Insulated return
Bob_115
Bob_115 Member Posts: 52
I have hydronic baseboard on a house that has a slab floor. The return lines are inside the metal covers. I insulated the returns with foam pipe insulation thinking it would prevent condensation in my old steel boiler. Was this a bad idea?
  • GGross
    GGross Member Posts: 2,017
    insulating the returns isnt bad, but its probably not going to effect the return water temp enough to change whether you boiler condenses. what was the reurn water temp before and after insulating measured at the boiler?
    Bob_115
  • Bob_115
    The return temperature with insulated returns is 120 degrees F. Im converting to natural gas and a combi boiler so I will remove the insulation to help the new boiler to condense.
    Probably.
    This is what I am picturing in my minds eye:
    pecmsg Member Posts: 7,379
    or below.
    either way it blocks air flow!
    mattmia2Bob_115
  • ChrisJ
    ChrisJ Member Posts: 17,583
    mattmia2Bob_115ethicalpaul
    Jamie Hall Member Posts: 27,644
    Assuming that the diagram is for real, I can't think of a better way to kill the heat output of those baseboards. I wouldn't care to estimate the output loss, but I'd guess at least 75% loss.
    Yes indeed. A very bad idea…
    Bob_115
  • Bob_115
    After reading your responses I'm convinced it was a bad idea. I consider this a learning experience and I am grateful for all your input.
    ethicalpaulEdTheHeaterMan
    ethicalpaul Member Posts: 8,958
    Don't mind us, you're a good sport.
    Did you have some evidence that your boiler was condensing?
    EdTheHeaterManBob_115