Boiler sizing based on EDR
Ldallas_87
Ldallas_87 Member Posts: 22
I need a new steam boiler. I calculated my current EDR as 370 without the piping pick up factor. When looking for a boiler do I just need to match the boiler steam sq. ft. output to the EDR because the boiler steam rating includes the 33% pick up factor that I did not account for? For clarity, based on the ratings for Burnham Independence boilers: the IN5I would be slightly below requirements and the IN6I would be somewhat oversized?
    Jamie Hall Member Posts: 27,367
    Match the boiler Square Feet rating to the EDR — don't add anything else. If the match isn't perfect (it rarely is!) better to go slightly undersized than go oversized — so in this case the IN5I would be the prper choice.
    ethicalpaulRobert_H
    ethicalpaul Member Posts: 8,786
    Although a Burnham IN model is possibly the worst choice amongst all the available boilers
    STEAM DOCTORRobert_H
  • Ldallas_87
    Thank you. What would you recommend ethical Paul?
    EBEBRATT-Ed Member Posts: 20,171
    I hate Burnham but the "Steam Max" is their best boiler. Otherwise, Peerless or Weil McLain. Weil McLain also makes the Williamson brand. A few $$$ less same boiler.
    Burnham Independence has a poor track record. You don't want that one. There are a few other decent boilers but most are "rebranded".
    Burnham in particular sells a lot of boilers with different names on them but they are all Burnham. Crown, New Yorker et are Burnham clones afaik
    Robert_H