Boiler sizing based on EDR
I need a new steam boiler. I calculated my current EDR as 370 without the piping pick up factor. When looking for a boiler do I just need to match the boiler steam sq. ft. output to the EDR because the boiler steam rating includes the 33% pick up factor that I did not account for? For clarity, based on the ratings for Burnham Independence boilers: the IN5I would be slightly below requirements and the IN6I would be somewhat oversized?
Comments
-
Match the boiler Square Feet rating to the EDR — don't add anything else. If the match isn't perfect (it rarely is!) better to go slightly undersized than go oversized — so in this case the IN5I would be the prper choice.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Although a Burnham IN model is possibly the worst choice amongst all the available boilers
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el3 -
Thank you. What would you recommend ethical Paul?
0 -
I hate Burnham but the "Steam Max" is their best boiler. Otherwise, Peerless or Weil McLain. Weil McLain also makes the Williamson brand. A few $$$ less same boiler.
Burnham Independence has a poor track record. You don't want that one. There are a few other decent boilers but most are "rebranded".
Burnham in particular sells a lot of boilers with different names on them but they are all Burnham. Crown, New Yorker et are Burnham clones afaik
3 -
Peerless. I like Utica fine. I’d like Weil-McLain but they say the pH shouldn’t be above 8.5 and that’s strange to me.
It makes me think they have problems with their elastomer seals that they blame on pH level. But that is conjecture and I have friends with WM who are happy with them.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Yeah. I forgot Utica/Dunkirk are fine as well.
0 -
Sounds like a good system for a WM EG40.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 119 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements