Two supply tapping

Options

Near boiler pipping installation instruction shows two riser tapping to main. Contractor only installed a single riser to main. Utica technical was contacted - they said that the boiler is designed to have two risers - one riser should not be used. Please. advise

E1A0C9B6-AE7B-4ABE-AFDE-4DBD8AE7AF61_1_201_a.jpeg BB6D22E9-057F-422F-B7F7-61EC1D320583_1_201_a.jpeg

Comments

  • mattmia2
    mattmia2 Posts: 18,399
    edited January 6

    the installer was unable to read and follow the installation manual. hope you haven't paid them yet.

    might be ok, we need to see a couple pictures from different angles, especially both sides. might be a header arranged in a U.

    make sure the pipe sizes follow the manual and that the order of the risers from the boiler, the risers to the building steam main(s) and the connection to the equalizer are in the order show in the manual too.

    magewick
  • mattmia2
    mattmia2 Posts: 18,399

    how many sections is your boiler/what is the model?

  • magewick
    magewick Posts: 32

    5 sections

    Model IUD-1605HSID

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Is your model # correct?

    All you or your installer has to do is read the manual that comes with the boiler. They show the piping diagram.

    Follow the diagram for pipe sizes and riser, equalizer and steam supply piping. It's very simple.

  • ChrisJ
    ChrisJ Posts: 17,763

    What is everyone's thoughts about the outer jacket (paper?) of the pipe insulation resting against the flue pipe?

    Since this is a new install I feel it needs to at least be made to meet the manufacture's minimum requirements which it currently does not.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • KC_Jones
    KC_Jones Posts: 5,964

    We might need a better picture here, I think I see 2 risers (marked in red). Can you take a picture further back so we can more clearly see all the piping?

    image.png
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ethicalpaulmattmia2
  • mattmia2
    mattmia2 Posts: 18,399

    I think @KC_Jones may be right, the header is arranged in a u right along the back, to the front then to the left but it is hard to see here. If the pipe sizes are ok, then it is ok.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    The guy that piped it didn't have a clue or he owns a supply house.

    I count no less than 5 unions and there is probably another one on the RH insulated riser making it 6.

    All you need is 3.

    If I had done that with 6 unions, they would have tossed me out of the union

    ethicalpaulmattmia2dabrakemanpecmsg
  • ethicalpaul
    ethicalpaul Posts: 9,076

    If I had done that with 6 unions, they would have tossed me out of the union

    How long have you been waiting to use that one? 😂 Pretty funny though

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    mattmia2
  • Steamhead
    Steamhead Posts: 19,007

    @magewick , it's wrong. Have them repipe it according to the diagram.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • mattmia2
    mattmia2 Posts: 18,399

    that's what i thought but I think it might be correct and in a big u that we can't see from the camera angle

  • mattmia2
    mattmia2 Posts: 18,399

    It looks like they had the boiler connections correct (assuming right size which you should check) in this post then thy added that loop in the equalizer to get the main connection correct:

    also note that this is a vapor system.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @ethicalpaul Truth is I never noticed the pun when I typed that (if that is what it is). 3 unions in the equalizer alone.

    ethicalpaul
  • Grallert
    Grallert Posts: 1,237

    I agree but he does say there's only one. Hopefully he'll come back to clarify.

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • pecmsg
    pecmsg Posts: 7,634

    The guy that piped it didn't have a clue or he owns a supply house.

    And galvanized pipe for makeup water?

  • ethicalpaul
    ethicalpaul Posts: 9,076

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el