OLD (1986) 36c84-209 crossover
Mole4x4
Mole4x4 Member Posts: 2
Replacing that valve - per SupplyHouse.com they said 36c84-912 was a direct plug and play match. the 209 fires right up but only .5"wc - so weak. 912 lights pilot, but main doesn't open. Has same terminals, same 3-prong (one larger) w/ matching numbers - all looks good except mgv not opening. Bad valve? Sure wouldn't think any re-wiring should be done, but dunno.
Help is surely appreciated. And, don't have model/s# - tags are unreadable, but since 209 'works' I only need a direct plug and play match. TIA
Mike
Red Stripe Service Company
    Steamhead Member Posts: 18,553
    What pipe size? Can you see the BTUH input rating?
    Consulting
  • Mole4x4
    Just curious why you would need to know that - I can check. But, my question is: is the 912 a direct plug and play replacement as far as no different wiring needed? BTU of the 912 is correct. The main valve in the 912 not opening.
    109A_5 Member Posts: 4,122
    Looks like the 209 vs. the 912 is the pipe size.
    Is the inlet pressure good ?
    GGross
    mattmia2 Member Posts: 16,946
    need to set it up with a manometer and combustion analyzer, replacing a gas valve isn't a diy job.
    why did you replace it in the first place? if there is an inlet pressure problem it may lock out altogether.
    Jamie Hall Member Posts: 27,425
    Sounds to me like a gas pressure problem, not a valve problem.
    In case the cross-reference was wrong, this would tell us what we're looking for.
    Consulting
  • pedmec
    pedmec Member Posts: 1,410
    Sounds like you need a mercury flame sensor
    EdTheHeaterMan Member Posts: 12,336
    edited 1:43AM
    I refer you to the question I would ask the technicians that worked for me. It happens to be my signature tag line just below this comment.
    I had two customers with that gas valve / mercury flame sensor set up. I seem to remember that the three prong Mercury Flame Sensor (MFS) was something that I replaced often on both customers. It seems that the original lasted 30+ years but the replacement MFS were problematic and didn't last very long. I actually remember that one of the MFS failes within one year and the place I purchased it honored the 1 year warranty. they were affiliated with Johnstone Supply at the time so the main office had a policy for that warranty. Today that store is a mom and pop supply house because they didn't have a large enough property to provide the minimum amount of floor / warehouse space and they only had street parking. Bye Bye Johnstone. Hello American Parts co.