Two supply tapping
magewick
magewick Member Posts: 29
Near boiler pipping installation instruction shows two riser tapping to main. Contractor only installed a single riser to main. Utica technical was contacted - they said that the boiler is designed to have two risers - one riser should not be used. Please. advise
E1A0C9B6-AE7B-4ABE-AFDE-4DBD8AE7AF61_1_201_a.jpeg BB6D22E9-057F-422F-B7F7-61EC1D320583_1_201_a.jpeg
    mattmia2 Member Posts: 16,117
    edited January 6
    the installer was unable to read and follow the installation manual. hope you haven't paid them yet.
    might be ok, we need to see a couple pictures from different angles, especially both sides. might be a header arranged in a U.
    make sure the pipe sizes follow the manual and that the order of the risers from the boiler, the risers to the building steam main(s) and the connection to the equalizer are in the order show in the manual too.
    magewick
    how many sections is your boiler/what is the model?
  • magewick
    5 sections
    Model IUD-1605HSID
    EBEBRATT-Ed Member Posts: 19,947
    Is your model # correct?
    All you or your installer has to do is read the manual that comes with the boiler. They show the piping diagram.
    Follow the diagram for pipe sizes and riser, equalizer and steam supply piping. It's very simple.
  • ChrisJ
    ChrisJ Member Posts: 17,180
    What is everyone's thoughts about the outer jacket (paper?) of the pipe insulation resting against the flue pipe?
    Since this is a new install I feel it needs to at least be made to meet the manufacture's minimum requirements which it currently does not.
  • KC_Jones
    KC_Jones Member Posts: 5,917
    We might need a better picture here, I think I see 2 risers (marked in red). Can you take a picture further back so we can more clearly see all the piping?
    2014 Weil Mclain EG-40
    ethicalpaulmattmia2
    I think @KC_Jones may be right, the header is arranged in a u right along the back, to the front then to the left but it is hard to see here. If the pipe sizes are ok, then it is ok.
    The guy that piped it didn't have a clue or he owns a supply house.
    I count no less than 5 unions and there is probably another one on the RH insulated riser making it 6.
    All you need is 3.
    If I had done that with 6 unions, they would have tossed me out of the union
    ethicalpaulmattmia2dabrakemanpecmsg
    ethicalpaul Member Posts: 8,463
    How long have you been waiting to use that one? 😂 Pretty funny though
    Steamhead Member Posts: 18,330
    @magewick , it's wrong. Have them repipe it according to the diagram.
    Consulting
    that's what i thought but I think it might be correct and in a big u that we can't see from the camera angle
    It looks like they had the boiler connections correct (assuming right size which you should check) in this post then thy added that loop in the equalizer to get the main connection correct:
    also note that this is a vapor system.
    @ethicalpaul Truth is I never noticed the pun when I typed that (if that is what it is). 3 unions in the equalizer alone.
  • Grallert
    Grallert Member Posts: 1,083
    I agree but he does say there's only one. Hopefully he'll come back to clarify.
    pecmsg Member Posts: 6,933
    And galvanized pipe for makeup water?
