Ignition problem
My neighbor's old gravity feed gas boiler has been running fine as long as I've known her.
A couple weeks ago the pilot went out. It would light and the boiler fire up again but go out after a minute or two (both pilot and main flames).
She has the thermocouple replaced, no improvement. Then she had the gas valve replaced with the same model (robertshaw). It worked for about 5 hours and then went out again. I dont think it's the thermostat because the pilot goes out as well.
She's had the same company (local plumbing) go out twice, each time with 2 different guys. After billing her 5 hours they can't figure it out.
Ideas? Thanks
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
Comments
-
This is natural gas supply? Was the gas valve set up for NG or propane? Did they check the gas pressure at boiler ? Static pressure? dynamic pressure? I don't see a sediment trap in that piping? I wonder if the line is obstructed?
0 -
what is the line pressure when it goes out? sounds like it might be a bad service regulator or something like that.
0 -
That is beautiful. More info please. I assume the pic is the old gas valve, pic of the new?
0 -
Boiler on a wood floor?
0 -
-
Restricted (contaminated) pilot orifice. Not enough pilot flame.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
if the pilot burner was clogged it would go out when it wasn't firing too.
0 -
Been in that spot over 100 years, imagine that.
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
I'll check it. Thanks
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
The combustion chamber is actually above that, behind the area with the central metal circle. Has always been there. Tomorrow I'll try lighting it after removing that sheet.
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
Natural. I'm assuming the techs she called knew that. Will have to find someone who can take those readings
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
Did you check the millivolts on the thermocouple with the pilot lit? did they change the pilot assembly? sounds like the pilot flame might just be barely making contact due to dirty pilot assembly.
0 -
-
I haven't. Initially I asked her to call licensed professionals since I'm not one. At this point I'll start the list in this thread the best I can.
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
let's clarify this, does the pilot stay lit with the main burner off?
0 -
It does not. When I light the pilot, the main burner turns on. While burning, the pilot goes out followed by the burner. About 2-3 minutes altogether
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
I have not. Let's say it stays on. What does that say? Low gas pressure?
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
gas supply or combustion air or maybe venting/draft
0 -
Yes low gas pressure, or maybe a more realistic scenario, the pressure drops significantly at the boiler due to a supply restriction. That's why testing not guessing usually works best.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
I'd be curious about the inlet pressure during all modes of operation and when off.
https://www.pscia.com/ASSETS/DOCUMENTS/ITEMS/EN/1-489.pdf
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
So 4 guys, 5 hours, a thermocouple and a gas valve and no pressure testing ? That seems a bit pitiful to me. Parts cannon troubleshooting fails again.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Yep. Same company that maintained the boiler in my apt building before I bought the place (It was a disaster). I give thanks for this forum everyday.
Heading over to light her pilot soon. Will report back.
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
Here are pics showing the new gas valve and pilot, which I've just lit, thermostat off. Will see if it stays lit until tomorrow
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
At less than $150 they were, relatively, cheap parts. I would have done the same. Now she has spares :).
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
that combination valve alone is around $300-$500.
unless the draft from the main burner is moving the pilot burner the issue isn't the pilot burner being dirty.
those doors being the way they were when whoever replaced the valve adjusted the combustion is important to the combustion. They affect how much primary and secondary air the burner gets.
0 -
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
0 -
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 50 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements