Groundwater (possibly high) and adding thin radiant slab over existing uninsulated slab, below grade
rossn
rossn Posts: 161
edited October 2025 in THE MAIN WALL
I'm planning to add insulation, radiant loops, thin concrete layer over 1960s slab, 4' below grade in an area that heats Mid-Oct to mid-May.
Then it happened Friday. I read a comment on this forum about ground water within 6'. I spent the weekend shooting elevations and reviewing neighbor soil tests. There is also a good sized farm irrigation ditch that crosses the property, running mid-May to July. My conclusion is #1) likely high groundwater while the ditch runs and a little after and… #2) possibly within the 6' zone at other times, but hard to know for sure. Could be a foot or two above or below.
Local average groundwater temps are 51F. Slab relative humidity (when it's been checked) ranges from 70%-99% RH.
I don't mind the situation #1. It seems #2 could be an issue.
a) how bad is this, practically?
b) are there any 'not quite full' soil tests that allow you to gauge water table level without spending big bucks?
c) open to any other information. Also have a diagram summarizing what is known that I can share… but it's complex.
Thanks, guys.
    hot_rod Posts: 28,708
    it sounds like you need a drainage system around the building, possibly a sump pump to keep the level down
    Water or moist ground under the slab, not good
    rossn
  • rossn
    rossn Posts: 161
    edited October 2025
    @hot_rod - there's no bulk water issue whatsoever. Years ago we excavated around the home, installed a perimeter drain near and slightly below the footer, etc and dimple mat on the stem walls. That was a BIG project… the crew hand digging it was here probably 6-8 weeks. It drains to a perforated sump inside the home which I installed, 3' deep, maybe perforated down 24"-28". That pump has run only a couple times that I can remember or have seen in the last 7 years - so the groundwater doesn't get within 2' of the slab. Is the water 4' or 12' when the ditch isn't running? I'm not sure.
    Of course, the perimeter drain was only slightly below the footer, and 5' more is a long ways down. When I dug the sump, which I am guessing was 2' after the ditch stopped running, the sandy soil I excavated down to 3' was 100% damp, but not to the point you could squeeze any moisture out of it.
    Im part of an irrigation system dating back to the 1920s As homes and subdivisions replace the farms we have been installing culverts to replace open ditches
    This solves a few issues like you mentioned as well as mosquitoes and liability. We use mainly 15” corrugated plastic pipe, concrete diversion boxes at property corners
    It seems a bore hole in a few places would shed some light on the water table level
    Maybe rent a powered post hole digger
  • rossn
    rossn Posts: 161
    edited October 2025
    In my county there are many of these ditches. Hand dug for 10's of miles in the 1800's. They fill some of the local reservoirs. You would need more like a 5' culvert, or two 4' :) It's probably 4' across at the bottom, 15' across at the top, and the bridge is about 5-1/2' above the bottom of the ditch.
    I would go for a post hole digger if they make one that would go that deep…. but we're talking 10' just to hit 6' below the basement. Or 6-1/2' if cutting the slab, which is a bit of a chore.. I'm not sure they will do those depths?
    Now, I do have a well near the house I've never opened in 9 years - has been inoperable. I started digging out the cover today to see if I can open the head and see if the top liner is perforated. Original hand written permit mentions 5-60' tan white limestone, which wasn't mentioned in soil studies 200' to the east and 160' to the S. The house is long and narrow… the ends may have entirely different soils… so I agree with your comment on multiple holes.
    The problem with high water table, but below your slab (which it sounds like it is) is that saturated soil is a wonderful conductor of heat — and it's even worse if the water is moving (it may not be in your case).
    However — it's easy enough to avoid the problem: insulation. You mention insulation in your original post — and that's your answer. As much of it — at least two inches, maybe four to six if you can lose the headroom.
    rossn
    If the ditch is causing the high water table, and only runs May- July it should not effect your radiant slab so much? Only one way to know for sure.
    Can you check the level in the well, that may tell you something. Although the well water should not be run-off water necessarily.
    The farms stop irrigating in July? We run May- September here.
    rossn
  • DCContrarian
    DCContrarian Posts: 1,588
    This is the answer. You're focusing on the wrong thing by looking at the groundwater. Without insulation, most of the heat you send into the slab is going into the ground and not the living space, regardless of the soil type below.
    rossn
  • rossn
    rossn Posts: 161
    edited October 2025
    I came to the conclusion over night that I likely won't know if I have groundwater here, without some tests, which can be expensive. On Jamie and DCContrarian's point, I don't know how significantly ground water or moist soil affects the overall heat loss, other than it's notable. My calcs, which are old and in Uponor's old ADS program jump up about 25% when I check the 'groundwater within 6' checkbox. I also saw postings here about natural gas consumption doubling or tripling. Is one of these closer to the truth than the other? I will ask my radiant guy to also re-run his numbers with groundwater considered.
    I spent an hour on the phone with my architect friend today. Since the company doing the soil studies for septic and construction near by is no longer in business, he gave me the name of the guy who had worked for them and took over. I will check with him.
    @Jamie Hall and @DCContrarian - The original plan I had built the stairs to was for a slim assembly. 1" EPS or XPS insulation, 1/2" loops, and 1-1/4" concrete over the insulation - so 2-1/4" assembly. My radiant guy said more insulation was better, but that I could get by with an inch. He mentioned 1-1/4 to 1-1/2" on the pour, with the right mixture. In my case, I am basing the 1-1/4" at the high point of the slab, as it has settled 1/4 to 3/4" lower across much of it, and of course we'd pour level. Note: no major cracking of the slab.
    Headroom is tight. With the planned 2-1/4" makeup, I will have finished ceiling height AFF of 7' 8-3/4" for most of the basement, and 7' 7" in one bedroom, with one bathroom at 7' 6-1/2". Equally notable is that several of the door headers are structural beams. So, with any increase in height, I'm cutting down 80" doors. Not the end of the world, but would like to minimize.
    After talking with my architect friend, we decide it should be OK to go up to 1-1/2" and possibly 2" thick insulation, with some sacrifices.
    I know Jaime mentioned 2-4" insulation. Do you all think that getting to 2" insulation beneath the pour, such that regardless of any ground water, my losses should be reasonable?
    @hot_rod - It would be great if the water was only present when the ditch runs. The neighbors soil tests 30' from the ditch (I'm 75' away) showed water at -7' in mid-july (2 weeks after the ditch stopped) and at -9' when tested in early october. So the water went down, but not away. They also mention a gravel/sand layer around -9', which is about 3' below the ditch. In their other test, about 100-120' from the ditch, and within 1' of grade of my house. They found no water in the 12' pit, and mineralization from prior water at about -9'. My slab is about 4' below grade.
    So, there seems to be some permanent/longer-term water there, just a bit lower. While I feel reasonably confident there's water within 6' when the ditch runs, I would guess 50/50 chance there's water within 6' in October. I'm considering boring a sample hole through the slab just to see if I can see if the soil is damp in October, but first I'll run some relative humidity tests on the slab today/tomorrow.
    These ditches were originally dug for farms. In fact, my country neighborhood (built in the 60's) used to be farm land. Some farms still use the water, but many of the shares have been sold to municipalities at this point, and they store it in a reservoir. Water rights are a massive deal here in Colorado, and certain ditches have different priorities than others, ours I think ranked like #23 or so. So regardless of if farmers still want the water, it gets shut off due to agreements.
    Other ideas by anyone, I'm all ears.
    yeah, without testing we are all guessing.
    A bore in the slab is not a bad idea Home Depot rents up to 5” or so core drills
    Have you done any Radon testing? High levels are fairly common in basements in my SLC Utah area
    That would involve some core in the slab to mitigate, it would be a good time to check that
    If the unknowns are too great, panel radiators get you about the same comfort and you don’t deal with all the slab and elevation change issues
    rossn
  • rossn
    rossn Posts: 161
    @hot_rod - yeah, I have an sds and core bit up to 2-1/2" bit but going deeper might be an issue that small. Like you suggest, I might have to rent the bigger max tool and bit. I was looking last night at some hand well drilling equipment. I even saw an auger at harbor freight that is 2" x 36", but I haven't seen yet if I could adapt that funky attachment to something I own and if I could successfully extend. I do have a camera I could send down if I can get a somewhat clean cut.
    Yes, radon galore here. I specifically tied in the new foundation drain system to a radon fan, which works great for that, but sucks some air near the sump and may cool the stem wall behind the dimple mat. I wasn't thinking about that at the time.
    I've been kicking this part of the project down the road for years now, somewhat because I could not determine how to deal with the moisture issues and not knowing what sealing the rest of the slab will lead to under my existing structural framing. Now it's time to get my house back together :)
    As to panel radiators, it is a good thought. I installed a few of the Myson decor rads upstairs in the MBR, along with some fintube under the bath.
    Last week I ran the numbers on radiant over slab vs radiators, and radiant won financially - even with the grind and epoxy of the slab and the concrete pour and having a contractor install the tubing/manifolds.
    I can still remember when we just had some baseboard and the nylon carpet + pad over the slab, and my feet literally freezing at my desk. I'm not sure radiators will address that, and based on the information coming together, think I may still need to insulate the slab with radiators. And I'd still need to level the old garage area with the floor drain slope.
    One of the killers with the radiators is I would have to rebuild the stairs, which was a long, slow process for me, though very much crafted, true, and robust to last a lifetime. I think just the framing materials to rebuild those is probably over $1000 today. I'd rather invest that in making the place comfortable.
    Well… more details would be needed.
    But.
    First, it is not so much where water stands in a borehole, although that is important — it is how saturated is the soil at the bottom of the slab. And that depends on the soil type as much as where the water stands. In very close soils, saturation doesn't get much more than a few inches above where the water stands. In loamy soils, it can easily reach six feet above the level of standing water.
    Second, if the soil is saturated at or near the slab bottom, you simply are not going to warm it up. Saturated soil is an excellent conductor of heat. Concrete (your existing slab) isn't quite as good — but a safe assumption will be that the top of the existing slab will be at — and stay at — average ground temperature pretty much regardless of what you do above it.
    Therefore, it becomes a rather simple matter to calculate how many BTUh you need to put into your radiant system to keep the floor temperature at, say 75 — and the biggest single factor in that calculation (other than the delta T) is how much insulation you have between your tubing and the top of the existing slab. Most foams have an R value of around 3.5 to 4.0 per inch. Heat loss in this application is inversely, linearly proportional to thickness and directly to delta T. The heat loss to the ground needs to be added to the heat delivered to the room.
    rossn
  • rossn
    rossn Posts: 161
    edited October 2025
    @Jamie Hall - That's fair. It's clear I need to core or cut the slab to get beneath and check the soil condition. I feel like I should be able to use a 2" auger bit attached to a long t-handle to pull out some soil increments and see how it is.
    On the inverse relationship of BTU loss to foam thickness, I was thinking it's not linearly proportional to thickness. Maybe by percent per thickness of foam, but if one doubles the thickness, doesn't the absolute BTU reduction in heat loss sees diminishing returns, only functioning on a percent of the heat passing through the outer surface of the 'first layer'?
    Tomorrow I'll drill some holes and start some slab humidity tests and core a 2-1/2" hole and see if I can determine the soil conditions below the surface.
    I recall seeing some guys water drilling a well using PVC pipe with teeth cut into it, then transitioning to steel after they broke. However, the idea might work as a simple drill, at least for the first 3' when drilling down (how deep I dug before). Then maybe a 3' auger bit to lift the dirt out in 6" increments. I did think about a strong vac attached to a small diameter pipe to suck out the dirt, but I may lose the ability to check the moisture level. I'll sleep on it and start learning some information tomorrow.
    Genuinely appreciate you sharing your knowledge here, Jamie! It's been a great help.
  • DCContrarian
    Usually the biggest issue with raising the floor is stairs, you want all the risers to be the same height and all of a sudden the bottom step is a couple inches less than the others. You then need to either cut new stringers or split the extra height over the stairs and pad each one a variable amount.
    Often, cold floors are caused by poor insulation and air sealing in the walls, cold air leaks in and settle down. Well-sealed spaces are much less stratified. That doesn't mean that insulation under the floor isn't important too, but if I'm experiencing cold toes I'd be checking the air sealing of the joist bays and the portion of the wall above ground. That will make the whole house more comfortable.
    rossn
  • rossn
    rossn Posts: 161
    edited October 2025
    @DCContrarian - yes, agreed - if I add an inch of insulation, I just need to add to each riser and glue it down, given no flooring is installed yet - I won't pass inspection if the steps don't meet IRC's 3/8" differential requirement. Going the other direction is definitely a bigger problem :) If I was going to shift plans to just using radiators, I'd have to consider rebuilding the stairs :(
    Yeah, the structure is leaky as a siv, which leads to what you described. Not to mention stem walls maybe being insulated non-continuously to R3ish. Basically they had a furring strip over the stem wall with insulation between… I think it was 3/4" fiberglass on one end and foam board on the other end. It's been framed out 4-1/2" with 2-1/2 iso across the stem wall now, except the very base, which will get mineral wool, should there be any moissture. Currently it's all gutted, and we will be doing proper air sealing and adding HRVs. That said, I think the slab was still just cold in the winter, adding to foot discomfort.
  • DCContrarian
    To the heat loss question, the heat loss to conduction through an assembly is determined by the R-value and the temperature difference between the two sides. So if you have an embedded pipe that's at 90F, the room is at 70F and the dirt below the floor is at 50F, there's a 20F difference between the pipe and the room and 40F between the pipe and the dirt. If you have the same amount of insulation above and below the pipe, you'd get twice the heat loss down as up, or two thirds of your heat would be going into the ground.
    Let's say instead you have two inches of concrete above the pipe, and two inches of foam below. The r-value of concrete varies by how dense it is, for a heated floor you want a highly conductive surface for even heating, so let's say it's a dense concrete that's R0.1 per inch, or R0.2 total. There's going to be an air film between the floor and the air in the room, that film is assumed to be about R0.5, so say R0.7 for the whole assembly. Foam is going to be R4 per inch or R8 total, no air film. So upward you've got 20F difference and R0.7, downward you've got 40F difference and R8, you get 5.7 times as much heat going up, or 85% up and 15% down.
    With only 1" of foam you get 2.8 times as much going up as down, or 74% up and 26% down.
  • Kaos
    Kaos Posts: 1,003
    Once you fix the basement air leaks and foundation insulation, the heat load drops low enough that the heated floors are not worth it. I'm in cold climate and I generally find that basement floor with something like LVL with a thicker pad is good enough.
    If you still want floor heat, you can do partial heat in section with high traffic. There you can do one of the pipe track systems over a layer of rigid which will be thinner than any concrete overpour. For the rest, go with rigid on the slab with OSB over it.
    This now gets you an overall warmer floor for much less money plus the heated areas will be extra toasty for that warm toes feel.
    hot_rod
    The equation for heat loss — which is usually an oversimplification, but in the case we are looking at here with solid contact (no air films) is quite simple: Q, the heat loss, is equal to the delta T between the two sides in our case here, the pipe (but it can be taken to be the top of the insulation under the pipe) and the soil at the bottom of the slab, divided by the R factor of the insulation layer.
    Thus if you double the thickness of the insulation, for example, the heat loss is cut in half.
    Now it is quite true that each extra inch doesn't have the same effect as the initial inch — but is still an inverse lineal proportion. The example of extra inches may be seen here: let us suppose that our assembly with one inch of insulation has a heat loss of 10 BTUh at our delta T. Now if we go to two inches, the heat loss drops to 5 BTUh. At 3 inches, it is 3.33 BTUh. And so on.
  • leonz
    leonz Posts: 1,994
    It will be a lot simpler if you hire a backhoe for an hour and dig a trench and wait to see how much water actually exists in your soil and if it is excessive just have a pit dug for an exterior sump pump.
  • rossn
    rossn Posts: 161
    edited October 2025
    Apologies for the delay - have been doing some investigation around the slab moisture, talking with a soils guy, etc. I also cored small hole in the slab. Here's what I learned:
    #1 the soil against the slab has just the slightest moisture… almost dry, not what I would call damp. That said, the slab currently breathes. Once there is a vapor barrier over the slab, I would think the soils would stay damp longer term. The soils engineer had similar thoughts, but we don't know for sure.
    #2 based on discussion with the engineer, in my area, it is really hard to know about the soil moisture levels (which can be influenced by rain) and how far down water is. Really, a coring is needed. He recommended coring and putting some perforated PVC in place, to be able to monitor. About $600-1200 for one core. Another guy, might be $1200 for 2.
    Based on prior discussion, I'm not sure it is worth doing the core because it won't change anything. It sounds, based on what you all mentioned, that I'll need insulation, and at least 2", regardless of whether I do radiators or radiant. I suppose the losses will be a little higher with radiant, due to the heat being within the subfloor sandwich. However, is the general consensus here that if I get 2" of foam down (that's really pushing it for me, so more isn't possible), my heat loss should be somewhat reasonable, even if there is water 5' down?
    @DCContrarian and @Jamie Hall - thanks for straightening me out on the heat loss - much appreciated. I was going at that wrong.
    @Kaos - your point is well made, understood and I will chew on it. If I do the insulation work along with the already planned airsealing, the space will be a lot more comfortable. Note that this basement is about 55% above grade with larger windows. I ran the $ numbers a week ago for doing radiators vs radiant, and they were pretty much neck and neck. However, that was without insulation and with wool carpet, so I will re-look at those numbers to see. If going to insulation on the slab (with radiators), then I still have to look at an epoxy vapor barrier, some leveling work (some sections don't meet the 'level' spec for certain types of flooring. I suspect it's still going to be relatively a wash on costs. I would think if they are relatively close in cost, the radiant would probably win. For me, one down side with OSB is it's not a water tolerant assembly. I've had water 3x in basements, so I'm gunshy on that front.
    @leonz - generally, yes. In my case, maybe not as easy. 1 - difficult to get a backhoe into the area, 2 - many mature trees close 3 - getting down 11' down with a backhoe means a quite big hole, and there's not much space for that. I have a sump beneath the slab - only goes down 3'. My take is that if I'm getting water flow, it is likely in a gravel/sand layer that is probably 4-10' below my slab. If water is coming in through that, it would continue to backfill anything I pump out - so efforts to remove may be futile.
    @hot_rod - a couple years ago, when I was originally planning to start this project, you suggested to me using spray foam on the slab. I checked into at the time, and the insulator who I was working with and while he didn't have experience with that use of the foam, did check into it and discuss with me. My recollection is that the foams were able to act as a very good vapor retarder, but not block enough of the vapor to meet the requirements of flooring mfg's. Now, keeping in mind my slab runs 70-98% RH, so probably different then typical applications. Are you aware of people putting down loops over the spray foam with the thin over poured slab? I'm not clear what developments have happened since then. Spray foam could possibly still be an option, but I think I'd have to put an fluid applied vapor barrier first, and then I'm unclear how well the tubing staples to the uneven surface. More importantly, I understand a slip layer is needed between the concrete and the thin poured slab due to expansion differences arising from the insulating layer. I believe foam board often acts as that slip layer. With the undulated surface of spray foam, could this be an issue with the thin slab approach over spray foam? Any developments/experience in the last two years, I'd love to hear.
  • DCContrarian
    "the soil against the slab has just the slightest moisture… almost dry, not what I would call damp. That said, the slab currently breathes. Once there is a vapor barrier over the slab, I would think the soils would stay damp longer term. "
    Where I am, the biggest challenge is keeping humidity out of basements, so you don't want the slab drying toward the finished space. Moisture doesn't in any way harm concrete, it's OK to trap the moisture in the slab.
    Having the soil under the slab damper may marginally affect the heat transfer of the soil, but you should have so much insulation in the floor that it's imperceptible. I would only worry about the moisture content of the soil if it got to the point where the soil starts to liquify and the footings sag. It sounds like you're a long way from that.
  • rossn
    rossn Posts: 161
    Thanks @DCContrarian - yes, no worries about moisture in the concrete, other than potentially leading to rot under the structural framing that sits on the slab. The absolute max I can go for insulation is 2", and that is a push. I think I was hearing above that if the soil and slab is moist, I might need to model the floor with 51F constant temp below the insulation to make sure it is reasonable
    @Kaos - I ran the numbers this weekend, and the cost difference for the insulation with OSB + radiators approach is < 10% cost difference, and that would require my labor to install all the radiators. That would save me 7/8" height and allow for better flooring choices in the theater area and more area rugs, but would ultimately probably not be a real cost savings, although I would using rads instead of heated pex directly against the foam would give a little bit more efficiency.
    I will model the 51F constant slab temp below the foam and see how bad that looks.
  • rossn
    rossn Posts: 161
    edited October 2025
    For radiant floor vs radiators, I'm getting overall heating BTU losses for radiant floors about 10% more (on the overall room losses). Is that expected?
    How much of that 10% loss (radiant floor vs radiators) typically gets recovered at the boiler with the lower temp floor system vs mid-temp radiator setup? I will have a 2 temp system.
    Per ADS, groundwater increases overall losses about 15% (2-4x if looking at slab losses, alone).
    no amount of foam under the slab can stop downward heat loss
    So the factors to know are temperature of the slab at the bottom ideally, , r-value of the insulation, and ground temperature below the slab
    At this point you know that damp soul or moving water under the slab adds to the downward loss
    So the exact number is not easy to pinpoint
    The slab may tun tun at or below room temperature if heated by FA or other non slab methods
    rossn
  • DCContrarian
    "no amount of foam under the slab can stop downward heat loss."
    This is true of any insulation, anywhere. You can't stop heat loss. But you can reduce it dramatically.
    I still maintain that the groundwater is a red herring. It's only going to be a factor if there is very little insulation; with little or no insulation the soil might otherwise warm, which would reduce heat flow somewhat. But that difference is going to be dwarfed by a reasonable amount of insulation; with two inches of foam below the floor it really doesn't matter if the dirt under it is at 45F or 55F.
    rossn
  • rossn
    rossn Posts: 161
    Thanks, guys. I'm not trying to be pedantic about no losses downward. The point I was trying to make is that it seems radiant loses a lot more heat out the slab than other forms of heat in the room. I was just being hopeful that some of those losses were countered by using a low-temp system (versus med-temp). I was just a little surprised to see the numbers.
    You all have been very helpful to me, which I appreciate; no need to continue the conversation on it.
    it all comes down to the laws of thermodynamic. The first states, simply put
    Hot travels to cold, always.
    2nd The rate at which hot travels to cold is dependent on the delta, the temperature difference between the two.
    So yes radiantly heated floor at say 80f at the slab bottom will transfer more energy than a slab at say 70 degrees or ambient temperature. There is no cheating that first law of thermodynamics.
    Without any underslab insulation, no radiant heat, I suspect the floor would be cooler than ambient a bit. Probably not 55, but probably not the same as ambient. Placing a bare hand on the slab is a good analogy. Skin temperature vs slab surface.
    Which is the main reason to put heat into the slab. Some suggest a slab at skin temperature is ideal. No heat will be pulled from you feet, no delta, no heat is added to your feet, no delta. So a neutral feel, but a comfortable space.
    I’m not sure what answer you are looking for? Cold soils conducts heat, moist soil is a better conductor than dry soil. Putting exact numbers to your exact situation is not an exact science. Whatever force keeps the soil always moist is also grabbing a portion of the heat. Based on the delta T
    The Holohan parable about cold 70. Walk down a grocery store aisle, the bread aisle maybe. with a thermometer, note the temperature. Now walk down the aisle with the refrigerated cases. What is the ambient temperature in that aisle. Near identical, but the cold glass is a radiant surface, heat from your supposedly, or hopefully, warm body travels to the cold glass, so the aisle “feels” colder.
  • rossn
    rossn Posts: 161
    Thanks, Bob. I'm looking for anything further. You all were immensely helpful to me.
  • rossn
    rossn Posts: 161
    Based on commentary here by @hot_rod and @Kaos I did look closely at just insulating the slab and using panel radiators. And with the uncertainty of conditions below the slab and my wife wanting to put out more area rugs than the at-the-edge radiant design would have probably allowed, it's looking desirable.
    Initial budget says it will actually cost us $2-5k more, much of which relates to the slab condition and prep. One thing that prevents us from just laying foam and OSB is a sunken end of the house (slopes down up to 7/8" over 6') and a former garage floor that slopes to a drain.
    This has me thinking about 1-1/2" of closed cell spray foam + min 1-3/8" concrete (no heat). This would be without tubing in the floor, but would be a water tolerant assembly, should any flooding occur (and I've had basements with water, before). Hot Rod - you had mentioned the spray foam in another thread. You also seem to have good knowledge on the concrete side. Do you think this could be a reasonable over-slab insulation+subfloor system? I notice the ccsf also absorbs more water than xps or eps. Do you have any insight as to if that could lead to curing issues on the thin slab?
    plenty if opinions on closed cell foam under ir on concrete
    The source explains pros and cons
    A fellow on you tube named Spray Jones seems knowledgeable
    https://www.greenbuildingadvisor.com/article/insulating-below-a-slab-with-closed-cell-spray-foam
  • rossn
    rossn Posts: 161
    edited November 2025
    Thanks for sharing those resources, Bob. I will check them out. I had not seen Spray Jones, and did find one concrete guy on YouTube that has done 500-1000 thin pours for radiant, so I did reach out to see if he's done any over spray foam.
  • I fear you may be associating the water level in the irrigation channel with that of the possible water level below your slab. In my experience irrigation water is precious and the trenches were typically lined with clay or bentonite to prevent water loss and reserve the flow for crops. The slab will have a high moisture content simply because it is in direct contact with the ground. It is also possible that there may not be a 6 mil vapor barrier under your slab which allows it to assimilate its moisture content with that of the local soil. Warming the area with radiant floor heat may help dissipate some of this moisture. To prevent the old slab from adding to humidity in the home I suggest adding a vapor barrier below the insulation upon which you are attaching the radiant tubing. I've heated a multitude of basements with radiant heat with no problems using this technique and they had sump-pumps that served to remove any water that came in around the foundations. A constant running sump pump would be a sign of a high water table and you do not appear to have that situation.
  • rossn
    rossn Posts: 161
    Geosman, thanks for sharing your thoughts and insights - genuinely appreciate it. You are right about water being precious, especially in the west. This ditch was dug in the 1860's; they're not lined with anything, and from my slab cuts, I do know that it is very damp soil when the ditch has run. It does appear to dry later in the year, most likely through the slab, so it's hard to know what happens when we add the VB. I also have spoken with a local geotechnical engineer, who maintains the same, so I feel that in my particular case, we are definitely seeing enhanced groundwater through a gravel and sand layer that's about 9' below grade (at least that is where it is for about 80' from my house). Like you suggest, we can be confident that the actual groundwater level is lower than the sump, whose perforations go down 24" - but that does not mean it doesn't wick moisture upwards to the slab. My best guess is that groundwater is 4-8' below the slab, with it being higher seasonally. Regardless, I can count on some enhanced losses of some amount.
    This old slab is merely concrete on compacted dirt without any capillary break, vapor barrier, or insulation.
    I agree with you on the vapor barrier at the concrete level. The biggest unknown is once the vapor barrier is in-place and the slab has gone to 100% relative humidity, what will happen to the structural framing that touches down on the slab without a capillary break. I'm convinced at this point that there's not a real solution, other than spraying the structural lumber (both the base plate and the lower ends of the studs) with a wood preservative to prevent rot and mold, but the lumber it could still hold moisture. So, fingers crossed.