Boiler Replacement Sizing Question
Hey all, we currently have a Utica PEG187 from 1991, that I am finally in the position to replace along with all of its crappy near boiler piping.
Our system has is smallish at 343.5 sf (82,440btu) of radiation. Using a standard 1.333 pickup factor places our system in between the Weil McLain ED-40 & EG-45 boiler models based on AHRI rating (no one installs Peerless around here).
All of the mains, branches, and condensate return lines still have their original asbestos insulation intact. We have added insulation in our attic and storm windows to increase the efficiency of the thermal envelope of the house. Would it be a mistake to "undersize" the boiler by using a EG-40 (resultant pickup factor of 1.24)?
  • ChrisJ
    ChrisJ Member Posts: 17,534
    Do not go larger than an EG-40.
    If it was mine id probably go EG-35.
    ethicalpaulmattmia2
    ethicalpaul Member Posts: 8,933
    edited November 2024
    Don't worry about the BTU, don't worry about the pickup factor. Just compare your installed radiation to the Net Sq Ft of steam of the boilers you are looking at.
    I wouldn't rule out Peerless or even Utica just because of what the contractors there like to install. There's no installation difference between any of the gas atmospheric steam boilers to speak of.
    For WM, the EG-40 is rated at 321, that's the one I would pick. The 33% pickup factor that I advised you ignore is outrageously oversized so 321 sq ft is plenty large. 388 (EG-45) would be a crime.
  • roc_rktec
    roc_rktec Member Posts: 46
    EBEBRATT-Ed Member Posts: 20,552
    The EG-40 is good for 321 sq feet of steam. That is what I would use.
    What part of the country are you in? Is your boiler actually failed?
  • roc_rktec
    Rochester, NY. Current boiler is still operational, but preemptively getting quotes to replace.
  • dabrakeman
    dabrakeman Member Posts: 1,020
    WM EG-40, Peerless 63-03 or a Burnham SteamMAx125 all in good range.
    roc_rktec
  • Marc_18
    Marc_18 Member Posts: 22
    My boiler size relative to radiation is similar. The boiler is a WM EG-45 and my best estimate of the radiation (from the various charts) is, say, 345 sq ft. If I had to replace the boiler at this point, I certainly would go smaller.
    However, the EG-45 can be pretty easily downsized to an EG-40 and I have had helpful discussions with @ChrisJ about doing this. Parts cost would be roughly $150. If the parts were not on extended back order, I would likely have already undertaken the modification.
    With the system as it is, I do observe cycling on pressure (2-2.5psi), but generally only when recovering from overnight setbacks of around 4 degrees or more. Main and radiator venting is all adequate. Steam mains and near boiler piping are all insulated. All the radiators fully heat up after an extended runtime.
    My question is whether you think making this modification makes any sense in terms of, say, potential fuel savings.
    I expect that a downsized system would mean - for every boiler firing - a somewhat longer time for the boiler to begin making steam and the lower rate of subsequent steam production would increase the time to heat up all the piping to the radiators. How much of this would be noticeable to me can’t be known without trying it.
    Your thoughts?
    mattmia2 Member Posts: 17,569
    is that a hot water automatic air vent?
    it’s minimal. You might be able to time it to see the difference but you’d never notice it from your living room.
    you can get a preview for free by blocking one of the burners with a small piece of aluminum tape over the burner supply orifice.
    Don’t block the one that the flame proving rod is attached to 😅
    By adding some 8-way water treatment and being vigilant about leaks you can dramatically reduce corrosion and the boiler could last years longer
  • Marc_18
    Ok. Then what about the potential benefits from downsizing? Fuel savings, less cycling on pressure after setbacks, lower average steam pressure. Noticeable or minimal? Crime not to do it in your view?
    "With the system as it is, I do observe cycling on pressure (2-2.5psi), but generally only when recovering from overnight setbacks of around 4 degrees or more."
    If it only cycles coming out of setback downsizing will do nothing. I would spend the money on something else. JMHO
    Steamhead Member Posts: 18,735
    edited October 2025
    @roc_rktec , if you're going with Weil-McLain, I'd use the EG-45 and downfire it a bit if needed. This would mean the cast-iron would run a bit cooler and last longer.
    The only thing wrong with your present Utica is the installer. There may be some illiteracy issues there- proper piping is spelled out in the manual. I'd repipe it, in such a way that when replacement time comes you won't have to rip everything out.
    That air vent in the first pic looks like it's in the wrong place. Steam from the header will reach it quickly and close it. The proper place for these vents is at the ends of the steam mains and, if this is a 2-pipe or Vapor system, at the ends of the dry (overhead) returns.
    If you're not sure what type your system is, post pics of some radiators that do not have covers. We can tell from this.
    Consulting
  • Marc_18
    Even if I see cycling on pressure only after long run times (mainly after setbacks), wouldn’t downsizing result in lower average steam pressure?
    Anytime I’m creating steam at pressures of more than just an ounce or two, am I not using more fuel than needed to fill the radiators? You might say yes, but the savings would be ‘minimal’ and likely not worth the time and expense to downsize in my case. This is what I’m trying to get at.
    edited October 2025
    The savings that would be even slightly more than negligible would only happen during the once a day during recovery from setback and even then would be tiny compared to the cost of replacement so it would never pay for the replacement cost. just do it right when it does need to be replaced.
    since you commented on someone else's year old post, can you show us your near boiler piping? If your near boiler piping is as bad as the piping from the op and it affects the speed with which the system heats then fixing it could be worth it.
    as stated above the savings are going to be very little. This is because for every unit of fuel you burn, about 80ish percent of the heat produced goes into your home envelope.
    this is true for oversized, undersized, correctly sized.
    A correctly sized or undersized boiler will run at lower pressure generally but that doesn’t change the facts above. It’s good to have it sized correctly but it’s not worth pulling a working boiler
    A smaller boiler is less costly. I wouldn’t buy a larger boiler and downfire it. I think the stated benefit of that is highly speculative. But different strokes for different folks
    the boiler piping looks pretty good, changing it isn't going to do anything for you. make sure you have good venting at the end of the mains.
  • Marc_18
    Thanks for having a look.
    I have a Big Mouth at the end of the single 60-foot, 2.5” main and also a spare Gorton #2 midway (since there was a tapping there.)
    One change I’ve made for this heating season is replacing my older thermostat with a VisionPro 8000. This model gives me the option for CPH setting of 2 instead of just 1 (or 3) like the older model. I’m expecting to see smaller temperature overshoots (and undershoots). So tighter temp control and therefore less boiler on-time opportunity for building the higher undesired pressures. Am interested to see the effects.
    the biggest difference will be made with air sealing and insulation of the structure
    @Marc_18 , I'd move that Gorton #2 to the end of the main, teed into the location where the Big Mouth is now. You want all your venting capacity at the end of the main.
    Consulting