  • psb75
    psb75 Member Posts: 1,125

    Ah yes, variable speed salvation. I'm guessing though, that it happens all at once. But what do I know? I'm only a plumber.

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,086
    edited March 9

    Blasphemy!

    Now say 10 Hail Mary's and a good Act of Contrition then go and sin no more ✝️

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • HVACNUT
    HVACNUT Member Posts: 7,420

    I'm not religious. I just like the stories. Besides, I only know "Hail Mary, full of grace", then I'm lost. Can I do 20 of the Lord's prayer instead?

    EdTheHeaterMan
  • bburd
    bburd Member Posts: 1,297

    At the First Baptist Church in the Back Bay section of Boston, built in the 1870s, the baptismal font had a cast iron one pipe steam radiator in it. The air vent was piped up above the flood rim. Simple and effective.


    Bburd
    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,086
    edited March 9

    For Cripe's Sake! @HVACNUT

    That would be Jesus Cripe, Son of Gosh, along with Great Cesars Ghost, of the Roman Church of Holy Moley. For those that are not of this faith

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Mail4tommo
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,113

    I think normal swimming pools run at 81-82

    Mail4tommo
  • Mail4tommo
    Mail4tommo Member Posts: 55

    @EdTheHeaterMan thanks ed .

    The customer is fixed on a boiler set up. For your proposed set up which I like, is that with the boiler loop with a automatic bypass valve or primary secondary? Can you make a piping arrangement diagram? And I was thinking a tekmar 150 for controlling the pool temp. Thanks again

  • hot_rod
    hot_rod Member Posts: 27,375

    With a CI boiler you need some sort of return temperature protection if the tub is heated to say 85- 100°?

    A 3 way protection valve is ideal, or cobble together 3 ball valves and manually adjust flow.

    So you can use whatever device between the boiler and tank.

    With an indirect it may have the temperature control built in. Set it to the desired temperature wire it to TT on the boiler.

    A setpoint control like a Ranco, Johnson control, etc would allow tighter more accurate temperature control, and digital readout. Probably less $$ than a tekmar 150 and more features.

    Screenshot 2026-03-11 at 2.18.05 PM.png Screenshot 2026-03-11 at 2.21.19 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2