Need advice on how to troubleshoot water hammering issue
Hi all,
So I have vertical supply pipe that runs from my basement to a second story radiator that is hammering every time the heating cycle starts going. The pipe is insulated in fiber glass in the basement, runs through my heated living room, and then into the heated bedroom above. The radiator itself has a recently new (purchased roughly a two months ago) Hoffman vent, and is pitched properly back towards the supply pipe. I'd say roughly 1/2 to 3/4 of a bubble on the level. At the end of the cycle I can sometimes here water dripping down into the supply pipe, with an audible thud.
The supply pipe in the basement obviously goes right to an elbow, and I'd say it has about less than 5' of horizontal pipe before it goes to the main supply pipe coming up from the boiler. So I'm not sure there is a lot of wiggle room to gain a lot of fall in the pipe in the basement.
Is there anything else I can do? This isn't like ting ting ting water hammer, this is like sledgehammer hitting concrete. I have listened in the basement and it is definitely isolated to this one pipe.
    Jamie Hall Posts: 27,738
    How does the supply pipe run in the second floor? Straight shot down to the basement, or is there a horizontal section in there?
  • Philip_B
    Philip_B Posts: 12
    @Jamie Hall - it's a straight shot. Radiator connects directly to the valve, and the valves on top of the vertical supply pipe. Supply pipe goes straight to to the elbow in the basement which is just above my stone foundation.
  • Grallert
    Grallert Posts: 1,184
    Is the horizontal pipe pitched correctly? Can you isolate the hammer? In the cellar? In the main?
  • Philip_B
    Philip_B Posts: 12
    @Grallert - as far as I can tell it is pitched down toward the main. There isn't a lot of run there so I'm seeing if I can lift the vertical supply any further and then put the radiator itself up on a wood platform.
    The elbow section didn't have any insulation, so I put 1" fiber glass (the proper heat rated version) around the whole thing, and I've ordered the regular white insulation sleeve to put there long-term.
    I think the hammer is right at the elbow. Because it is very audible on the 1st floor.
    ethicalpaul Posts: 8,993
    that’s where the water is collecting, cooling, then collapsing the steam that hits it at the next call for heat, then gets slung against the pipe.
    I had that and had to repipe it
  • Philip_B
    Philip_B Posts: 12
    @ethicalpaul - I think some repipping and potentially a boiler replacement is in my future, because the unit definitely wasn't taken care of properly before I got the house. There is also quite a bit of copper between the boiler and the mains, so it looks like it got jerry-rigged too.
    That being said, I've put new Hoffman 40 vents on all of the rads, replaced the auto water-feeder, and will replace the vents on the mains when its more conducive for me cutting them out (they're stuck beyond convincing, so I'm waiting for it to be less cold).
  • Philip_B
    Philip_B Posts: 12
    So today I uncoupled the rad on the second floor, repositioned it a little bit, and exchanged the newish Hoffman 40 for one of the old Hoffman 1A's that was still reasonably in working shape when I changed them out in September. I set it to 6. So far no hammering. Will update everyone about if the "fix" continues to work or not. Not really sure why swapping out the vents and going backwards would make a difference, but I did it just because I had tried everything else.
  • Philip_B
    Philip_B Posts: 12
    Welp, sadly the vent "fix" was not a fix. The hammering was back within a few hours. So probably the only reason it didn't hammer for a bit was that I rested the system for longer and the water had more time to work itself out.
    I can hear a lot of dripping coming from the second floor at the end of the cycle though. I've checked and rechecked the knuckle on the valve, and the radiator is pitched at roughly 1/2" fall from end to end towards the valve.
    Anyone have any other ideas other than repiping the thing down the road?
    edited February 4
    You can try to lift the radiator a little at a time (like 1/4" to 1/2") to try to "undo" the likely settling that caused the water trap to form.
    Gently but firmly pry it higher with a 2x4 on a fulcrum then put shims under the feet. Lift it equally on both sides, the pitch of the radiator doesn't do anything. Try to lift it a little more every few days or so. You can only lift so much though before something won't let you lift more.
    I have had some success with this…it went from banging to more like gurgling (before I completely repiped it).
  • Philip_B
    Philip_B Posts: 12
    @ethicalpaul - thanks Paul. I tried to raise the main pipe by itself the other day, after disconnecting it from the rad. It doesn't want to budge much at all. But its also on a pretty short run in the basement. Not a lot of flex unfortunately.
    I can't tell for sure from the pictures, but I'm not thinking it's the main that has to be lifted, but rather part of the "runout" (the supply pipe to the radiator that branches off of the main) that had the settled part in it
    And I can sympathize about lack of flex. We hear about "swing joints" but after a decade or ten they get rather unswingable.
    Here is my old discussion where I had what I think is a very similar issue. You might find useful stuff in there:
    delcrossv
  • delcrossv
    delcrossv Posts: 2,204
    "I can't tell for sure from the pictures, but I'm not thinking it's the main that has to be lifted, but rather part of the "runout" (the supply pipe to the radiator that branches off of the main) that had the settled part in it"
    This. it's in the takeoff.
    Also I might have misunderstood your use of "main pipe". Don't disconnect the radiator, use a lever under the radiator to raise it and its supply pipe. If you disconnect the radiator, you will have nothing to hold onto.