Flues or chimneys need to be heated to vent?

Options
captainco
captainco Member Posts: 854

I am constantly reading posts and comments about how flues need to be heated before they will vent. I have looked everywhere for charts on what temperature different type of flue needs to vent. I have checked B-Vent specifications and not one of them list the temperature they need before they vent. Does anyone know where to find such a chart? Could this just be BS because they don't know how venting works?

ethicalpaul

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 27,600

    What what? Where on earth are you finding that notion?

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ethicalpaul
  • HydronicMike
    HydronicMike Member Posts: 381

    I think it goes back to old time thinking when people would light those huge fireplaces, first with some paper to 'heat up the chimney'.
    But I've never heard anything about heating up flues for them to work. If anything, clean an oil fired piece of equipment in the dead of winter on a service call that's been sitting for hours, and as your brushing the thimble, soot is being sucked up the chimney.

  • winnie
    winnie Member Posts: 73

    The 'stack effect' is the natural effect of warm buoyant air in a flue rising, essentially creating a draft. The warmer the chimney is the greater the 'stack effect'.

    What I don't know, and what is really needed to help answer the original question: how much stack effect is necessary to support the function of any particular combustion device. I am certain that some combustion devices require some stack effect to function properly, but I can't give any specifics :)

  • pecmsg
    pecmsg Member Posts: 7,312

    that flue “Should” always be warmer and exhausting building air.

    EdTheHeaterMan
  • ChrisJ
    ChrisJ Member Posts: 17,534
    edited January 27

    My understanding is sometimes when lighting a fire in a cold building, you might want to establish draft by lighting a small fire first to limit the amount of smoke you end up with leaking inside etc. If the inside of the building is the same as the temperature outside, there won't be much going on.

    I just asked my dad, and he said years ago he'd go up to his cabin and often it was actually colder inside than outside and he'd light a small fire in the elbow of the stove (6" flue out the back into a 90 and up) to get a draft going first. He said there were a few times it was below 0F inside when he got there.

    But I don't know whether or not the temperature of the pipe really mattered. Not really my wheelhouse.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • hot_rod
    hot_rod Member Posts: 27,904

    I think this is more of a fireplace flue question.

    I remember the ball of newspaper trick in the home where I grew up. It worked for the 18 years I lived there.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    ethicalpaulEdTheHeaterMan
  • Jamie Hall
    Jamie Hall Member Posts: 27,600

    Ah. Fair enough. A dead cold flue in an environment which is colder may not draught — at first — and the assorted tricks mentioned can be used. But even slightly warmer air going up will keep it going — and it's not the temperature of the flue which matters, but the slightly warmer air being buoyant. It's perhaps helpful to note as well that with some chimneys the wind can be a factor in getting a cold flue to draw. Not much if the thing is done properly — far enough away from things that are higher.

    Once any kind of heat is going up the flue, it should be fine — unless it is wildly oversized.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ChrisJ
  • mattmia2
    mattmia2 Member Posts: 17,564

    what about undersized? why does the code say in certain combinations of common venting you have to upsize the vent after it leaves the appliance?

  • captainco
    captainco Member Posts: 854

    If I heard it once I have heard it a thousand times, "If your flue is too big you won't be able to heat it".

    You might find a recently posted video that states flue gas will spill out of a barometric if the flue isn't warm.

    If a boiler is vented into a flue why would the flue not be warm?

    Outdoors doesn't need to be pre-heated for a campfire to vent.

    Hot air doesn't rise, it gets displaced by cold air.

    Pressure difference determines which way air goes in a flue also. Fortunately temperature difference is great enough most of the time to overcome negative building pressure. But why does Code require us to make mechanical rooms negative?

  • ethicalpaul
    ethicalpaul Member Posts: 8,933

    Hot air doesn't rise, it gets displaced by cold air.

    it gets displaced as it rises, yes

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • jesmed1
    jesmed1 Member Posts: 1,487
    edited January 27

    I can attest to what NOT having a vertical flue/stack effect does.

    I installed a Jotul direct vent gas stove in our sun porch several years ago. The vent pipe is a short double-walled horizontal run only about 18" long, with a horizontal termination cap. Both exhaust and intake air, coaxial.

    Jotul specifies a very small rise/run, like 1/4" rise in 12" run, meaning there's almost no buoyancy effect to the force the exhaust gases through the vent. (They do rise up inside the stove from the burner to the vent pipe at the rear of the stove, but the rise inside is maybe 1 foot at most).

    The result is the flame is very sensitive to wind direction. If the wind is from the back of the house blowing the horizontal exhaust backwards, even just a few mph, it will blow the flame and the pilot out. I think it's because there's no buoyancy effect of a large slug of hot exhaust gas moving vertically up a flue and providing some resistance to opposing pressure/wind forces. I've considered adding an elbow and a short vertical extension to induce that stack effect and thereby make the flame less sensitive to wind direction, but it's not high on my priority list.

    As others have mentioned, when you grow up lighting fires in a wood-burning fireplace or stove, you quickly learn the difference between a cold flue pipe and a hot one. A cold flue pipe or chimney can get you a faceful of smoke from a wind-induced downdraft before there's enough hot gas inside the flue to establish a steady upward flow.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,536

    Semantics: Isn't cold just the absence of heat, isn't dark just the absence of light, isn't evil just the absence of good.

    I think that the hot air rises and is replaced by cold air

    You say that cold air displaces the hot air.

    I think Sandra Bullock is hot. You might think that Julia Roberst is a Pretty Women, I had a friend that was a Marlyn Monroe fan.  None of them have anything on @Erin Holohan Haskell     That might be off topic. Oops Sorry!

    The net outcome is that if the air in the vertical vent pipe is lighter than the air surrounding the vertical vent,  then you should have no problem getting the smoke out.  

    Where you run into problems is when other factors like a building with an extreme negative pressure, or a tree grown above the top of the vent exit, or there are hills or buildings that cause the wind from a certain direction to act as an air scoop make downdraft problems, you need to address those problems in some fashion or another.  

    I think that @Bob Harper should comment herein.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Jamie Hall
    Jamie Hall Member Posts: 27,600

    Mechanical room negative pressure is to try to keep fumes out of the rest of the building…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • PDTech
    PDTech Member Posts: 19

    I believe the Venturi effect or Bernoulli’s theorem is part of the equation, too.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,548

    Usually, no matter how cold it is out it is warmer inside the building, so most chimneys don't need much help to get going.

    ethicalpaul
  • Bob Harper
    Bob Harper Member Posts: 1,180

    Jim and I have gone rounds over this one. Start with the campfire/ candle scenario: it is surrounded by relatively cool, homogenous air. You introduce a flame, which reduces the density of the flue gases relative to the surrounding air, this the flue gases rise as they are being displaced by the colder, denser air. Out in the open, it has to go somewhere so it fights and forces itself upwards against gravity and the falling cool air. This, combined with the Coriolis Effect, cause the characteristic helical flame/ smoke pattern. Being exposed to the cooler air, this column quickly cools to the surrounding equilibrium instead of rising to space so it diffuses out.

    Now, slide a conduit over that flame leaving both ends open. The conduit is full of cold, dense air that cannot be pushed aside as it was unrestricted. Therefore, it takes the path of least resistance. If it has sufficient energy, defined as the difference in air density vs. flue gas density, the flue gases may be able to force that column of cold dense air up and out similar to a push-pop or a piston. However, if there is sufficient relief and a lower pressure gradient in the CAZ, it will backdraft. Most CAT I appliances do this at startup. ANSI allows this nonsense to go on for 10 minutes. That's because when it was written houses still leaked like a sieve. It didn't matter. Now we live in Tupperware.

    If the walls of the conduit are cold relative to the flue gas column, they will naturally absorb BTU's until they both are at equilibrium all the way to the outer wall of the flue liner. If this liner is terra cotta properly installed, you have about 1" of clay to heat. If it's mortared in as most masons from the old country did it, the heat continues on all the way through the mass of masonry until it either reaches a capillary break or the outer wall. This is why skinny chimneys heat up more quickly than huge, high mass chimneys. It also explains why high mass chimneys that are kept hot all season rarely suffer chimney fires while the skinny ones burned for short periods do gunk up with creosote (wood) or acidic condensate with gas or oil, and rot. A hot flue is a happy flue.

    If BTU's are being robbed to heat the walls of the flue liner, less heat is available to reduce the flue gas density, thus it hinders creating draft pressure. Thin-walled, low mass metallic liners heat up very quickly, thus leaving those BTU's to generate the requisite draft pressure differential to get mass flow, popularly erroneously referred to as "draft". Draft is pressure- not flow. So, how does this factor into Jim's question? For me, it seemed quite obvious he was dead wrong from all the above: you MUST heat the flue liner walls and cold flue air at standby before mass flow upwards can begin. Binary thinking. As I got into things, I discovered impossible situations.

    For instance, I had a gas direct vent where the concentric fresh air intake had been 100% blocked for two years yet the appliance periodically ran fine. As crazy as it sounds, this unit forced itself to pull sufficient air down the exhaust flue passing the flue gases going the other way. It set up a two way stream. This is what happens in larger flues or the outdoors. A small, tight column of helical flue gases will fight its way up past the falling cold air. If firing is sustained, more heat is transfered to the flue liner thus leaving more heat for draft pressure until virtually all the air in the stack becomes flue gases.

    Except, on cold exterior stacks, you get a permanent downward flow of air hugging the flue liner walls. This happens in hot air balloons and exterior walls in heated buildings. This happens in large smoke stacks. Despite years of seeing non-stop gazillion BTU's of input, the walls only get just so hot. That boundary layer creates an airwash of cooling air that simply cannot be fully overcome. The high thermal mass, usually 3 wythes thick at the upper reaches, does store heat but only enough to stabilize the draft during high winds, cold weather, rain, etc. Rain is another problem altogether cooling the walls and flue gases unless there is a rain cap.


    On small venting systems, such as residential, I think the phenomenon of a cold backdraft from a large stack can be significant. However, as you approach the 10" or so/ 1 million BTU club, the two-way phenomenon is definitely real. To be sure, I see MOST residential flues cold backdraft, which is partially solved by a properly sized low mass metallic liner. The other part of the equation is CAZ depressurization, which is a whole another discussion. On most 4 story apartment buildings and similar commercial stacks, I find a positive flow at standby. This, I think is partially due to how much heat is being lost up the stack from these old inefficient boilers and partially by the length of firing cycles with extended wet times in between. It's a weird juxtaposition between dewpoint and minimum draft pressure for positive flow versus stack losses and firing cycles.

    I have seen more flow reversals and backdrafting in residential applications with oversized flues, but again, those also typically have negative pressure regimes and cold exterior chimneys serving orphaned water heaters. The ~10 MBH stack losses on a 40 MBH DHW heater into a cold, wet 2 story masonry chimney with a 3" vent connector will backdraft for most, if not all of its firing cycle. A ranch house with a nominal 8"x8" flue also struggles to develop sufficient lift. Here, the larger flue, ONCE HEATED, generates more lift than a smaller volume flue. Think of flues as hot air balloons. The bigger the greater lift- once the whole balloon is full of hot air. BTW, air inside hot air balloons slides down the walls of the balloon and out as ambient air is entrained up into the bag, similar to our discussion.

    Now, can you take a commercial building with a 16" square ID TC flue that once served a couple million BTU's firing almost constantly then expect it to behave predictably when you replace those old inefficient boilers with much higher efficiencies firing at markedly reduced input rates? You might get it to work but you will still have to contend with firing cycles, negative CAZ pressures and condensation.

    See attached DV handbook for fun.

    Howzat Jim?

    There was an error displaying this embed.
    ChrisJHydronicMikebburdSuperTech
  • Jamie Hall
    Jamie Hall Member Posts: 27,600

    Fun trivia (and thank, @Bob Harper , for that excellent discussion!). Some —perhaps many — older houses and other buildings had flues which were much too big, and had that updraught/downdraught conflict going on. With inevitably smoke (we're looking at fireplaces here). One of the more interesting variations which created the remarkably good fireplaces was the development of a smoke shelf in the chimney flue, at the back of the flue, This redirects the hot gas flow up the front of the flue, and there will be a corresponding downflow at the back. The result is a flue which is easy to start, but which is remarkably resistant to backdraughts and which does not use as much room air as a simple straight flue would. Quite an improvement!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • captainco
    captainco Member Posts: 854

    Why do flues in the summer on a water heater have a lower draft?

    Are flues heat exchangers that are supposed to cool the flue gases down?

    Why were the flue venting tables produced by a computer and not field testing?

    If you put some oil in the bottom of a glass does it rise or get displaced when adding water?

    Do Flue Liners increase flue temperatures avoided condensation?

    Why do the GAMA/AGA state they cannot be used in windy conditions?

    What flue material keeps the flue gases the hottest and not absorb excess heat?

    When venting into a chimney, we want the flue temperature to stay hot until the exit.

  • SlamDunk
    SlamDunk Member Posts: 1,824

    when my dad had to fire an old Federal boiler in Manhattan, which was used as a back up if the main boiler was out of service, he would go to the basement, get a ladder, open a steel door, fill the opening with broken pallets and cardboard and light it on fire. That hole was a horizontal portion of the brick chimney. He had to warm the brick so the chimney would draft. The boiler burned No. 6 oil. There were no charts, just hand me down knowledge and the experience of not warming the chimney.

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,536

    Why do flues in the summer on a water heater have a lower draft? Because I said So!

    Are flues heat exchangers that are supposed to cool the flue gases down? Maybe

    Why were the flue venting tables produced by a computer and not field testing? Laziness

    If you put some oil in the bottom of a glass does it rise or get displaced when adding water? YES

    Do Flue Liners increase flue temperatures avoided condensation? No, Flames increase flue temperatures. Anything after that will cool flue temperatures. DAH!

    Why do the GAMA/AGA state they cannot be used in windy conditions? Nobody knows

    What flue material keeps the flue gases the hottest and not absorb excess heat? Good Question!

    When venting into a chimney, we want the flue temperature to stay hot until the exit. Agree!

    I hope this makes the whole subject clear as mud!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Larry Weingarten
  • captainco
    captainco Member Posts: 854

    Thanks Ed, I am impressed by your response.

    Aluminum flue material cools flue gases more than any material and cause condensation. (B-vent and liners)

    Water heaters have warmer flues in the summer but lower draftl Draft is created by the temperature difference of the outside air and the flue gas. The temperature of the flue can only disrupt this as it gets warmer.

    Why does a 30 foot tall flue have a higher draft than a 10 foot flue? It can't be because the flue is warmer!

    Does anyone know what installation recommendations have ever been field tested for variable conditions?

    If a furnace or boiler are vented into a 6" flue or a 7" flue, which one stays the hottest? Unless a flue is falling apart a liner is a waste of money but I guess if it generates more income it is okay.n.

    The biggest cause of flues not venting is combustion air being stubborn

  • Jack
    Jack Member Posts: 1,059

    The best natural flue designs are those which can help establish draft quickly, limiting the “wet time” of operation of the flue/appliance. On cold starts all appliances will condense. The trick is to use materials which will heat and dry quickly which will allow the appliance to establish proper draft conditions. That material is never masonry. Masonry never looses its appetite for a btu. Sizing is critical. Take a 4” breech of 12.5 sq in. Throw it into a 6” (28.26 sq in) or 8” (50 sq in) chimney and that nice concentrated pile of btu in the 4” hits that cold mass of stacked air and it just goes ”proof” as it diffuses into the larger space attempting to get the draft moving. Compounding that is inadequate CA.

    The gas codes changed in ’92.You could cover up a lot of design deficiencies with a high stack temp on a 6o-65% appliance but with the high stack temp but at a minimum 78% all hell was breaking loose. We trained using that wet time concept. I think App E was added to 31 in about ‘00. It was stuffed into an appendix due to the cost of relining. The physics and testing were done at Brookhaven, but his was a cost issue, gas/oil.

  • Bob Harper
    Bob Harper Member Posts: 1,180

    GAMA and the AGA got together through the Gas Research Institute or GRI to sponsor the testing at Battelle Labs for venting tables in 1990. Early on they realized the variables were too many for any modicum of repeatability with cold exterior chimneys. Thus, all the venting tables in the codes are for INTERIOR chimneys only. The code directs you to engineering methods, meaning freestyle. They ran a few interations then used VENT II computer modeling to compile a stack of empirical calculations that are taken as gospel down to the BTU. Note these calculations are based upon a very rigid set of parameters. For one, they do not account for flow restriction and disruptions as found in the real world. They do not take into account various materials used for connectors such as stainless steel, heavier gauges than called for, etc. Note that ss L vent robs less heat from the stack than B-vent with its aluminum liner hence higher stack temps. SS is lousy and unpredictable at heat transfer. Another example would be using 22 ga. 'stovepipe' instead of 26ga. The wall thickness of 22ga. is 0.0299 inches vs. 0.018 or 40% thicker. That higher mass, once heated, holds stack temps much better than the beer can connector. Ok, I know you're dying to know: a beer can is 0.009" thick or about 30 ga..

    A lone CAT I water heater in summer will backdraft virtually 100% of the time.

    A larger diameter flue is harder to get primed as I've noted but once you can get it moving upwards and warmed up, the larger volume creates more lift than a smaller stack. When you use atmospheric injection, the total volume of gases entrained is often much more than the total actual flue gases. Add that dilution air to the stack gases and a larger stack moves more mass than a smaller stack. Therefore, due to Bernoulli, anybody standing around in the combustion chamber is more likely to get sucked up into the stack compared to a smaller conduit that barely has just enough volume. Think of a meeting hall or gymnasium packed full of people trying to exit through one door. Most people are standing to the sides not moving. Now, open both doors wide open and there is the rush where everyone gets swept up into the flow. Its analogous to the appliance collector box at the vent collar. Now, add some people entering from side hallways (draft hood) and you see how disruptive it can be. Now, if everyone is running down the hall too fast but someone opens a side door and lets some people enter from the side, that tends to slow things down a bit until it drops to a safer speed then the side door (barometric damper) closes.

    Yes, a heat exchanger reduces stack temps. as does the venting system. We want heat transferred in the unit but not the stack so use a chimney liner material that tends to not absorb heat. For years chimney liner companies harped using insulation around metallic liners to reduce condensation and maintain stack temps. Dead air does this better so a liner not touching the surrounding mass of masonry with the concentric space plugged top and bottom forms a Dewars Flask or thermos bottle effect. If you are going to backfill with insulation, you want a material with a very low k (thermal conductivity) factor of about 0.458 or R=1.09.

    While everyone is hung up on 'draft', as the term is mis-used, why don't they put more into understanding flow restrictions and design better venting configurations? Air Heads live and breathe duct work performance. The principles are the same. A hard 90 from a tee is very distruptive compared to a broad radius ell compared to stacking two lesser ells. Of interest, there is the dichotomy between vent rise vs. static pressure/ flow resistance. For instance, if you come right off the top with a 45 ell over then return 45 into the chimney, there is less penalty compared to rising up to a 90 then over….except, you kill the stack velocity with the ell off the top. It is generally better to get a head of steam up so to speak before encountering offsets. Put that ell as high up as you can and you'll get less spillage. Also, NEVER use 3" connector on a 40MBH water heater- ever. The mfrs. now swage a 4" adapter on the draft hood so just use it. You'll save lives. FYI, those vent tables start with a 1 foot vent rise before any offsets yet 99% of the water heaters I find start that that damned 3" 90 right on top….rarely with any screws attaching it btw. Note, min. 3 screws per joint equidistantly spaced and preferably none btw 5-7 O'clock on horizontal runs nor any seams in this zone. On larger pipe, put a screw in about every 7-8" of pipe circumference. Just spread your fingers out and measure thumb to pinky. You have a built-in screw spacer gauge. Support your vent connectors about every 6 lineal feet and in two planes at each offset/ return. Vent connector failures are a major source of CO exposure.

    Wear a personal CO alarm.

    HydronicMike