thanks, I meant to put the word “residential” in my original post!
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
For what it's worth.... Part of my regular maintenance, is to put 8-way into the boiler. Fire boiler until it steams. Shut off. Fire on and off to keep boiler hot. For approx half hour. Drain boiler completely down. Fill, with manual valve. Full speed. Until boiler is full. With cold water. Drain and fill, drain and fill...until water is clean. Fill back up and fire.
1 -
- A house I was renting had a steam boiler crack. The LWCO was broken, the boiler steamed itself dry, and then returning condensate caused it to crack when it met the red-hot boiler.
- As part of my on-going experiments in improving (hydronic) boiler efficiency, I've settled on a scheme that immediately opens all of the zones in the house to do a 'thermal purge' cycle when the last zone is done calling for heat. This effectively means dumping a lot of cold water into a hot CI boiler, and it can drop the temperature from (up to) 180F down to 65F or so in a few minutes. I haven't noticed any detrimental side effects though, and the temperature change seems pretty gradual, as the cold water is mixing with the last-active hot water loop (plus the water + thermal mass of the boiler itself).
I'll definitely report back if I crack my boiler in half this winter!
1 -
-
ok good data there! But I didn’t even know you had a steam boiler!
Now I have to ask, why do you drain it? It should be staying clean with 8-way in it even with no draining
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I’m definitely not doubting your story, but condensate returns at a steady rate. It can’t really get dry until all the water is gone. Is it possible that makeup water was added after it was dry and HOT?
NJ Steam Homeowner.
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
LWCOs are only required on hot water boilers if they have emitters below the boiler in most jurisdictions, if there is no water in the boiler sometimes the aquastat doesn't see the temp of the part near the burner and sometimes gas valves stick on, you combine that with another failure like the pvr is stuck closed or someone keeps the feed to the prv off because they don't want a flood if a hydronic pipe breaks and suddenly you have a dry fire event. The same sort of things can happen with a warm air furnace.
0 -
-
analysis paralysis😯
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@ethicalpaul - I don't actually know. This was before I got interested in home heating, it was a poorly maintained rental, and I was vaguely recalling that's what the plumber told us (over a decade ago). I think we just came home from work and noticed the house wasn't heating. I don't recall the basement flooding in the same incident.
1 -
-
you could have had something going on with pressure that was keeping the water from returning to the boiler then you shut down the burner and as it cooled the pressure decreased and the stacked up condensate rushed in to the boiler.
0 -
there was like a 10 page discussion on hartford loops that I didn't read but the main upshot is that it is largely leftover from solid fuel fired boilers where stopping the fire is difficult to do quickly if the water runs out of the boiler.
0 -
Smith (if there still in business) the last 28s I did which was about 8 years ago they stopped using the blend pump as far as I know. They now provide a "return temperature stabilizer". It is a perforated tube of expanded stainless steel with I think a flange on one end. It goes in the 6" tapping in the back section and goes through the top nipple port and runs the length of the boiler. The return water is now piped to the 6" tapping. The return water flows through the "stabilizer" to all sections so I guess it puts the back section under less thermal shock
1 -
No.
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com1 -
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements