Your thoughts and opinions please
RayWohlfarth
RayWohlfarth Member Posts: 1,951
I was asked to do a 3 1/2 hour class in Pittsburgh next month. They would like a hybrid class, one hour on hydronic, one on low pressure steam and one on reading boiler wiring diagrams. I put together an outline and would love your feedback on what Im including. What would you or your techs want to learn? Thanks so much for your thoughts on this.
Ray
Hybrid Class Steam Hydronic Electric
 Class Outline: Top Ten Problems in Hydronic, Steam, and Wiring Diagrams
Introduction (5 minutes)
Section 1: Hydronic Heating Systems (60 minutes)
Top Errors & Problems
  1. Air in the system – symptoms, prevention, removal
  2. Improper circulator location (pumping toward vs. away from the expansion tank)
  3. Wrong circulator sizing – sizing a circulator
  4. Insufficient expansion tank capacity – waterlogging, relief valve discharge
  5. Mixing glycol incorrectly – concentration, leaks, efficiency loss
  6. Lack of water treatment – corrosion, scale, oxygen ingress
  7. Undersized piping – high velocity noise, poor flow distribution
  8. Boiler system controls – residential & commercial PTA, control, limit, low water
  9. ystem balancing – hot/cold zones, valve adjustments,
  10. Neglected maintenance – dirty strainers, plugged air vents, circulator wear
  11. What you must do before connecting a new boiler to old pipes – flushing system, checking flue, chimney
Break
Section 2: Low-Pressure Steam Heating Systems (60 minutes)
  1. Poor or missing main venting – long warmup times, uneven heating
  2. Radiator vent problems – stuck open/closed, mismatched sizes
  3. Water level issues – surging, flooding, dry firing risks
  4. Improper near-boiler piping – header height, equalizer, carryover
  5. Neglected low-water cutoffs – blowdown frequency, failures cause accidents
  6. Condensate return issues – leaks, hammer, waterlogged returns
  7. Incorrect pressure settings – high pressure wastes fuel, short-cycles
  8. Oversized boilers – short cycling, fuel waste, wet steam
  9. Dirty boiler water – oils, sludge, need for skimming/flushing
  10. Ignoring insulation – bare pipes = wasted energy & poor balance
  11. Water Hammer – why are the pipes banging
Break
Section 3: Reading Wiring Diagrams (60 minutes)
  1. Confusing line vs. low-voltage circuits
  2. Misidentifying series vs. parallel wiring
  3. Not following electric flow (power source → switch → load → neutral)
  4. Skipping safety switches – high limit, LWCO, rollout switches
  5. Misreading symbols – pump, transformer, contactor, relay coil
  6. Assuming color coding = function (colors vary by manufacturer)
  7. Overlooking common/neutral connections
  8. Not verifying with a meter – trusting the drawing only
  9. Failing to read legend or notes on the print
  10. Troubleshooting blindly – not breaking the circuit into sections
Wrap-Up & Q&A (10 minutes)
Ray Wohlfarth
Boiler Lessons
    EdTheHeaterMan Member Posts: 11,982
    edited August 2025
    Wow That looks pretty comprehensive. Are you going to be able to squeeze all that into one hour each? You man need to look at some of the importance of each item and be prepared to glaze over some of them as you watch the clock in order to cover the important points.
    When I did my one day seminars on Hydronics, I had a 4 minute blurb on steam boilers where I used one power point slide to touch on important basics, then told the mechanics in the class to put their hands in their pockets and step back and call someone that knows about steam.
    I also stopped my presentation in the middle of discussing safety devices like high limits, flame safety controls, and relief valves. I had three slides to go over the importance of "Operating" the relief valve. I had a blow up of the yellow tor green tag that is usually torn off, that states: "YOU MUST OPERATE THE RELIEF VALVE ANNUALLY" and highlighted those words and zoomed in on them. Dan H taught me that one. Then I asked about what does a maintenance visit include?, and why the mechanics don't operate PR valves as part of the maintenance? If the valve fails, you have a sale for a new valve if you present it properly, and doesn't your boss like it when you sell stuff over and above the loss leader maintenance  price?  Aren’t we in the business to replace defective parts?
    Larry Weingarten
    HVACNUT Member Posts: 7,381
    I think you've got all the major topics covered. But what if someone has a question? There's always questions. And if you want all that information to sink in, those questions need time for answers. From what you're covering, I would think 6 hours minimum. You could probably go deeper with 8 hours and still not be boring.
    This class is for service techs and installers? All levels?
  • ScottSecor
    ScottSecor Member Posts: 1,026
    edited August 2025
    Ray, I agree with the comments above.
    I am being brutally honest here, not trying to be disrespectful.
    Do you want to listen to yourself talk, or do you want to teach. What I am trying to say is, let it sink in. Give the students time to respond. Reduce the amount of information you are trying to fit into a few hours.
    Ask the class for responses to your questions to judge if they are picking up what you are putting down.
    For example, you are gong to cover sizing a circulator pump in what, about four minutes? I am amazed at the amount of people in the trade that have no idea how to size a circulator. This includes service techs, installers, supply house "designers", and even some reps. I think you could spend an hour easily just on on sizing and identifying pumps.
    With regard to electrical troubleshooting, keep it simple. Think of the hundreds or thousands of no heat calls you have been on. Only focus on the the common problems, not the obscure with such a short time frame. Start with simple hand drawn line diagrams, show the people how a simple circuit works. Use water, valves and pipes as examples. Then work your way up to more complicated examples based on the response you get.
    I am thinking back to Dan Holohan's early seminar days. He made it simple, fun, had props, and spoke in a language that most of us understood. Everyone I spoke to after one of Dan's seminars learned something, most learned a lot. For me, I learned plenty and I gained confidence in what I was unsure of.
    Hopefully your students will learn something and ask plenty of questions.
    Alan (California Radiant) ForbesEdTheHeaterManethicalpaul
  • HydronicMike
    HydronicMike Member Posts: 317
    edited August 2025
    I didn’t see anything (unless I missed it), about proper sizing and problems with oversizing.
    Honestly it could (should) be an 8 hour class.
    EBEBRATT-Ed Member Posts: 20,051
    Could be 8 hrs on steam, 8 hours on water and 8 on electrical but that's not what the customer wants.
    Depends on the knowledge level of the students.
    If they ask a lot of questions you may run out of time.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,695
    What Scott said, and he said it better than I ever could. Thanks Scott.
    Retired and loving it.
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,502
    Your curriculum is excellent for a well seasoned person with years of experience as a brush up and review...A full day class, no less. It's a pretty good bet, the class experience will vary greatly. Could it be that this is the client's wish list? Cover all bases AND in 3.5 hours?
    Just covering all those points, without anyone asking a single question is rough. I would run my concerns by the client, hopefully he will modify accordingly. All salient points from the guys. Mad Dog
    CLamb
  • leonz
    leonz Member Posts: 1,799
    Speaking as a homeowner,
    I would add this to items number one and item number 4.
    Item no. 1a; how the steel compression increases expansion tank capacity at a lower cost uses smaller piping and improves air removal with the airtrol valve if an air scoop is used or not and how it works silently and how it will outlast every boiler installed under it as long as it is properly installed.
    Item no. 4a; how the steel compression tank eliminates automatic water feeders, automatic air vents and the problems with them leaking and ruptured bladders and the resulting water logging and the loss of the point of pressure change.
    hot_rod Member Posts: 27,262
    it is a tough go to keep a crowd for more than 1/2 day, even with two breaks
    Id pick 4 topics for a 1/2 day session, leaving time for discussion
    Mad Dog_2
  • RayWohlfarth
    First of all Thanks to everyone. I have been fighting with this as each topic could be 8 hours or more. The customer was thinking of a quick thing about what to look for on each type system. For example, what's the system pressure, delta t on a hydronic system Near boiler piping and boiler pressure on a steam I guess they were hoping I could do the matrix thing and just upload knowledge. Back to the drawing board. You guys are awesome Thanks
    Ray Wohlfarth
    Boiler Lessons
  • GGross
    GGross Member Posts: 1,829
    A lot of these hydro topics can be sort of breezed through to fit in an hour but I do worry that pump sizing, pipe sizing, and expansion tank sizing may raise so many questions that these topics dominate the hydro hour. I might condense them all into one topic and move them toward the end, and print some cheat sheets for these topics so you don't need to get too deep, each one could be an hour in itself give or take. If I were planning to teach to the service techs I would avoid sizing topics personally, and focus on the things I want service techs to do better on the jobs I visit, If I were teaching owner operators, or designers I would be happy to get in the weeds of sizing topics, thats where sizing gets the most use anyway.
    Personally I think you could get through all these topics in the allotted time, I just might condense a few subjects in case you have a good audience that is asking questions. Im sure planning for 3.5 hours you figure it will actually be about 4 though, I would definitely allow enough time for about 10 minute of Q&A in each section if needed in addition to the break time
    mattmia2 Member Posts: 16,357
    You need to figure out what level your audience is at. I suspect it is mixed which will make touching on all that in such a short time really hard.
    I think the only way you have a chance of covering all that in a couple hours is by describing how a hot water system works and how a steam system works and covering all those points in your description.
    I would add one thing to @ScottSecor's comment: After you hone in on your presentation, Practice in front of the mirror with the stop watch to see if it fits! 45 minutes in front of the mirror = 1 hour in the classroom.
    I'd give them TLAOSH and Modern Hydronic Heating and Idronics as things to look at for more information too.
    What @Ironman said.
    Unfortunately, the culture today is to just Google the answer.
    Thats the reason I quit teaching at the union hall 6 years ago.
    They act like if they can learn it quick its ok,
    If it takes time its not worth it.
    Mad Dog_2Ironman
  • jumper
    jumper Member Posts: 2,521
    In addition to air in HHW I'd address proper pressure.
    Defeating safeties is another important issue that ought to be emphasized.