What's a good humidity meter?

Options
ChrisJ
ChrisJ Member Posts: 17,534

I'm looking for a good, accurate humidity meter. Preferably relative humidity.

Any ideas? Recommendations?

Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,543
    edited July 2025

    Bacharach Sling Psychrometer is the standard for measuring relative humidity

    https://www.grainger.com/product/BACHARACH-Sling-Psychrometer-6T173

    As far as a "humidistat" to operate a humidifier or dehumidifier is concerned, there are many different models that can be employed. I have never found any of them to be that accurate. Calibration is the key to proper humidity control. A standard combination Thermometer/hygrometer for measuring temperature and humidity with an analogue dial readout can be purchased for less than $10.00 on amazon. Likewise the digital version is also available for under $10.00. For accuracy, you can calibrate any device when you place it in the room you want to measure for 24 hours, then use the Sling Psychrometer to measure the accurate RH then set the inexpensive dial meter to the proper RH based on the accurate reading measured by the professional instrument.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    pecmsgmattmia2ChrisJ
  • mattmia2
    mattmia2 Member Posts: 17,571

    The psychometer is accurate(as long as you wait for the water to get to ambeintish), not necessarily that practical. I have an electronic meter made by Extech. No idea how accurate it actually is

    https://www.flir.com/products/rh300/?vertical=condition+monitoring&segment=solutions&srsltid=AfmBOorFoxCQotZWv4TIaNWXno3Fa29W32yMiAgCKs4FaTUnAOCcLqSp

    ChrisJ
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,554

    Sling is probably cheaper and accurate. Humidity is always a moving target.

    EdTheHeaterManChrisJ
  • mattmia2
    mattmia2 Member Posts: 17,571

    Before I bought the electronic hygrometer I used to use an oven probe type thermometer with a piece of wet cord over the probe.

    ChrisJ
  • HVACNUT
    HVACNUT Member Posts: 7,539
    17520107938775213305570836824107.jpg

    I've been using this for years. The only accuracy tests are comparing it to the display on dehumidifiers or humidistats I work on. Its always within a percentage or 2, so for the +/- range I need, to me its DOBA. I don't need wb or dew point often. It does take some time to acclimate when you first turn it on. About 5 minutes. After that it registers fairly quickly when taking supply and return readings or something.

    SuperTechChrisJ
  • ratio
    ratio Member Posts: 4,267

    +1 for the Fieldpiece. I've got a couple of 'em (improves the odds since I can only ever find one), plus a dual input and a single input psychrometer, both of which connect wirelessly to my manifold for calculating target superheat.

    None of them are calibrated. I should probably look into doing that.

    ChrisJ
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,543

    I have used a dual temperature probe thermometer that can be checked by submerging the probe into ice water.  When the water is saturated with ice it is at 32°F or 0°C.   Once I know the two probes are accurate, I place a wet cotton shoelace over one of the probes and blow a fan over both probes to get the wet bulb and dry bulb at the same time.  Once you have that info, all you need is to have a college course in interpreting a psychrometric chart and Viola! You have the RH you so desperately need for some reason. 

    Although you do look a little silly swinging a Sling around in circles when you are on the job. I can't remember how many times someone gave me a L👀K when taking that measurement.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ChrisJ
  • SuperTech
    SuperTech Member Posts: 2,669

    I have the same psychrometer that @HVACNUT uses. It doesn't get used very much since I got the Fieldpiece Bluetooth probes

    ChrisJ
  • SlamDunk
    SlamDunk Member Posts: 1,824
    edited July 2025

    from Amazon


    image.jpeg


    govee bluetooth works very well for $12.00. Battery lasted for several years.

    SuperTech
  • ChrisJ
    ChrisJ Member Posts: 17,534

    Curious, has anyone used one of these bad boys?

    1000018130.png

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,571

    maybe in middle school

    HVACNUT
  • HVACNUT
    HVACNUT Member Posts: 7,539
  • HVACNUT
    HVACNUT Member Posts: 7,539

    I've never even seen one of those bad boys. It looks like the wb is on the right but the wick must be dry because the temperatures are the same. And its not raining in the photo.

  • mattmia2
    mattmia2 Member Posts: 17,571

    it is a very old school hygromteter, i think it was in my elementary school science books that were published in like 1970 and i think one of the middle school science rooms had one. i'm guessing they've been around since the 20's or 30's. that tube in the middle fills with water and keeps the wick wet.

    HVACNUT
  • ChrisJ
    ChrisJ Member Posts: 17,534

    Id think a hair type hygrometer is older and still being used.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,571

    i think cellophane is more common now. the wet bulb dry bulb is more accurate if the thermometers are accurate.

  • ChrisJ
    ChrisJ Member Posts: 17,534

    That's the issue I'm having with it.

    Most alcohol thermometers aren't terribly accurate.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,571
    edited July 2025

    You could always make one with 2 thermocouple thermometers.

    I'm not sure that it is so much that they are inaccurate rather than the tube slides where it attaches to the scale.

  • ChrisJ
    ChrisJ Member Posts: 17,534

    If that tube slides I should be able to calibrate it and maybe a dab of rtv to keep it there.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Member Posts: 17,571

    the lower quality ones could also have non uniform tubes too. i have never tried to test or calibrate them, i just know i have seen a lot with the tube sliding around in the pieces of wire if you touch it.

  • SlamDunk
    SlamDunk Member Posts: 1,824

    I have a nice, old brass bodied one that my wife's grandfather used for the wood kiln at the furniture factory he worked at. Never tried it though. Just decorative these days.