Gorton #2?
Good morning. This vent on a friend's, 2pipe steam, boiler seems to be stuck open. Can it be replaced with a gorton #2?
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
Yes, just be aware the Gorton #2 has a 1/2" male connection and is quite large so you might need to adjust your riser there
couldn’t he just use a gorton #1?
He could use a Gorton #4 if he wanted to, but he asked about the #2
It would depend on how much venting he needs. It is my opinion that in many of the cases where people are using one or even 3 Gorton #2, a #1 would be good enough, but it's that kind of thinking that makes people click the "LOL" button on my posts without providing any evidence that I'm wrong.
500+ LOLs provided, you're welcome!
See my sight glass boiler videos: https://bit.ly/3sZW1el4 -
Interesting.. why?
I'll give my answer—it was because they take forever and a lot of steam to close, they don't stay closed, and they fail open real quick (in my experience)
Thanks, it's on a return line so #1 should be fine.
The radiator it's attached to hasn't been heating up.
@guzzinerd , if that's the only vent in the system, use the #2. In that case it has to vent the mains as well as the radiators.
Consulting0 -
Alrighty then. Thanks!