Gorton #2?
guzzinerd
guzzinerd Member Posts: 461
Good morning. This vent on a friend's, 2pipe steam, boiler seems to be stuck open. Can it be replaced with a gorton #2?
Bryant 245-8, 430k btu, 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains. 26 radiators 3800sqf
    ethicalpaul Member Posts: 8,928
    Yes, just be aware the Gorton #2 has a 1/2" male connection and is quite large so you might need to adjust your riser there
    guzzinerdtcassano87
  • guzzinerd
    Thanks
    edited January 13
    He could use a Gorton #4 if he wanted to, but he asked about the #2
    It would depend on how much venting he needs. It is my opinion that in many of the cases where people are using one or even 3 Gorton #2, a #1 would be good enough, but it's that kind of thinking that makes people click the "LOL" button on my posts without providing any evidence that I'm wrong.
    500+ LOLs provided, you're welcome!
    guzzinerdtcassano87TezakPeteA
  • guzzinerd
    edited January 13
    Looks like the only vent in his mains, and only one crossover near the boiler. A #1, 2 or 4...I don't care either way, the #2 seems to be the popular choice in here
  • Tezak
    Tezak Member Posts: 44
    I’ve never felt as free as the day I replaced all my big mouths with #1s.
  • guzzinerd
    Interesting.. why?
    I'll give my answer—it was because they take forever and a lot of steam to close, they don't stay closed, and they fail open real quick (in my experience)
    Tezak
  • Tezak
    Yeah, I was losing a significant amount of water due to them taking g forever to heat up and close. With the #1s I lose almost nothing. I haven’t noticed any difference in performance or efficiency.
  • guzzinerd
    Thanks, it's on a return line so #1 should be fine.
    The radiator it's attached to hasn't been heating up.
    Steamhead Member Posts: 18,693
    @guzzinerd , if that's the only vent in the system, use the #2. In that case it has to vent the mains as well as the radiators.
    Consulting
  • guzzinerd
