Ran out of oil, unable to restart with bleeding
Options
Juggatweet
Posts: 17
EK System 2000 - usually when we run out I grab 5 gallons of diesel, dump it, bleed it and it's good to go. I've done 10 gallons of diesel and bled it at least 10x still goes off as soon as it gets to ignition eact time. Do I just keep trying?
0
Comments
-
-
-
Thanks @HydronicMike I realized I was leaving the bleeder open too long, closed it timely and it started up the first time. Not running out of fuel would be a great plan, I just always forget to check it. #goals
2 -
check out the Smart Oil Gauge. Easy to install and sends alerts to your phone. We have one. It’s great. Www.smartoilgauge.com
0 -
Get an auto fill plan.