 7 inch flue and what would you recommend?
Thanks,

Comments

  • Robertw
    Robertw Member Posts: 83

    Our ek-1 frontier uses a 5 inch flue connector to the chimney. Which boiler are you thinking of useing?

    Robert W.

    Energy Kinetics

  • pecmsg
    pecmsg Member Posts: 7,124

    might as well pull a new 4” flew

  • arcticman
    arcticman Member, Email Confirmation Posts: 35
    edited April 30

    Looking at the ek-1 system 2000…. sorry I meant 5" flue.

    "

  • Robertw
    Robertw Member Posts: 83

    That will take a 5 in chimney liner and 5 in from the boiler to the liner. Use an increaser to step up from the 4 inch flue collar at the boiler to the 5 inch.

    Robert W.

    Energy Kinetics

  • HydronicMike
    HydronicMike Member Posts: 356

    You’re fine, if properly installed, emphasis on 'properly' as per the manual. Which should include cleaning the existing and a Level II inspection.