Unbalanced system or Wrong piping near boiler??
we had a new boiler replaced last year, attic this winter gets all the heat - windows need to be opened - middle floors struggle to heat- not all radiators heat evenly - Is the piping install our problem ? Multiple “specialists” have inspected and said pressure is set right, piping is correct and boiler may be undersized.
Looking From here, you got a much better than average installation. Boiler sizing is a whole 'nother question. Was the new boiler's output matched up with the connected radiator and piping load ? Mad Dog
If the boiler is possibly undersized, insulating the heck out of every steam pipe may be your salvation.
Unbalanced one pipe steam? Hardly unusual — but can be kind of fussy to fix. The balance is controlled by the radiator vents.
So. Step one — make sure all the radiator service (feed) valves are all the way open.
Now start fussing with radiator vents. Start by putting slow vents on radiators which get their spaces too warm. Don't try to speed up cold rooms at first! Slow the too warm ones down. Then as you get closer to where you want to be, adjust individual rooms — one at a time. And let things adjust for at least a few cycles of the thermostat — preferably a day or so.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England4 -
Check the gas pressure. The regulators on the gas controls, are very often set incorrectly out of the box.
And water quality water quality water quality water quality.
Insulation will only get you so far out of trouble. Borderline undersized...maybe...But the thickest insulation will not rescue a significantly undersized system. Bottom line, what does the installer say? Is he still on board or walking away? Mad Dog
What was installed for main vents?
It would be extraordinarily rare for a steam boiler to ever be undersized, not least of all because every manufacturer oversizes them vs their sq ft of steam rating by 33%
But unless we see your radiators it's all speculation. I'm curious to know what led your specialists to say it might possibly be undersized. If they were there they could measure your radiators and know rather than speculate, so I suspect they were just throwing out a guess rather than help you fix the real problem.
Follow Jamie's advice above and slow down your radiators in your hot rooms.
Did your installer skim the boiler? Does the water level in the gauge glass ever dive to the bottom during a call for heat? I do see a nice skim tapping with valve on it so it seems like they might have.
will check main vents when back home-
installer has been back multiple times and stands by the size -
Last guy here for second opinion said the boiler was cycling off due to water cut off not pressure. So that’s why he was thinking undersized…
I’ve tried turning attic radiator, that gets boiling hot, off to see if steam distributes better to other rooms on 2nd floor but not much of a difference
will try to insulate basement pipes regardless as the basement is always warm1 -
If your installer sized the boiler to the load correctly and it's tripping the LWCO it's either losing water or it's bouncing so much it trips the LWCO. The latter can be fix by a good long skim. Are you having to add water when it trips? Check for steam and or water leaks around valves and vents. How is you wet return?
Check your sight glass for water level during a burner cycle if someone is telling you the LWCO is stopping the burn. You may have much worse problems than venting, probably water quality. Did the installer skim all the oils out? Did he add anything like Steam Clean or Squick to bind to the oils and absorb them so they can be flushed out the drain?
Yeah, this is key: Was the water actually low, or was the boiler carrying over its water into the main?
I can't imagine what the boiler cycling off would have to do with being undersized unless he thinks all the water in the boiler is turning to steam and going into your system, which I will say has literally never happened in a single family residence in the history of steam heat.
Just for a rough idea, how many radiators are in your home?
It goes off and then cycles back on in 1-3 minutes - no water added - and I don’t hear the auto feeder adding water either. The sight glass never goes to empty or bounces much.
Old house and about 17 radiators total
the return was clogged last year after the new install and was fixed. I know the oil was skimmed after the install but don’t think anything else was added.No water leaks around vents
Guy who thinks it’s undersized and cycling off due to water not pressure took off a radiator vent from the attic and put a piece of toilet paper which was barley blowing he said it should be blowing a lot more than it was…
Are we talking about a cycle guard again?
Then I am skeptical of the fellow claiming it was going off on low water rather than pressure. Did he say why he thinks it is turning off because of low water? The gauge glass would have to be empty for this to be the case.
Your Cyclegard low water cutoff turns off the boiler every 15 to 20 minutes for 60-90 seconds, I wonder if he misunderstood seeing that.
That is very odd. The actual way to determine this would be to be looking at the pressure and the water level when the boiler shuts down.
If the water level is low, it is probably due to water level. (and a light would light up on the LWCO)
If the pressure is high, it is probably due to the pressuretrol cutting out on high pressure.
I wish you good luck and possibly don't call that guy back.
Low water cutoff might be defective
Do you actually see water movement in the glass, when boiler is firing. Are the valve, above and below the glass, open
Could be the ignition control.... There are lots of things that can go bad on a boiler. Brand new boilers,, do you come with defective parts, sometimes.
All true, but by far the most common defective part we see is the contractor.
Ahh the industry-standard toilet paper boiler sizing test, got it
unsure if the valve above and below sight glass is open but the water does bounce slightly up and down inside when the boiler is firing.
This is installed on the two main vents in the basement - gorton vents as pictured
While running the low water light on the cycle guard flashes on and off then the boiler shuts off for about 3 minutes - cycle guard has the low water light on now (not flashing)- then the boiler cycles back on - the sight glass through this time has about 1/3 or 1/4 water that you can still see
thanks will find someone to clean it up - can this alone be the cause of the uneven heating on the ground and second floor ?
Could you ask the installer for the details relative to the sizing. What was his total EDR for the 17 radiators in the house and what model boiler do you have?
I'd venture to guess that a single Gorton #1 per main on a system with 17 radiators might be a bit on the light side but we need details on length of mains and pipe sizes to know for sure.
The basic order of things:
- proper sizing (?)
- proper piping (good)- although you should insulate NBP and mains
- proper skimming (?) although you did say, "It goes off and then cycles back on in 1-3 minutes - no water added - and I don’t hear the auto feeder adding water either. The sight glass never goes to empty or bounces much."
- sufficient main venting (?)
- start balancing (?)