Washing machine drain solution
    mattmia2 Posts: 18,101
    you would support the cast iron stack be fore cutting it then leave the support after you're done
    hot_rod Posts: 28,346
    the trap arm is the length from the trap to where the vent takes off. Codes vary, but 5-8’ is typical length.
    In your case the is no vent before the WC connection, so when you flush the shower trap may siphon some. If so you end up with sewer gas smells.
    The vent taken off a horizontal grain line should be above the centerline if the drain, also.
    you could cut a 2” y into the shower trap arm, wet vent the washer into it. Not exactly legal but it solves two issues. It gets you a 2” washer drain and vents the shower drain.
    1-1/2” washer drains were allowed in codes for many years. If the washer discharges 9 gpm or less, they work.
    Many washers drain into laundry sinks in basements.
    But you have options to correct that rube.
  • azward
    azward Posts: 129
    This is the existing washing machine drain in the basement. The drain hose is tucked into a 2" stand pipe.
    The existing PVC pipe inside the vanity is a standard 1.5". The steel pipe that it ties to looks also like 1.5". Due to the concerns on overflow, the planned washer drain inside the vanity cannot use a standpipe. Question is how to connect the corrugated drain hose to the planned T via a control valve as you mentioned?
    Years ago, I used to manually drain the washer into the sink or bathtub each time. What I'm looking for is probably a semi permanent solution.
    i believe the manufacturer of the washer says it has to drain in to a laundry tub or standpipe, it can not directly connect to the drain pipe.
    Intplm.
  • azward
    azward Posts: 129
    edited February 8
    the wye cut into the pvc pipe.. can it be hub x spigot? So spigot end should use a fernco coupling to join to the PVC pipe?
    When the washer drain brings into the other hub, it naturally forms a wet vent for the shower drain?
    Intplm.
  • azward
    azward Posts: 129
    The next question would be how to break the siphon on the washer drain, so that the shower water is not siphoned into the washer.
    I don't understand why the air break kit could be installed there.. the water will not be pumped out of that vent?
    the siphon break is a vacuum breaker, it is a check valve that only lets air in, it doesn't let air or water out.
    azward
  • azward
    azward Posts: 129
    A relevant question is, need to drill about 1 1/2" hole through the wall. After renovation, the outer part of wall is still plaster wall, made by stacking up horizontal wood strips, with plaster spread between layers, and a plaster finish covering on the outside.
    Does anyone have experience drilling through this type of wall?
    a screwdriver and oscillating tool is probably the best way to cut through plaster on wood lath. use an old screwdriver and hammer to tap the outline of the hole you need somewhat gently and break out the plaster then use the oscillating tool to cut the lath. if you do it too violently you'll break the part of the plaster that is keyed between the lath and then the plaster will come loose. if you use a different type of saw to cut the lath it is best to cut almost all the way through one side then cut through the other side then cut the last of the first side. that keeps the saw from grabbing the lath and shaking it around when you cut the second side.
    azward
  • azward
    azward Posts: 129
    I will check if the washer already has a built-in air break, in that case I wouldn't add a second one
    A carbide or diamond hole saw works for the plaster, also for wood if you go slowly. Dirt cheap at Harbor Frieght.
    Here is an option.
    Cut a 2" combo into the shower trap arm. turn up into the wall, then about 8" above the floor a 2 X 1-1/2 san tee.
    2" facing out for the washer trap, 1-1/2" up, tie into the 1-1/2' horizontal circuit ventcircuit vent
    Technically the vertical should increase 1 size when you wet vent, but this would work fine for a washer drain.
    Now you vent your shower properly and have a 2" washer drain. Without messing with the CI soil pipe.
    It could be two stud spaces to the right, 1st pic, if that helps. Cut off the last right ell on the horizontal 1-1/2 vent couple the new pvc vent on there. Then remove piping below to the tee in the floor. A Fernco cap on the 1-1/2 where you cut it.
    Looks like that was an old tub drain and vent?
    Screenshot 2026-02-08 at 5.06.55 PM.png Screenshot 2026-02-08 at 4.49.59 PM.png
    Intplm.
  • azward
    azward Posts: 129
    edited February 9
    Yes, the end stub of the L is the original shower drain.
    Why does the number of stud spaces matter?
    Access to where the wall joins the floor might be difficult. Using a rubber hose may overcome this difficulty. Is a type a1 hose up to standards?
  • Intplm.
    Intplm. Posts: 3,151
    No…do not pipe it like that. Too much chance of drain issues with the toilet and the high velocity discharge from the washing machine.
    I believe the original post does not want to demo the new bathroom.
    The washing machine. Where is it going to be placed if not in the newly renovated bathroom? Next is where I mentioned above on where to discharge the unit. That would be the cast iron stack pictured above.
  • Grallert
    Grallert Posts: 1,192
    I can't imagine that the copper is connecting to steel. More likely threaded brass. I could be wrong
    around here there is still lots of galvanized supply around.
    Grallert
    pecmsg Posts: 7,551
    I believe the OP has already closed in the walls and floor!
    Intplm.
  • azward
    azward Posts: 129
    it's a pipe to sweat cup adapter, right?
    so threaded copper does exist. probably only in an adapter to other materials.
  • azward
    azward Posts: 129
    edited February 9
    it's planned in the bedroom right behind the wall
    there's some hope to do the cutting from the lower floor ceiling.. in that way in the bathroom i only need to open part of the USG DUROCK cement board (11 posts earlier).. but access is still challenge which is why i asked if reinforced rubber hose can be used to substitute pvc
  • Intplm.
    Rubber re-enforced hose for a sewage drain is not recommended. Only the hose supplied by the manufacturer as a drain to a properly installed house drain meant to receive the discharge of a washing machine. You seem to be looking for short cuts. There are none here. You need to do this properly.
  • Grallert
    edited February 9
    I personally have never run across threaded copper plumbing of any kind I have run across threaded brass. I misspoke when I said of any kind. Of course I've seen used and adaptors But never tees elbows nipples etc.
  • Hi @Grallert , I was just going from the somewhat fuzzy picture of the piping early in this thread, but it looks just like galvanized steel transitioning to copper via a copper female adapter, as pictured above. I've seen people do this around here, and it always either leaks or plugs up with rust. If it were exposed and accessible, maybe it could be left alone for a bit. But being inside of a wall is a guarantee of problems that will be unpleasant to fix. 😈
    Yours, Larry
  • azward
    azward Posts: 129
    considering replacing that copper adapter to an s.s. pipe to PEX adapter
    On the other end of the PEX, use sweat or press to PEX adapter.
    Would this be a good repair?
  • azward
    azward Posts: 129
    Is this type of wall, (wood lath interlaced with mud then finished with plaster on the exposing side), load bearing?
    If not structural, is it safe to open two 1 sq ft area from the other side for access to the fittings?
  • pedmec
    pedmec Posts: 1,485
    The structural is scary. That floor is gonna sag so bad. When the floor tiles start cracking and your blaming the tiles remember what they did to the framing in the floor.
    No vent for the shower. You had all that room in the ceiling below to do repipe the bathroom.
    Absolutely no inspection. Nobody would sign off on that
  • azward
    azward Posts: 129
    I believe what you said is true, now that the weight of the shower floor is supported by that compromised section of the joist. Considering to open part of the shower floor and move the shower drain to be in the same joist bay as the trap arm is ..
    is that wall load bearing? considering opening 1 sq ft for plumbing repairs. then I can add a hatch door there for future repairs
  • Larry Weingarten
    Larry Weingarten Posts: 4,194
    Hi, Lath and plaster is not load bearing. The studs and other framing have that job. Still, if there were any chance of horizontal movement (earthquake, etc) I'd be wanting to install either cross bracing or plywood on the wall to prevent future plaster damage.
    Yours, Larry
  • azward
    azward Posts: 129
    do you mean filling the 1 sq ft opening with a 2x frame like this?
  • Larry Weingarten
    Hi and no. Cross bracing would be used between studs, but is only practical to install when the wall is open, like the photo shows. 😉
    Yours, Larry
    EBEBRATT-Ed Posts: 21,026
    Cut the holes in the lath and plaster load bearing or not. Make a frame out of 2 x 4s around the cut opening with the upper and lower 2 x 4s running stud to stud
    PC7060
  • azward
    azward Posts: 129
    Oh ok. But it was closed and finished a long time ago unfortunately.
  • azward
    azward Posts: 129
    I like the idea. Yes the studs provide a natural framework for the 2x to be nailed to.
    The new frame is important if the those laths bears load to some extent. But this requires the opening to be wider than 16". I'm used to make openings that are barely large enough. For this access, a 10" opening is enough.
  • Larry Weingarten
    Hi, It would be tricky, but you could cut the 10" opening you want and then fit the horizontal cut lengths of wood in, and "toenail" them in place with screws. Same thing for the shorter vertical pieces. 🤠
    Yours, Larry
  • Intplm.
    You could put a larger access panel in too. It would make things much easier to access, Just follow the above advice that ^^^^^^ @Larry Weingarten suggests above ^^^^^^
    Larry Weingarten
  • azward
    azward Posts: 129
    can someone comment on the notches on the floor joists?
    3 notches were opened to through the steam pipe (in 1930?), the new notch was opened by a contractor to through the shower drain last year.
    is the new notch a concern? should I (open the floor, ) move the shower drain over to the left joist bay and glass the notch?
    The 2nd photo is a worse example I found on youtube where the joist was to be reinforced.
    Yeah its not very good. Your joists are cut up and notched pretty bad. The pipe crossing a joist should go through the middle but he is limited by the pitch and the height of the stack drain..
    If it was me I would get the shower drain into the same stud bay as the toilet. If you can't do that I would try and find a way down to a lower floor or basement by opening up a wall or building a chase to enclose the pipe and then sister up the old joists.
    pecmsg Posts: 7,551
    that’s completely unacceptable!
    Rip it out and do it correctly.
    full 2x6 in engineered lumber and use a hole saw to limit the damage.
    pecmsg Posts: 7,551
    what’s below that room?
    PC7060
  • ChrisJ
    ChrisJ Posts: 17,675
  • azward
    azward Posts: 129
    Its difficult to lower the steam pipe so that it travel through the middle of the joist. But the steam pipe has been there for many decades, any crook and settling has already stabilized. The shower drain is thicker so that new notch is a problem.
    a full span sister requires opening up the entire floor in the bathroom. Are there alternative repair approaches like using fiberglass?