Co-op in Brooklyn looking for steam consultant, 120 unit, single pipe, 1950s building
jgurin
jgurin Member Posts: 2
Hello -
I'm newly elected to my co-op board and would like to hire a company for survey, analysis, and retro-commissioning of our steam system, to make some short term and long term work recommendations. Our building is 6 stories, 120 units, 115,000 SF, built around 1954. Our boiler I believe is from 1985. We have one pipe steam with fin-tube elements.
I would like to be able to present some possible improvements, such as installing thermostatic vents, fixing leaks, re-pitching, reflectors, etc. I would also like to improve our preventative maintenance, to see if we can do any testing to anticipate leaks, videoscope, remove rest, etc.
Long-term we will have to comply with LL97, but I am not eager to replace our system with split units. I would hope to plan for something like a an air source heat pump to produce high pressure hot water, but I don't know how feasible that technology is, or how long we can wait.
Could anyone recommend some consultants local to Brooklyn, NYC, or LI?
If it helps, I am a registered architect and have a decade of experience in building restoration, but mostly envelope work. So I'm very interested in buildings but not well-versed in steam.
Thanks,
Jacob
Mad Dog_2
    ethicalpaul Member Posts: 8,958
    Contact @JohnNY
    PC7060jgurin
    mattmia2 Member Posts: 17,760
    Also @EzzyT @clammy possibly @Mad Dog_2 (not sure if that is something he does) and a couple others.
    PC7060jgurinMad Dog_2
  • JohnNY
    JohnNY Member Posts: 3,406
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Steamhead Member Posts: 18,771
    Consulting
    mattmia2PC7060jgurin
  • ARobertson13
    ARobertson13 Member Posts: 152
    edited July 2025
    Those buildings to which local Law 97 applies have a real challenge. My Coop is exempt at around 20,000 sq ft. I would advise any Coop board that is in a situation similar to jgurin to take time and learn as much as you can about your building, steam heating systems and associated technologies as possible. Then make decide what you want to do according to your budget. Please note that the legislators make up these requirements but they exempt the City owned buildings. There is a lot of talk about using electric only. I can state from experience, we have real power grid issues in this City. Currently in Williamsburg my location, the voltage will drop from 117 in the morning to 108 without a load. This is before Con Ed issued reductions. Last week the voltage was so low after Con ed reductions my oil burner would not turn on. I had to change electrical connections to a line with a lower load.
    9326yssh
  • mattmich
    mattmich Member Posts: 227
    » drop from 117 in the morning to 108 without a load.
    Gah! That's third-world level.
    As my old boss was fond of saying, "The laws of physics are strictly enforced."
    Politics is not a good way to make energy policy. One day, electricity is the answer to everything, and fossil fuel = bad, then it's good again, same with wind and solar, just 180 degrees out of phase.
    It's a complex game. Electricity is great, but it has to come from somewhere. Renewables are fantastic, but they require a stable infrastructure that can smooth out the dips and valleys.
    Gas is a great way to heat, because it's highly efficient and works down to arbitrarily cold temperatures. Heat pumps are good but at 5 F you'd be more efficient with gas. And when it's 5 F outside, most of your electricity will come from burning gas, but half the input energy is lost between the gas turbine and the wall outlet.
    What we need is an intelligent mix, not rigid rules based on the doctrine du jour.
    I'm not a fan of the present administration but I agree with energy secretary Chris Wright, who basically says, We Need It All.
    9326ysshjgurinBobC
    how much gas is lost between the well and the burner on your furnace/boiler?
  • jgurin
    I agree! City agencies are also blindly pursuing 100% electrified heating in some buildings to meet LL97 goals, sometimes simply because (of politics) there is funding for new split systems and no funding for maintenance of existing steam systems. I think there is a lot of improvement to be made to building envelopes first, and maybe eventually our goal can be 90-10 or 80-20 gas-electric, which would be a massive improvement already, but 100% with no backup seems like a recipe for a couple months every year of low efficiency, high bills, and burst pipes…
    9326ysshdabrakeman
    EBEBRATT-Ed Member Posts: 20,717
    They are out of their minds. The grid is borderline as it is . More electrical load without improving the grid is just nuts.
    From my experience when you get down around 108ish volts things stop working. Voltage is suppose to be within 10% of the equipment name plate. 120v which most things are rated at-10%=108
    PeteA
    let’s hopefully not base our opinion about the entire grid on one person’s reported voltage measured one day
    At my house, the standing voltage gets down to 100 during a heat wave, like we're experiencing now. The local grid just can't keep up.
    Consulting
    which of your appliances failed?
    More solar capacity might be in order
    for profit utilities aren't going to do anything to maintain their system unless someone makes them. there is significant investment required to fix the natural gas infrastructure too.
  • ARobertson13
    To All, there is something you should know about Electric utilities that engineers know. When the utilities do a 8% power reduction, they do it not for you. They do it so that the compressors in your AC units will not work. Only the fans will come on. Reducing load to sections of the grid. This will protect their equipment and prevent overloads and automatic disconnection. The utilities have a short time [less than a second] to correct an overload or a shift in frequency caused by high loading. I have gotten around this by using an AVR automatic voltage regulator. When I replace my burner this fall, I will connect one to it.
    PeteA
    Jamie Hall Member Posts: 27,647
    Well now. There is a reason for load shedding when the voltage (or frequency) sags, but it isn't to spike the customers. It's to protect the utility's generating and switchgear equipment — and to try and protect the entire grid from collapsing. I agree that having consumer equipment turn off or fail to start is rather a bore from the standpoint of the consumer. But may I humbly point out that having some major piece of generating equipment or switchgear fail (and yes, today that includes the oddly delicate equipment which allows wind and solar to connect) is a bit more inconvenient for lot more people… and a grid failure, such as the recent one in Spain (they're still trying to figure out exactly what did happen) which might necessitate a black start may take days to recover from.
    PC7060PeteA
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,702
    It's $$$ well spent. Mad Dog
  • Mad Dog_2
    Thank you Steamhead and MattMia. Appreciate the kind words. Mad Dog
    pecmsg Member Posts: 7,380
    I'd like to see documents showing that 8%
    Here 10% + or - of rated voltage. Motors also fall into that 10% + or -
  • ARobertson13
    edited July 2025
    Jamie, I did not say it was to spike the customer. I said it was not for you the customer. The main goal of the utilities is to protect their equipment. As for the situation in Spain, They and any person with a good understanding of power grids knows what happened. They just did not admit that they did not know what they were doing. Your power network cannot rely on a high percentage solar and or wind energy plants mixed in with coal, diesel or hydro turbines. If they do when there is a sudden drop of power because of cloud cover, wind velocity or load change, you will have chain reaction disconnects. Why, Because gas, oil powered and hydro powered systems have centrally located large turbines. Solar and wind systems do not. The massive size of the turbines spinning will have inertia and temporarily compensate for any sudden changes in the grid so they can be corrected by automated systems. Politics in Spain [the push for solar and wind power] led to their situation. How can you not know what happed days later, with an automated and fully monitored system?. Getting back on the subject, those of you who have local law 97 requirements should do all you can to optimize your steam systems and think twice before playing games with these heat pump alternatives. Heat pumps have compressors too and the reliability and cost of these systems must be determined. The price of electricity is also an issue. Coop managers and Directors: Do your home work
    mattmia2clammy
  • ARobertson13
    edited July 2025
    To All, you do not need documents to know that an 8 percent reduction will cause AC units and other equipment to to fail. Ask the people in my community. Just think about it. If you have a normal reduction in voltage that occurs during the summer, lets say just 4 volts, then you add a reduction of 8 percent, which is about 9 volts. What do you have?
    mattmia2clammyPeteA
    The latest on Spain which I've seen — and I've not seen a full engineering analysis of it — is that a large solar array dropped out, and there was a frequency instability as a result. That tripped a good bit of other generation off, and there wasn't enough spinning reserve to stabilise the system.
    I'll wait a few months for the full analysis…
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,630
    FWIW, my go to electrician (a master of his trade), told me that significant voltage reductions are common during high demand periods, and that there is often significant equipment damage. This is in the queens and Nassau County area. New York. He obviously has no ax to grind. Presumably, electrification is good for the electricians.
    PeteA
  • mattmich
    » let’s hopefully not base our opinion about the entire grid on one person’s reported voltage measured one day
    Agreed.
    Before this gets shut down for thread drift, let me pass this along: my cousin runs a large municipal power plant in the town of Mainz, Germany, that also provides hot water for heating… overall a highly efficient setup. From him I have the value of 60% efficiency for a modern gas turbine with 400 C at one end and liquid water at the other, just like we're using collapsing steam to pull heat into radiators — see, this is on-topic after all.
    The German grid is more complex than the American one and it's networked with other countries… Germany just has more neighbors than the U.S. does, obviously. They are buying nuclear-generated electricity from France, which helps with stability. The grid is under huge stress, largely from having to splice in renewables and doing so preferentially, i.o.w. when the wind and solar rolls on, it MUST be put on the grid. Traditional power plants — mostly fossil-fuel based, nuclear got shut down after Fukushima — have to manage the stability of the grid while having reduced revenenue. I heard a talk by a retired engineer who showed a graph showing interventions necessary to keep the phase steady — he said, we used to have to do these once every few weeks.. now it's constant, dozens of times a day. Inasmuch as these are technical matters, they can be handled, but it requires investment to go along with new rules.
    Transitioning to renewables is a wonderful and worthwhile project, but it works better when it's driven by engineering than politics, especially when the rules get crated by those trained in legal matters. It'd be a shame if wind & solar got a bad name because of poor implementation…remember what General Motors did to Diesel engines. Perception does become reality.
    I'll stop now.
  • mattmich
    @ARobertson13 et al:
    Remember that power = voltage x current, or voltage squared divided by resistance.
    Talking round numbers, a ten percent drop in voltage equals a twenty percent power drop. It's a bigger deal than it seems at first.
  • ARobertson13
    To All,
    This is not an opinion based on one day. Yesterday my burner did not start again [6th time this summer]. I don't care about other power grids. As for New York City and my area, You can go on the local utilty's web site and look at the power outages and voltage reductions that they list. They are required by law to notify you in New York for reductions of 8 percent. My location in Williamsburg of the past 5 years has had an increase in high rise buildings and residential housing and associated loading . I had to call the company that services my steam boiler 3 times in the last heating season at a cost of $1,800 because of this problem and the damage caused. That is why I mentioned people in my situation install the AVR in their steam systems to prevent this. The shareholders in a Coop who spend $500,00 for their units do not want to hear about power grids or even local law 97 compliance. They want the problem solved, preventative measures taken and their maintenance cost foe their steam system kept low.
    misterheat
  • dabrakeman
    dabrakeman Member Posts: 1,021
    Well, sounds like coop hired a good man and the OP here is doing the right thing getting with this forum to get guidance on performance improvements for the steam system.
    Long Beach Ed
    Induction motors with conventional controls will not shut down with an 8% voltage drop. They will draw more current and run hotter. Depending on the load and service factor they may trip out an overload and shut down after a while. It may shorten their life but 8% isn't going to make them shut down in most cases.
    pecmsg
  • ARobertson13
    mattmia2, if you read what I stated, you will see that these motors and controls will not operate under the conditions I stated. Why do you think the power companies do this? They do not want higher power consuming devices and units to operate. In many cases, if the motor or compressor is not already in operation, it will not start. How many motors do you think will operate below 100 volts? When the voltage is below a certain level, the high current draw will trip a breaker or fail in the case of my burner fail to generate proper voltage for the electrode causing the burner to shut down. They do not want motors and other equipment to draw more current because the power draw will be the same. They want certain equipment not to work at all. They know what there doing. They just do not want to say it.
    Fighting anecdote with anecdote, here in North Jersey it's 95F at 2pm and the voltage in my outlets is 121.9
    The grid is fine, updated, and constantly being improved.
    pecmsgmattmia2old_diy_guy
    the eight volts you stated, of is that on 110, 220, 460, 880, single phase, three phase?
  • ARobertson13
    To all, This is the last I will comment on this power issue not related to steam. Please pardon me if I seem a bit frustrated. Among my many duties I served as an instructor. Did I say 8 volts or 8 percent? Did I say that I was interested in New Jersey [Which I worked for 10 years at T Mobile in the field] or any other utility? My concerns were for those steam heating systems in Coops which are most likely commercial boilers and more than 25 units and 5 floors or more in New York. It is my understanding that more than 70 percent of the buildings in New York use steam heating. Those of you in this class of buildings should do your due diligence.
    Long Beach EdJohnNY
    8% and 8 volts RMS are virtually the same with a potential that is about 100v rms.
    don't forget about the whole hey why is your aluminum drop wire 1/3 the area of my copper service conductors thing. if your building has a lot of load the drop in the utility drop will be significant.
  • JUGHNE
    JUGHNE Member Posts: 11,617
    I believe utilities have reduced drop wire sizes because they use charts that show amperage draw with the conductors in free air.
    Also they may figure the highest load will be in the wintertime because of electric heat. This theory may not hold because of the AC load in the summertime being higher and the winter heating may not be resistive elements, rather some heat pump compressors……down to cut out point.