System 2000 and EK1 - Oil or do Propane Conversion?
Hi All,
I am trying to decide if and how I should upgrade our boiler system.
Background: 7 months ago we moved into a 26 year old house in Connecticut with the original Weil Mclain Gold Oil cast iron boiler and two 275 gallon oil tanks. 5000 sq ft house with 4200 sq ft space heated by a hydro air system made of the boiler with two air handlers (1 in basement for 1st floor and 1 in attic for 2nd floor). Hot water is indirect heater (HTP SSU-45N) installed in 2020. So 3 total boiler zones. The rest of the house square footage is a finished basement heated via heat pump/minisplits.
We also have a buried 500 gallon propane tank piped to the house that serves a whole house Generac, cooktop, and fireplace.
Since moving in, we have already done an energy audit, which resulted in air sealing the attic, aerosealing the air handler ductwork, and adding blown in cellulose to the attic over the original insulation batts. I feel like we have already maxed out available energy efficiency gains.
I suspect that we will use between 1,200 - 1,500 gallons of oil per year in the current setup depending on weather. The oil company that has previously serviced this house estimated 1,600 gallons but that was before energy improvements and I also think the previous owner just kept the thermostats set higher than we do.
We plan to be in the house 20-30 years, so I am considering updating the system now to capture efficiency gains that will pay us back over the years instead of paying more for oil for X number of years before eventually having to replace the boiler anyway.
So I am considering a few different options:
Option 1: replace WM boiler with System 2000 EK1 oil boiler. Our oil company is an experienced EK dealer/installer. I would probably go ahead and replace the two oil tanks at the same time so I don't have to worry about them leaking. I would also probably keep the HTP indirect water heater instead of using the integrated System 2000 storage tank since the HTP is only 5 years old.
Option 2: remove the oil boiler/tanks and convert to propane with high efficiency condensing boiler. I would probably need to bury another 500 or 1000 gallon tank next to the existing 500 gallon tank.
Option 3: convert to propane like in Option 2 but still get the System 2000 EK1 with a propane burner.
Option 4: do nothing. wait until current cast iron boiler leaks to replace. wait until oil tanks leak to replace, etc.
I plan to get pricing on all these options soon but was curious what the helpful people here think.
Thank you!
Comments
-
Using last weeks energy costs for CT. Your actual prices may vary. Both operating at 82%
EIA has fuel costs dating back as many years as you want to look.
Oil is the clear winner. Crunch the numbers to see at what $$ LP would be the better choice
LP in my area is currently $2.27, heating oil $3.65
www.coalpail.com for energy calculator
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
We're in a similar size house (4800 sq ft), with similar boilers (two circa 1990 Weil McLain WGO-5's) and similar oil consumption (1200 gal/yr) in similar climate (Boston area). But our DHW is from a natural gas heater.
I'm just a homeowner/engineer, not a heating pro, but I've learned a bit from the generous pros here. I've looked at a lot of new heating system options, and the one point warning I would give about considering a switch to a "high efficiency" condensing gas boiler is that you will NOT get the advertised high efficiency number UNLESS your heating system can heat the house for most of the heating season with supply water temperatures below 130 F. If your supply water has to be hotter than that, it will prevent the water vapor in the boiler exhaust from condensing, and you won't get that heat back. Your "high efficiency" condensing boiler is now not so high efficiency.
You'd need someone who knows what they're doing to analyze your system and evaluate how much of the season your boiler would actually be condensing. From that you can then figure how much fuel you'd be saving. Usually it's not as much as you think, because of the inherent limitations of a heating system that was (probably) designed for higher supply water temps.
If it were me, I'd go for the System 2000 EK1. It's a very nice system, and will probably be as high-efficiency as you can get (with the indirect for DHW) without condensing. Support is excellent, and you will avoid many of the headaches that come with servicing/repairing condensing boilers that cost $$ and eat into your fuel "savings." It will last a long time and work well with minimal problems.
It is possible that you could save in the long run with a condensing boiler, but the key is knowing how much of the time the boiler will be able to condense based on your required supply water temp. A heating pro can calculate that. But the unknown unknown is how much more it will cost you to service and repair a condensing boiler.
1 -
actually even at high operating temperatures the mod con efficiency can be quite impressive
Low return and turned down burners gets you into 90%+ efficiency. 50 degree return at 25% modulation is at the top efficiency
So the rumor about oversized mod cons doesn’t actually pencil ✏️ out
Example from Idronics 25
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Do your sums very carefully… but I think you will find that oil is going to beat LP anywhere in Connecticut., even supposing you can get the extra say 8% condensing all the time. Which you won't.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
304,000 net BTU's for 4,800 sq ft is ludacris if the boilers are firing what they're rated for.
0 -
Haha, yes, you must have missed the last 3 years of my posts discussing this ridiculous oversizing.
I was able to talk our heating oil company into downfiring to 1.0 gph nozzles running at 140 psi for an actual firing rate of 1.2 gph. But even so, we're still oversized by 3x. Outside air temp was 4 degrees last night, and the boilers ran a 33% duty cycle. So our actual building heat loss at near-zero outside air temp is 80-100MBH depending on what you assume for overall boiler efficiency. I use the 100MBH number for convenience and to be conservative. But our design day heat loss is probably closer to 80MBH because we're probably only getting 65% total efficiency out of the boilers.
1 -
Thanks everyone for the responses. Since a couple folks mentioned fuel prices: currently we pay $3.29/gal for oil (capped contract price from July) and just got a 200+ gallon propane delivery at $2.60/gal last week.
If we're going to make a change, my inclination is to go with the EK1 given our long runway in the house and all the good things I've read about them in this forum and elsewhere.
My desire to switch to propane is mostly about getting rid of the hundreds of gallons of oil sitting in my basement, and about only having to deal with one type of fuel delivery in the future. We also already have a lot of the infrastructure for LP in place (likely just need another supplemental tank). But maybe oil is still the way to go.
Someone from the fuel company is supposed to come this week to go over options and I look forward to getting actual prices to compare.
0 -
Your oil is cheaper. $3.29 for oil is about $.0235 per 1,000 BTU. Propane is $.027 per 1,000 BTU. Your 1200 gallons of oil would cost about $4,000; the same amount of heat from propane would be around #4,600.
I don't know about you, but that is NOT the kind of "savings" I can afford…
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Your at 26 years and I would say 30 years from a boiler and oil tanks are a good run. I would not consider propane.
Not only is propane more $ but any decent?? service tech can keep a Weil McLain going, a service tech that is good with modcons…..not so much. If your dealer knows EK I would go that way with oil.
Make sure the new boiler is sized correctly. Using hydro air means you need hotter system water which is not to a mod cons advantage
1 -
Great comments all around - it's always encouraging to see homeowners like you ,@ctboiler28, digging into the analysis to make a good long term decision for comfort, efficiency, service, and reliability. Many excellent points have been made already, so I will only chime in on a few.
I come up with the same figures as @Jamie Hall to compare the fuels at 1200 gallons equivalent ($4,000 and $4,600 for oil and LP respectively). A reasonable rule of thumb to calculate the input heat loss is to use 1% of annual consumption on design day and divide by 24. So 1200 gallons would be about 70,000 BTU/hr input (1200 gallons x 138,600 BTU/gallon oil x 1% / 24hours/day). If you are running with an annual efficiency of 80% (generous), that would be 56,000 BTU/hr heat loss. And that covers hot water production as well. The 1% figure is the fraction of heating degree days on design day compared to annual heating degree days (this is a very good approximation everywhere in the Northeast).
In the BNL heat and hot water boiler performance study, the System 2000 low mass with thermal purge design performed with an annual heat and hot water efficiency higher than the 95 AFUE modcon and other condensing boilers tested. Low idle loss is a primary contributor to high annual efficiency - we've discussed this in many other threads, so I won't go into detail here; basically when a boiler shuts off, remaining heat energy is wasted, so finishing "cold" with thermal purge through thousands of cycles is a proven pathway to high annual efficiency. That means you'll get exceptional performance in a 30 year proven boiler. An indirect tank with a coil will provide very good hot water temperature and volume with System 2000, but it will not thermally purge as well as a plate heat exchanger with a stratified storage tank so there is a further opportunity to improve performance when the HTP tank reaches its end of life.
If you decide to stay with oil, Roth and Granby double wall tanks look much more modern and "appliance like" than typical steel tanks, and they have exceptional warranties; maybe something to consider.
Please PM me, call customer service at (908) 735-2066, or reach out to our territory manager from Connecticut, Mark Santangelo (413) 575-0210 msantangelo@energykinetics.com if we can assist with any questions you may have.
Best,
Roger
President
Energy Kinetics, Inc.2 -
contact your propane supplier and tell them you are considering becoming a heating customer and ask them to quote you a price with an additional 1800 gallons of annual volume.
0 -
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements