What digital thermostat will work 2 black wires
Moved into an apartment.
Boiler. Hot water baseboard. Zone valve fails open (the moment I disconnect the wires on the old system it goes full heat). Two black wires.
I tried Rthb20c Honeywell. Two calls to Honeywell and it was still full heat.
Here is the old one. I put the painters tape on the one wire when I was troubleshooting.
  • Ironman
    Ironman Member Posts: 7,886
    It sounds like you have “normally open” zone valve which means they have to be powered shut. That’s the reverse of most.
    Any thermostat that has cooling terminals available (R and Y) should work.
    Bob Boan
    EBEBRATT-Ed Member Posts: 19,881
    You can figure this out by disconnecting the wires from the thermostat. Leave them apart. If the valve goes closed you need a heating thermostat. The wires would go to r or RH and W
    If the valve goes open you need a cooling thermostat and would hook the wires to R or Rc and Y
    Jamie Hall Member Posts: 26,991
    And in either case, a digital thermostat will need to be battery powered.
  • Dwheat
    Dwheat Member Posts: 2
    Thanks gentlemen
    R+Y
    Switch the thermostat to cool.
    Works perfect