Azimuth, Solar Elevation, And Solar Irradiance

desert_sasquatch
desert_sasquatch Member Posts: 135
edited September 14 in Solar

I have a DIY solar thermal project idea that has me trying to work out how hot the panel would get depending on where it is facing. In other words I'm trying to work out, say, how much a panel tilted up 45 degrees from the horizontal with azimuth of 180 (due south) would receive when the solar elevation is 78 degrees and azimuth is 177 vs when the solar elevation is 73 degrees and the azimuth is 232.

Using trigonometry I've been able to figure out how to much solar radiation loss I should expect when the angle between the sun and the panel change on one axis (ie if the panel tracked up and down but not east to west). The formula for "percent of solar irradiance compared to a perfectly perpendicular panel", as far as I know, is:

[Cosine of Angle Deviation From Perpendicular]^2 = Efficiency

Edit: On further reflection (and having checked my work by reading an article, the formula is actually just the sine of the angle of incidence. For the link see my post below.

However I'm getting a bit stuck figuring out how to make the math work in three dimensions. In other words how do I determine how much sunlight a panel a x angle to the sky and at y azimuth will receive at each moment of the day? (I'm not looking for total daily irradience, that doesn't help me here. I need to know how the irradiance at noon compares to the irradiance at 1:00 et on the same sunny day). A formula would be great, but I'll take a calculator if someone has one….

Thanks in advance to anyone who can help!

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,038

    Interesting query. Does anything in the engineering toolbox help with that? Here's the link:

    https://www.engineeringtoolbox.com/

    Just type in Solar Radiation in the search bar.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    desert_sasquatch
  • Jamie Hall
    Jamie Hall Member Posts: 26,357

    What you need is the angle between the perpendicular to the panel and the sun. Given that angle — which, of course, changes with the time of day and the season — then the effective area of the panel is equal the the gross area time the cosine of that angle (not the cosine squared). Using that effective area you can calculate the gross solar radiation.

    A useful reference for the math for the angle to the sun is here;

    zenith-angle-calculation-Guoyuan-Li.pdf

    Now.. That is not.. Repeat NOT related the the efficiency of a solar collector. The efficiency of the collector is, simply, the usable power output from the collecter divided by the net effective area of the panel and the instantaneous solar power — which, of course, varies with atmospheric condition. This efficiency varies with the design of the collector, and may — or may not — also be influenced by the angle between the perpendicular and the direction to the sun. This may be closely related to the cosine of that angle, in the case of collectors with flat glass surfaces or some (but not all) types of photovoltaic arrays. Or it may not…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    desert_sasquatch
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,951

    Hi, Being more of a hands-on type, I'd be tempted to get or build a collector that fits what you're looking for and set it up. Data-log temperatures and you'll know with more certainty than any calculation can give you, just how well it performs. Feed it with warmer and warmer water to see how performance drops off. You'll be able to graph it, and get a clear idea of what sort of temps you can expect from a system using that collector. It certainly is some work to make happen, but you'll get results you can trust.

    Yours, Larry

    desert_sasquatch
  • hot_rod
    hot_rod Member Posts: 25,650

    you need a solar simulation software to make it quick and easy to do those calculations and comparisons.

    RET Screen out if Canada had a powerful, free program with solar calcs

    Possibly some freebie at the NREL site also

    IMG_1002.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    desert_sasquatch
  • desert_sasquatch
    desert_sasquatch Member Posts: 135
    edited September 14

    Thanks everyone.

    Thanks Hot Rod, I'll check out RETScreen.

    FWIW I did figure out this trigonometry problem—it has been a while since I used three dimensional graphs or the law of cosines… probably half my life… but I did get results that I think are right by plotting two points on a 3D graph, one for the direction of the sun, one for an angle perpendicular to the face of a flat solar panel. Both points were an arbitrary one unit from (0,0,0), which let me figure out the "distance" between those points, which let me figure out the angle between those two lines.

    Also I found a website that explained how to determine the intensity as a function of the incidence—and I had screwed up the math before, so I'll edit that post to show I was wrong there. But the equation seems to just be sin(angle of incidence).

    (For anyone reading this who doesn't know, angle of incidence is the angle that the sun makes to the panel, so 90 degrees is perfectly perpendicular and 0 means you won't get any sun.)

    Of course as yall mentioned there is also the incident angle modifier, though I'm having a tricky time coming up with information on how that works with opaque surfaces, all the info seems to be about how it happens with the glass on solar panels. But assuming it works similarly for a roof, it seems like it doesn't really have much impact until the incident angle is something like 70 degrees, at which point you're already not getting much sunlight anyhow. I do recall learning (probably from someone here 😉) that some special glass is made to be bumpy so that it can avoid this problem to some degree…. And was this part of what you were referring to @Jamie Hall? But anyhow, since my concern for now is how hot the panel gets when the angle of incidence is around 45 or so at most, it seems like mostly a non-issue.

    Aaanyhow, I think I have my answer and will start a new thread on my possibly-still-misguided idea.

  • desert_sasquatch
    desert_sasquatch Member Posts: 135

    @Larry Weingarten

    I agree, making a tiny version of what I want to do would be important, eventually. Alas, I'm kind of limited on space and even tools at the moment, so it'll need to be theoretical until I can get the stuff together to rig it up. Also, for better or for worse, I kinda love the math part. And I do prefer to plan things out as much as possible before prototyping…

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,951

    Hi @desert_sasquatch , I'm pretty sure this tidbit has nothing to do with anything, but I've been playing with low efficiency collectors for DHW. Some benefits are: it eliminates the need for overheat protection, greatly reduces cost, can be homemade, and has freeze resistance. With inefficient collectors, I can greatly oversize the collection area with no real downside. This allows quick reheating in partly sunny conditions too. I've built systems that do 90% of the DHW load at less than half the cost of conventional solar thermal… So, I'm really curious about what you're up to! 😎

    Yours, Larry

  • desert_sasquatch
    desert_sasquatch Member Posts: 135

    @Larry Weingarten You're right on target, actually :). Are you the guy who suggesting making like 3-foot spirals of black garden pipe to put on the roof? That was kind of the inspiration for what I'm thinking of doing, which is put PEX under a dark metal roof. I'll leave the link to the thread below, I'd love your thoughts. I seem to recall you used black garden pipe and if that's you I'm curious how that plan would compare to sticking PEX under the roof….

  • desert_sasquatch
    desert_sasquatch Member Posts: 135

    Here's the link to the thread with my maybe-bonkers idea for cheap solar thermal by putting PEX under a dark, sloped metal roof.

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,951

    Hi @desert_sasquatch , I likely am that guy making coils 😉 Here's an article in the help center: https://www.heatinghelp.com/systems-help-center/another-solar-myth-bites-the-dust/ More recently, I used with this concept to help a local high school win a sustainability competition. https://www.pbs.org/newshour/brief/518687/rancho-cielo We built a coil using 3/4" NSF rated black poly pipe about ten feet in diameter, and used it as a shade structure over a door. Works!

    Yours, Larry

    IMG_8407.JPG
  • hot_rod
    hot_rod Member Posts: 25,650

    It seems like if you have the ability to store the energy in some thermal tank, or thermal mass, you would want to build the most, not least efficient collector?

    Grab as much solar energy as you can while the sun is out? Store it for evening or no sun days. The cost to run an efficient collector is no more than an inefficient one?

    Drainback systems have been around for a long time, they handle both overheating and freezing potential by simply turning off the pump.

    I still don't see a load number for the project? How much energy would you ideally collect to cover heating and dhw loads. Maybe calculated on a design day.

    Depending on your fluid temperatures you can get into the 40% efficiency with a typical flat plate collector, even homemade ones.

    Why spend time and money to purposely build a 20% or less efficient array, for the same or more money and more complication?

    While an unglazed pool type collector can reach near 90% efficiency in warm months, the black line on the graph below, in the winter when you need heat you are looking at dismal performance.

    Screenshot 2025-09-16 at 7.41.51 AM.png Screenshot 2025-09-16 at 7.49.54 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Member Posts: 1,239

    @hot_rod "It seems like if you have the ability to store the energy in some thermal tank, or thermal mass, you would want to build the most, not least efficient collector?"

    On site thermal storage for more than about a day rarely pencils out.

    The graphs you post show an important limitation of solar collectors — the colder it is outside, the lower the efficiency. So in the summer:

    • The days are longer, so you get more sunlight
    • You need less heating
    • The air is warmer, so collectors work more efficiently

    I ran the numbers years ago for my home, Washington, DC. Even if I angle the collector to maximize collection on the shortest days of the year, I still would collect three times as much heat per day in June as in December. In June my only heating load is domestic hot water. January is my coldest month, and in January my heating load is over eight times my hot water load.

    If I size a collector to provide 100% of my load on a summer day, on a January day it provides 3% of the load. If i size it to provide 100% of the load on a January day, on a July day it's 35 times oversized.

    Do the math for your climate, in my climate there's no way around it.

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,951

    Hi, I cannot disagree with @hot_rod on most points. Still as Martin Holladay said, "solar thermal is dead". This is largely because we weren't able to keep it simple and inexpensive. This coil type, inefficient system isn't for all climates… no one system type is always superior. But for temperate areas, it has demonstrated for many years now that it works nicely and performs better than more expensive systems, with less need for upkeep and at a far lower cost. I did my first solar thermal system in 1978. Rethinking solar was a mind bender for me, but I think we arrived at something useful.

    Yours, Larry

  • Jamie Hall
    Jamie Hall Member Posts: 26,357

    I tend to agree, @Larry Weingarten — and I also agree with the Martin Holliday quote you mentioned. Not, however for any inherent problem, but because utillising solar for domestic space heating or cooling (and yes, properly designed in some climates but not all, essentially passive solar systems can be used for space cooling) requires adapting to the specific site and climate, and that is just too much trouble for the architects and building owners. Further, there is a rather strong fixation on having some sort of collector with some sort of complicated plumbing and tanks or it isn't solar — and that isn't true either.

    (Fun fact: the Persians and Nabateans and Israelites were cooling their civic buildings and palaces and some houses and were making ice to cool their beverages… 2500 years ago… with passive structures…) (Have you ever visited some of the cliff dwellings in the southwest, or Chaco Canyon?)

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 25,650

    Use it or lose it has always been the solar thermal motto

    If the OP wants a system to supply a portion of the heating load. Yes it may be oversized for summer dhw loads, unless he has a need got a lot of thermal or dhw in the summer.

    The solar pros in NM sized for around a 30% fraction of the heating load to keep the array size reasonable, affordable, and and less dump

    I think we have gone way beyond “penciling out” with Sasquatch

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • DCContrarian
    DCContrarian Member Posts: 1,239

    @Jamie Hall : "Have you ever visited some of the cliff dwellings in the southwest?"

    Last year I visited Taos Pueblo. It was February, a pretty raw day, not super cold but mid-30's, sunless and a stiff breeze. Just about every building in the place was downright miserable to be in. The ones without fires were bone-chilling, even the ones with fires were cold and smoky. The only building in the place that was bearable was the church, which had a propane heater.

  • DCContrarian
    DCContrarian Member Posts: 1,239

    @Jamie Hall : "Fun fact: the Persians and Nabateans and Israelites were cooling their civic buildings and palaces and some houses and were making ice to cool their beverages… 2500 years ago… with passive structures…"

    The coldest you can get with nighttime radiative cooling is the dew point of the outdoor air. That's why you get dew at night. If the dew point is below freezing, you can get frost even when the air temperature is above freezing. If you live in a climate where the dew point doesn't get that low, you don't get a lot of evaporative cooling.

    Fun fact: moonlight — sunlight reflected by the moon — can be enough to overcome radiative cooling and prevent the formation of dew or frost.

  • Jamie Hall
    Jamie Hall Member Posts: 26,357

    Yes — the cooling is dependent on the dew point. Having said that, I remember one summer — I think it was July — camping in southwest New Mexico… and ice on the water buckets in the morning!

    I haven't been at Taos in years, but I do vaguely remember it as being rather dank. Acoma doesn't seem to be — but Acoma is a lot lower in elevation, and has NO shade!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • desert_sasquatch
    desert_sasquatch Member Posts: 135

    Oh cool, thanks! I remember reading this article before but am rereading it now… I think my main question today is: How long do these collectors last? Doesn't even UV-treated plastic usually break down when exposed to constant sun for several years?

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,951

    Hi, About longevity, I used coils after this type of system had been under test by the maker for sixteen years, and undergone multiple freezes along with good sun in San Jose, CA. suffering no apparent damage. This is NSF rated black poly tube which is thicker wall than some of the irrigation tubing. Also, I've read that if you can find tubing with 2% carbon black in it, the sun doesn't degrade it an any appreciable rate. The system described in the article has now been in service about 11 years and is doing fine, except some of the glazing got blown off once. One more tidbit is that I've never seen black poly tubing that was brittle and fractured, while I have had to replace UV damaged PEX. I haven't tested coils under a hard freeze, or subjected them to temps over 170F. So, aside from extreme conditions, it seems pretty durable stuff.

    Yours, Larry