you would support the cast iron stack be fore cutting it then leave the support after you're done
0 -
the trap arm is the length from the trap to where the vent takes off. Codes vary, but 5-8โ is typical length.
In your case the is no vent before the WC connection, so when you flush the shower trap may siphon some. If so you end up with sewer gas smells.
The vent taken off a horizontal grain line should be above the centerline if the drain, also.
you could cut a 2โ y into the shower trap arm, wet vent the washer into it. Not exactly legal but it solves two issues. It gets you a 2โ washer drain and vents the shower drain.
1-1/2โ washer drains were allowed in codes for many years. If the washer discharges 9 gpm or less, they work.
Many washers drain into laundry sinks in basements.
But you have options to correct that rube.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
This is the existing washing machine drain in the basement. The drain hose is tucked into a 2" stand pipe.
The existing PVC pipe inside the vanity is a standard 1.5". The steel pipe that it ties to looks also like 1.5". Due to the concerns on overflow, the planned washer drain inside the vanity cannot use a standpipe. Question is how to connect the corrugated drain hose to the planned T via a control valve as you mentioned?
Years ago, I used to manually drain the washer into the sink or bathtub each time. What I'm looking for is probably a semi permanent solution.
0 -
-
-
The next question would be how to break the siphon on the washer drain, so that the shower water is not siphoned into the washer.
I don't understand why the air break kit could be installed there.. the water will not be pumped out of that vent?
0 -
-
A relevant question is, need to drill about 1 1/2" hole through the wall. After renovation, the outer part of wall is still plaster wall, made by stacking up horizontal wood strips, with plaster spread between layers, and a plaster finish covering on the outside.
Does anyone have experience drilling through this type of wall?
0 -
a screwdriver and oscillating tool is probably the best way to cut through plaster on wood lath. use an old screwdriver and hammer to tap the outline of the hole you need somewhat gently and break out the plaster then use the oscillating tool to cut the lath. if you do it too violently you'll break the part of the plaster that is keyed between the lath and then the plaster will come loose. if you use a different type of saw to cut the lath it is best to cut almost all the way through one side then cut through the other side then cut the last of the first side. that keeps the saw from grabbing the lath and shaking it around when you cut the second side.
1 -
I will check if the washer already has a built-in air break, in that case I wouldn't add a second one
0 -
A carbide or diamond hole saw works for the plaster, also for wood if you go slowly. Dirt cheap at Harbor Frieght.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Here is an option.
Cut a 2" combo into the shower trap arm. turn up into the wall, then about 8" above the floor a 2 X 1-1/2 san tee.
2" facing out for the washer trap, 1-1/2" up, tie into the 1-1/2' horizontal circuit ventcircuit vent
Technically the vertical should increase 1 size when you wet vent, but this would work fine for a washer drain.
Now you vent your shower properly and have a 2" washer drain. Without messing with the CI soil pipe.
It could be two stud spaces to the right, 1st pic, if that helps. Cut off the last right ell on the horizontal 1-1/2 vent couple the new pvc vent on there. Then remove piping below to the tee in the floor. A Fernco cap on the 1-1/2 where you cut it.
Looks like that was an old tub drain and vent?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Noโฆdo not pipe it like that. Too much chance of drain issues with the toilet and the high velocity discharge from the washing machine.
I believe the original post does not want to demo the new bathroom.
The washing machine. Where is it going to be placed if not in the newly renovated bathroom? Next is where I mentioned above on where to discharge the unit. That would be the cast iron stack pictured above.
0 -
I can't imagine that the copper is connecting to steel. More likely threaded brass. I could be wrong
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
-
-
it's planned in the bedroom right behind the wall
there's some hope to do the cutting from the lower floor ceiling.. in that way in the bathroom i only need to open part of the USG DUROCK cement board (11 posts earlier).. but access is still challenge which is why i asked if reinforced rubber hose can be used to substitute pvc
0 -
-
I personally have never run across threaded copper plumbing of any kind I have run across threaded brass. I misspoke when I said of any kind. Of course I've seen used and adaptors But never tees elbows nipples etc.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
-1 -
Hi @Grallert , I was just going from the somewhat fuzzy picture of the piping early in this thread, but it looks just like galvanized steel transitioning to copper via a copper female adapter, as pictured above. I've seen people do this around here, and it always either leaks or plugs up with rust. If it were exposed and accessible, maybe it could be left alone for a bit. But being inside of a wall is a guarantee of problems that will be unpleasant to fix. ๐
Yours, Larry
0 -
considering replacing that copper adapter to an s.s. pipe to PEX adapter
On the other end of the PEX, use sweat or press to PEX adapter.
Would this be a good repair?
0 -
Is this type of wall, (wood lath interlaced with mud then finished with plaster on the exposing side), load bearing?
If not structural, is it safe to open two 1 sq ft area from the other side for access to the fittings?
0 -
The structural is scary. That floor is gonna sag so bad. When the floor tiles start cracking and your blaming the tiles remember what they did to the framing in the floor.
No vent for the shower. You had all that room in the ceiling below to do repipe the bathroom.
Absolutely no inspection. Nobody would sign off on that
0 -
I believe what you said is true, now that the weight of the shower floor is supported by that compromised section of the joist. Considering to open part of the shower floor and move the shower drain to be in the same joist bay as the trap arm is ..
is that wall load bearing? considering opening 1 sq ft for plumbing repairs. then I can add a hatch door there for future repairs
0 -
Hi, Lath and plaster is not load bearing. The studs and other framing have that job. Still, if there were any chance of horizontal movement (earthquake, etc) I'd be wanting to install either cross bracing or plywood on the wall to prevent future plaster damage.
Yours, Larry
0 -
do you mean filling the 1 sq ft opening with a 2x frame like this?
0 -
Hi and no. Cross bracing would be used between studs, but is only practical to install when the wall is open, like the photo shows. ๐
Yours, Larry
0 -
-
Oh ok. But it was closed and finished a long time ago unfortunately.
0 -
I like the idea. Yes the studs provide a natural framework for the 2x to be nailed to.
The new frame is important if the those laths bears load to some extent. But this requires the opening to be wider than 16". I'm used to make openings that are barely large enough. For this access, a 10" opening is enough.
-1 -
Hi, It would be tricky, but you could cut the 10" opening you want and then fit the horizontal cut lengths of wood in, and "toenail" them in place with screws. Same thing for the shorter vertical pieces. ๐ค
Yours, Larry
0 -
You could put a larger access panel in too. It would make things much easier to access, Just follow the above advice that ^^^^^^ @Larry Weingarten suggests above ^^^^^^
1
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements