Boiler Replacement Sizing Question
Hey all, we currently have a Utica PEG187 from 1991, that I am finally in the position to replace along with all of its crappy near boiler piping.
Our system has is smallish at 343.5 sf (82,440btu) of radiation. Using a standard 1.333 pickup factor places our system in between the Weil McLain ED-40 & EG-45 boiler models based on AHRI rating (no one installs Peerless around here).
All of the mains, branches, and condensate return lines still have their original asbestos insulation intact. We have added insulation in our attic and storm windows to increase the efficiency of the thermal envelope of the house. Would it be a mistake to "undersize" the boiler by using a EG-40 (resultant pickup factor of 1.24)?
Comments
-
-
Don't worry about the BTU, don't worry about the pickup factor. Just compare your installed radiation to the Net Sq Ft of steam of the boilers you are looking at.
I wouldn't rule out Peerless or even Utica just because of what the contractors there like to install. There's no installation difference between any of the gas atmospheric steam boilers to speak of.
For WM, the EG-40 is rated at 321, that's the one I would pick. The 33% pickup factor that I advised you ignore is outrageously oversized so 321 sq ft is plenty large. 388 (EG-45) would be a crime.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
0
-
-
What part of the country are you in? Is your boiler actually failed?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
WM EG-40, Peerless 63-03 or a Burnham SteamMAx125 all in good range.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements