Two-Pipe Steam System – Boiler Locks Out on LWCO, Requires Power Reset (Mostly Mornings)
We are working on a residential two-pipe steam system and are looking for input from experienced steam professionals.
Reported Symptom
The boiler intermittently shuts down and requires the homeowner to cycle power to restore operation. This happens most often in the morning on the first call for heat.
Findings During First Service Visit
Initial Condition
- Boiler was found shut down on the Low Water Cutoff (LWCO).
- Water in the sight glass appeared relatively clean at arrival.
Control Settings Observed
- Vaporstat set at approximately 12 oz cut-out with a 6 oz differential
- Secondary pressure control (Pressuretrol) set around 0.5 PSI
Initial Actions
- Boiler was filled to the proper operating water level and restarted.
- Noted minor surging while firing.
Drainage and Flushing
- Drained the boiler from the lowest boiler drain and from the wet return hose connection.
- Discharge water was extremely dirty, indicating heavy sediment/sludge in the boiler and/or return piping.
- Performed multiple fill-and-flush cycles to remove as much debris as possible.
Operational Behavior Observed After Flushing
While monitoring the boiler in operation:
- During firing, the water level in the sight glass slowly dropped below the normal operating range, repeatedly tripping the LWCO.
- The automatic water feeder added water multiple times during this period.
- After shutting the boiler off and allowing the system to sit, the water level rose back up, at times above the normal fill line.
- This strongly suggests condensate is slow to return while firing, then returns after burner shutdown.
Return Piping Inspection
- Visible return piping near the boiler appeared properly pitched with no obvious sags.
- Access to the wet return is extremely limited due to tight spacing between the brick wall, boiler, and domestic hot water tank, making inspection, cleaning, or replacement difficult without disassembly.
Current Assessment
The observed behavior:
- Falling waterline during firing
- LWCO activation and feeder operation
- Waterline recovery and rise after shutdown
is consistent with delayed condensate return, most commonly caused by a restricted wet return due to sludge and debris.
While failed radiator traps or crossover devices allowing steam into the returns could contribute, the large volume of debris observed during draining, combined with the fact that the system reportedly operated normally for many years and the problem started recently, points to the wet return as the primary suspect.
Next Step and Question
We are scheduled to return to open and clean the wet return piping.
If cleaning or replacing the wet return does not resolve the issue, what other causes should we be focusing on?
- Traps?
- Boiler piping issues?
- Control interaction (LWCO, feeder, vaporstat)?
- Other less obvious two-pipe steam system faults?
Any guidance from those with deep two-pipe steam experience would be appreciated.
Comments
-
Note: All radiators in the home are heating properly except for one. The most likely cause is a closed or partially closed supply valve. Access to the valve requires opening the wall to confirm its position and operation.
0 -
If the wet return isn't the problem… I'd be kind of surprised.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
There's a chance it is pushing water out the back as pressure increases but it's impossible to say from here
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Could be a partially plugged wet return, especially if everything except 1 radiator is heating. I am assuming no water hammer.
What pressure is the boiler running at if any?
Does the LWCO trip and the water level drop soon after starting to steam? Or does the water level stay fairly normal and drop after the boiler has run a decent cycle
0 -
- There shouldnt be a mud loop on a 2 pipe boiler, but mud loops usually keep the wet return from getting jammed up. Where is that mud loop tied in?
- Disconnect mud loop wiring and lock it up, see if the boiler does the same thing on first fire.
0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements




