In imminent danger of house freezing (Minnesota) - solutions?

Options
tmoritz
tmoritz Member Posts: 1
edited November 10 in Gas Heating

Hi - My Buderus GB142-60 is cooked. I had renters and whatever happened led to the side glass with the little mirror melting. It won’t boot up anymore, immediately goes into lock down mode. Had a boiler guy who told me it cannot be repaired (which I believe - boiler discontinued in 2018). For a comparable setup (4000 square foot house), I was quoted a whopping $. There is literally no way I can do that at the moment. Question: What can I have installed to keep just the heating side going since I have to be gone for a month at a time? Next year I can work on a permanent solution, including hot potable. I won’t need that until then. Right now it’s about saving the house in freezing temps. Thank you all so much!

Comments

  • Ironman
    Ironman Member Posts: 7,859
    edited November 10

    Why don’t you have the house winterized?

    Pipes drained and blown out with air, then filled with antifreeze. Make sure you get someone who’s competent and thorough.

    There’s no cheap work around if you need a new boiler. Maybe look into financing options.

    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    mattmia2HVACNUT
  • hot_rod
    hot_rod Member Posts: 26,605

    electric boilers are less $$ but to replace a 168,000 boiler with electric would require a large circuit to operate

    A heat load calculation would indicate what size boiler would be needed.

    Could be a 4000 sq ft home only needs 80,000 btu boiler?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Jamie Hall
    Jamie Hall Member Posts: 26,842
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    WaherPC7060
  • hot_rod
    hot_rod Member Posts: 26,605

    So you are gone, home empty, for a month at a time during the winter?

    I'm not sure winterizing and bringing it back on line multiple times a winter is practical? Especially if you have to pay to have it done?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,602

    4000 sq foot is pretty large. Electric would be the way to go. Drain and winterize what you can and maintain a minimum temp.

    A couple of air handlers with electric heat strips would do the job.

  • hot_rod
    hot_rod Member Posts: 26,605

    You might size the electric just to maintain, say 50° while you are gone. That would reduce the breaker size.

    Digging deep may even show some off peak rates you could maximize. A visit to your electric providers website would answer some questions. They may have rebates to get you to switch or go dual fuel.

    I'd first get a second opinion on the Buderus, even the entire block is still available if you look around. Reps often keep donor boilers in their inventory for situations like this.

    Contact the rep in your area for some suggestions on a qualified Buderus serviceperson. In many cases a rep will pay you a visit if you are in a bind.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 15,634

    @hot_rod I think it is a combi mod con though they don't describe what is wrong with it specifically.

  • hot_rod
    hot_rod Member Posts: 26,605

    Was the GB offered in a combi version? I've only seen the boiler version.

    Screenshot 2025-11-10 at 11.59.29 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 15,634

    I assumed it was a combi because they mentioned dhw but I didn't dig that deep. Anything you replace it will will have significant cost in fittings and labor.

    What is specifically wrong with it?

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,602

    Chances are the right guy could get it running. Sounds like the "TECH" that looked at it couldn't be bothered

    mattmia2Ironman
  • DCContrarian
    DCContrarian Member Posts: 1,369

    I recommend this article to estimate the approximate size based on past fuel usage:

    https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler

    From that you can also estimate how much more it would cost you to heat with electric for a season. You may find the number eye-popping.

    I'm with @Ironman , drain the house down if it's going to be sitting vacant.

  • HVACNUT
    HVACNUT Member Posts: 7,235

    When the inspection mirror melts, that would tell me the HX has a nice hole in it. There's no repair for that because there's no more GB-142.

  • GroundUp
    GroundUp Member Posts: 2,466

    Where in MN is this located, and why is a rental home sitting vacant? Would getting the heat on allow you to fill the vacancy and bring income in to cover the cost of the new system? Winterization is going to be the best option financially if it'll be unoccupied all winter anyway, but a simple boiler swap isn't a crazy expense and perhaps a small personal or equity loan would get you back going quickly…

    Intplm.Ironman
  • Intplm.
    Intplm. Member Posts: 2,831

    If you are going to winterize, and I believe you should as mentioned above, have the meter removed by your water company and have the entire house's piping system pumped with non-toxic/recreational vehicle (RV) anti-freeze. All low points must be evacuated of water, including any appliances, ice maker, refrigerator etc.

    And then pour antifreeze in all toilet tanks, toilet bowls, and any "P" traps that would hold water. This will save the house till warm weather returns and a replacement can be installed.

    Ironman
  • DCContrarian
    DCContrarian Member Posts: 1,369

    I've done that. It took a long, long time to get all of the antifreeze out once the water was back on. The taste lingered for quite a while. I now prefer to blow the supply lines and fixtures out with compressed air. Traps and appliances get antifreeze.