Makeup water causing boiler failure due to thermal shock
2»
    ethicalpaul Member Posts: 8,093
    thanks, I meant to put the word “residential” in my original post!
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,506
    For what it's worth.... Part of my regular maintenance, is to put 8-way into the boiler. Fire boiler until it steams. Shut off. Fire on and off to keep boiler hot. For approx half hour. Drain boiler completely down. Fill, with manual valve. Full speed. Until boiler is full. With cold water. Drain and fill, drain and fill...until water is clean. Fill back up and fire.
  • fentonc
    fentonc Member Posts: 323
    1. A house I was renting had a steam boiler crack. The LWCO was broken, the boiler steamed itself dry, and then returning condensate caused it to crack when it met the red-hot boiler.
    2. As part of my on-going experiments in improving (hydronic) boiler efficiency, I've settled on a scheme that immediately opens all of the zones in the house to do a 'thermal purge' cycle when the last zone is done calling for heat. This effectively means dumping a lot of cold water into a hot CI boiler, and it can drop the temperature from (up to) 180F down to 65F or so in a few minutes. I haven't noticed any detrimental side effects though, and the temperature change seems pretty gradual, as the cold water is mixing with the last-active hot water loop (plus the water + thermal mass of the boiler itself).
    I'll definitely report back if I crack my boiler in half this winter!
  • ChrisJ
    ChrisJ Member Posts: 17,060
    If anything I'm amazed at all the comments about dry fired boilers.
    ethicalpaulGGross
    ok good data there! But I didn’t even know you had a steam boiler!
    Now I have to ask, why do you drain it? It should be staying clean with 8-way in it even with no draining
    I’m definitely not doubting your story, but condensate returns at a steady rate. It can’t really get dry until all the water is gone. Is it possible that makeup water was added after it was dry and HOT?
    mattmia2 Member Posts: 15,520
    LWCOs are only required on hot water boilers if they have emitters below the boiler in most jurisdictions, if there is no water in the boiler sometimes the aquastat doesn't see the temp of the part near the burner and sometimes gas valves stick on, you combine that with another failure like the pvr is stuck closed or someone keeps the feed to the prv off because they don't want a flood if a hydronic pipe breaks and suddenly you have a dry fire event. The same sort of things can happen with a warm air furnace.
  • ChrisJ
    So all of the fear with Hartford loops etc on steam boilers yet hot water doesn't have it and doesn't even have a lwco?
    hot_rod Member Posts: 26,565
    analysis paralysis😯
  • fentonc
    @ethicalpaul - I don't actually know. This was before I got interested in home heating, it was a poorly maintained rental, and I was vaguely recalling that's what the plumber told us (over a decade ago). I think we just came home from work and noticed the house wasn't heating. I don't recall the basement flooding in the same incident.
  • STEAM DOCTOR
    edited November 21
    I do this on every steam boiler that I am service. Just for clarity, I only service residential. Cleaning is part of maintenance. The eight way will break down the sludge. Repeated draining remove the sludge. Adding eight way after the fact, will greatly reduce the sludge going forward.
    you could have had something going on with pressure that was keeping the water from returning to the boiler then you shut down the burner and as it cooled the pressure decreased and the stacked up condensate rushed in to the boiler.
    there was like a 10 page discussion on hartford loops that I didn't read but the main upshot is that it is largely leftover from solid fuel fired boilers where stopping the fire is difficult to do quickly if the water runs out of the boiler.
    EBEBRATT-Ed Member Posts: 19,502
    @retiredguy
    Smith (if there still in business) the last 28s I did which was about 8 years ago they stopped using the blend pump as far as I know. They now provide a "return temperature stabilizer". It is a perforated tube of expanded stainless steel with I think a flange on one end. It goes in the 6" tapping in the back section and goes through the top nipple port and runs the length of the boiler. The return water is now piped to the 6" tapping. The return water flows through the "stabilizer" to all sections so I guess it puts the back section under less thermal shock
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,529
    No.
    newenglandsteamworks.com
  • GGross
    GGross Member Posts: 1,732
    We are definitely required to install LWCO or a flow switch safety on all boilers in my county, residential and commercial. Technically the entire state of michigan has to but local inspectors are allowed to interpret the code however they please.
    ChrisJ