Steam boiler
steam boiler keeps running 10-12 minutes then shuts off for a minute or 2 then comes on. Pressuretrol and pigtail are new. All radiators are hot. Its going off on pressure what do you think is the problem i appreciate your feedback
    Boiler is slightly oversized and cycling on pressure, unless the LWCO is a Cyclegard, in which case it may be the Cyclegard which also cuts out with about that timing to get a really good read on water leve.
    Sounds normal, either way.
    bburd
    edited January 2
    Oil or gas boiler? What pressure is it tripping off at? Is your venting adequate?
  • Gas boiler; it has a safeguard LWCO that goes off every 20mins for a self check but in-between that the pressuretrol goes off at 5psi then a minute later boiler comes back on
    Has it always operated like this? What has changed?
    109A_5 Posts: 4,759
    5psi seems excessive, what is the pressuretrol set at ? Are any radiators closed off ?
    5 psig is WAY too high. Picture, please, of the pressure control device. Also, has the pigtail to it been cleaned?
    109A_5 Posts: 4,759
    Kind of wonder if the gauge is accurate. Since "Pressuretrol and pigtail are new". Is the tapping into the boiler blocked ?
  • Pressuretrol is set at 2;2 pigtail and Pressuretrol are both new gauge is tapped into the top of the boiler all radiators are open and hot
    If the pressuretrol is set to cut out at 2 but the pressure still goes up to 5, something is quite wrong. The pressuretrol might be out of calibration — most of them are — but that far out would be odd. One has to wonder… is it properly wired in?
    109A_5 Posts: 4,759
    If you have a PA404 Pressuretrol it should be set like this picture, however you may have other issues if the pressure is actually going up to 5psig.
    Gomichigan7383