high humidity in my house
Comments
-
10 on and 50 off is your issue. Not enough run time to drop the RH.
0 -
Is this the HRV or the AC? Those're fine times for an HRV, but not for the AC.
Also, heat recovery (HRV) or energy recovery (ERV)?
0 -
Good question.
0 -
outdoor temp and humidity depends on time of day but the low is 13 f and high would be 90f
and rh is anywhere from 50% to 80%.
0 -
Let me clarify the question.
Ventilation will only reduce the humidity indoors if the absolute moisture content of the outside air is lower than the moisture content of the inside air. If the opposite is true, ventilation will increase the humidity indoors.
Relative humidity, as it names implies, is not a measure of absolute moisture content, it's a temperature-dependent measure. The easiest measure to use is dew point. So ventilation only helps reduce humidity when the dew point outside is lower than the dew point inside. In most of the US, in weather where you would be running air conditioning, the outdoor dew point is higher than the indoor dew point.
The reason I asked about the outdoor conditions is that dew point can be calculated from temperature and humidity. What matters is not the range over the course of the year, but at the instant you're running the ventilation.
0 -
is your system cycling off and on. How long does a cycle run in your system. At a 69 degree return air temperature I don't know how much humidity you expect to remove if your system is cycling off. How low do you set your thermostat. if I was to guess you might have an over-sized system which is great at lowering sensible heat but not much latent heat, which is where all your dehumidification happens.
0 -
69 return if the unit is cycling on temp too much it will never lower RH enough. You may need reheat but that is expensive to run a bigger 9thicker coil is better.
I asked this before: With the water and air temps you have it this coil dumping a lot of water? It should be, and is it dumping the water outside the house?
0 -
clarify what's running 10 and 50, the AC needs to be 50 on, and maybe 10 off, to dehumidify,
8 systems running off the chillers, sounds over sized, which is the worst thing you can do with AC / Dehumidification, how big is the place?
this seems to be an "Engineered" system, with bells and whistles, is there by chance a HUMIDIFIER for the winter season? and is it shut off?
known to beat dead horses0 -
In my experience I find that if HRV vents are at ground level (say if the HRV is in a basement) all they are doing in the summer is bringing in high humidity ground level humidity that defeats the AC system. Where I've found such systems I've asked the customers to turn off their HRVs anytime the outdoor temperature is above 50 degrees and to use them only when needed and only for as long as needed. They are intended to help control humidity and provide some heat exchange for fresh air make-up. However, in regions with high summer humidity they can easily over-ride conventional AC equipment and introduce high humidity air 24/7 if left running.
0 -
HRV’s have no way of lowering RH. If it’s raining and cool out the indoor RH will go up
A whole house dehumidifier with outside air hookup is a much better option.
0 -
I think that where people get confused is that HRVs — or air conditioners without condensation, or shade, or whatever — do not change the actual moisture content of a volume of air — measured most conveniently by the dew point. Relative humidity is the relationship between the dew point — at which temperature the air mass holds as much moisture as it can without condensing — and the sensible air temperature, as measured by a normal thermometer. If you lower the sensible temperature, the relative humidity increases. Raise it, and the relative humidity decreases.
The only way you can lower the relative humidity at a given sensible temperature is to cool the air enough to lower it below the dew point, at which some of the moisture will condense out, and then warm it back up to where you want it.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 999 Plumbing
- 6.3K Radiant Heating
- 391 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 45 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements