Steam and bubbling water coming out the main vent
We have a 1920s vapor system on a gas boiler.
Vaporstat and a Pressuretrol that is supposed to be a backup.
Was getting really loud hammering and loads of steam and bubbling water coming out the sole main vent. (2700 sq ft four square style home).
The expert we use is backed up due to the weather. Only 3 radiators have conventional traps, the rest are original water traps. Almost all.but maybe a ceiling radiator in the basement have orifice plates. I thought steam must be going straight thru a radiator or two to get steam out the vent so I made sure all un-trapped rads had orifice plates. I closed the suspect ceiling rad.
My pressure gauges read 0.
Next I took off the gauges and controllers and cleaned the pipes. Couldn't get the pigtail off (and didn't have a spar) but I cleaned with a wire at least to where it goes horizontal and poured water in and it drained.
Reassembled with tephlon and Oatey white dope.
Now the gauges show pressure.
Pressure is going up past 35 oz/in2. The other gauge shows 3 psi.
Still banging, venting steam and bubbling.
Positive note, the gauge shows 1 psi vacuum when the boiler is off.
Suggestions?
Maybe I put too much dope and obstructed the vaporstat?
Comments
-
Possibly. That vapourstat should shut off at 5 ounces, and they are pretty reliable.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Vaporstat was not obstructed. Pressuretrol wasn't either. Pressure gauges were bouncing.
The steel pigtail broke off with a little tapping and a little torque.
Now what?
Best methods for getting that out?
Drain first, penetrating oil or no?
Utica boiler PEG262CDE from 2006
0 -
-
-
Too bad I didn't see this until the morning.
0 -
New pigtail is on, had to add a nipple which made the wiring a harder fit.
Boiler is back to boiling.
System is a 1920s vapor system with mostly original water "traps" (which are really more of a vacuum holder for the condensate line)Still getting lots of steam coming out of the main vent.
System is still in the process getting the house back up to temp so cycling constantly.
I have no one to run this by so hopefully The Wall can give me some feed back.Questions:
The Vaporstat is designed to break the connection between the Line and the Load when the pressure reaches the Main setting. (in this case about 4 OZs/IN2) - Correct?
The Pressuretrol (PA404A Additive Diff) is also designed to break the connection between Line and Load when pressure reaches the setting (set near 0.5 PSI). - Correct?There is a remote temp sensor installed on the main line out near the main vent (about as far from the boiler as possible) that is supposed to allow the boiler to continue to fire until the main gets to a certain temperature where the sensor is installed (to reduce short cycling).
That should mean the temp sensor is Making the connection until the desired temp is reached, then Breaks the connection to allow the Vaporstat to manage the boiler. - Sound right?Boiler is shutting off at what could be 45-50 OZs/IN2 on the small gauge and about 3 PSI on the big "useless" gauge. Seems to be in the ballpark of 16oz per PSI.
Question is: what device is cutting off the load at this point and why is the Vaporstat not keeping the pressure at 4 OZ?Does it make sense that the remote temp sensor has failed and is not "Breaking" the connection when temp is achieved? Thereby continuing to over-ride the Vaporstat until the Presuretrol takes over?
Photos
Line is connected to Vaporstat "R" terminal
Load is connected to Pressuretrol "Left" terminal (I can't find a diagram or label for the Pressuretrol terminals)
Remote Temp Sensor is connected to Vaporstat "R" terminal - therefore getting Line current. and also connected to Vaporstat "B" terminal (if sensor failed in a closed position - transferring Line to "B" terminal constantly)
Vaporstat and Pressuretrol are connected by a double/joined black/red wire (twisted together) from Vaporstat "B" to Pressuretrol "Right" terminal.
If Remote Temp Sensor has failed in a closed position - Line power is then being transferred from Vaporstat "B" to Pressuretrol "Right" terminal. (if failed is closed - which seems odd but possible)I disconnected the Remote Temp Sensor.
Boiler is cycling on and off when pressure reaches 45-50 OZs/IN2.
Seems like the Vaporstat is not working and boiler is being governed by the Pressuretrol - Sound right?I am still getting steam coming out of the main (only) vent.
How is steam getting to that vent? The vent is only connected to the Condensate return.
Does this mean that steam is passing completely through one or more radiators and entering the Condensate line? Seems like the only way.0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.8K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements