Steam boiler
steam boiler keeps running 10-12 minutes then shuts off for a minute or 2 then comes on. Pressuretrol and pigtail are new. All radiators are hot. Its going off on pressure what do you think is the problem i appreciate your feedback
Boiler is slightly oversized and cycling on pressure, unless the LWCO is a Cyclegard, in which case it may be the Cyclegard which also cuts out with about that timing to get a really good read on water leve.
Sounds normal, either way.
Oil or gas boiler? What pressure is it tripping off at? Is your venting adequate?
Gas boiler; it has a safeguard LWCO that goes off every 20mins for a self check but in-between that the pressuretrol goes off at 5psi then a minute later boiler comes back on
Has it always operated like this? What has changed?
5psi seems excessive, what is the pressuretrol set at ? Are any radiators closed off ?
One Pipe System0 -
5 psig is WAY too high. Picture, please, of the pressure control device. Also, has the pigtail to it been cleaned?
Kind of wonder if the gauge is accurate. Since "Pressuretrol and pigtail are new". Is the tapping into the boiler blocked ?
One Pipe System0 -
Pressuretrol is set at 2;2 pigtail and Pressuretrol are both new gauge is tapped into the top of the boiler all radiators are open and hot
If the pressuretrol is set to cut out at 2 but the pressure still goes up to 5, something is quite wrong. The pressuretrol might be out of calibration — most of them are — but that far out would be odd. One has to wonder… is it properly wired in?