Trane Air Handler Fan Constantly Running
I won’t be able to check amps at startup, but when I get home this afternoon I’ll check for voltage at the contactor and test the capacitor. I’m really hoping it’s just the capacitor as that would be an easier fix 🤞🏼
@EdTheHeaterMan , all we carry is the Turbo 200, 200X, and Mini. There's too many to stock individuals. The big ones don't typically fit the original strap, so I always have a roll of vinyl Band Iron, or as some call, Plumbers Roll.
2 -
I think failed capacitors are one of the most common service calls there is now. Didn't used to be that way. Back in the day you very seldom found bad caps. The meters we had back then wouldn't check caps. You could use an analog ohmmeter but it was not a definitive test. Didn't have digital meters back then. If you had problems the service instructions would say "Substitute a known to be good capacitor"
They had a meter called an "Annie" which we had 1 in our shop. I don't know who "Annie" was but she new how to check capacitors. 🤣
They used to be made in uSA, GE, Sprague etc and they lasted and were twice the size of the ones you buy know and were filled with good old PCBs
Maybe that's why they worked
you can test them with an ammeter, voltmeter, and light bulb. put it in series with the light bulb, measure the current through and voltage across the capacitor and calculate capacitance the same way you do with it connected to the compressor or blower motor.
they are smaller because they use more effective insulators that can be thinner and have the same dielectric strength. i remember learning about the starting/run caps in the 80's when my grandfather was telling us about how he had to replace the cap in his condenser. maybe they didn't fail as often but they were usually what failed.
Hmm ok so it looks like the original cap failed and was replaced at least once before. Look like they put in an Amrad Turbo before, surprised that it may have failed based on what I've read.
There's also what appears to be a second capacitor inside too. Should I disconnect both and test them both with a meter?
I believe this unit was installed back in 2017.
EVCON Air Conditioning Condensing Unit 14 SEER, Single-Phase, 4 Ton, R407C
Model #: GAW14L48C23S
Ok I'll have to do some reading on replacement caps/hard starts/run capacitor vs start capacitor since I'm not too familiar on the topic. I'll work on tracing out the wiring in the meantime. Thanks!
I've attached a screenshot from the unit's manual.
Ok so it looks like the Turbo is configured for 55 uF (hermetic) + 5 uF (fan).
The 55 uF —> thin brown wire (hermetic) → compressor motor (S)
55 uF also —> blue wire —> relay —> blue wire —> Common (Turbo)
Common (Turbo) also —> red wire —> T2 (Contactor) —> 2 red wires —> compressor motor R + fan motor R
Relay —> white wire —> bakelite capacitor —> white wire —> Relay
or maybe it is just a replacement for the compressor and fan run caps as i look at it more. i thought i saw 2 caps in bakelite cans but maybe what i though was a cap is just the contactor. buying caps that are the needed values is a lot less expensive than the universal cap, just buy the made in mexico like the titan hd
So is the Turbo capacitor likely the culprit based on what I described earlier or should I remove and confirm with meter?
If it is faulty, then would this be the appropriate replacement?
could be the start cap too. i'd probably replace both. or the potential relay although those usually don't go bad very often under normal conditions.
does the compressor hum but not start with the overload reset?
if the voltage of the universal cap is the same or less than the titan cap then that should be the right cap.
Hmm it was hard to tell if the compressor was humming with the condenser fan running. I just pulled both capacitors from the system.
There was a dead spider near one of the terminals near the start capacitor, not sure if that would cause an issue.
However, checking both capacitors with the meter shows acceptable capacitance for both.
The Turbo has capacitance readings of:
4.6 uF @ 5 uF
2.5 uF @ 2.5 uF
54 uF @ 55 uF
5.6 uF @ 5 uFThe Kickstarter has capacitance reading of:
324 uF @ 270-324 uF
So it seems that the capacitors are functioning. What's the best way to test the 521 relay?
Is that Turbo 200 dated? That has a 5 year warranty!!! You may not have a bad capacitor. Here is a great video on how to check the capacitor while it is operating
Read the Amps thru the CAP to the start winding of the motor or compressor Amps x 2652 = X
Read the Volts across Cap and divide X ÷ volts across the CAP
That will be the Microfarad (uf or mfd) reading of that Capacitor. I started to include that actual test on all the maintenance calls for every PSC motor and compressor. My Capacitor sales went up by about 18% and there were less "NO AC" service calls from agreement (or club member) equipment. Found the bad ones before they caused a problem. Replaced them with the "Better" 5 year warranty Turbo 200 and increased customer satisfaction and parts sales on maintenance calls. WIN WIN WIN for everyone. The company, the service tech, and the customer all win!
No one wrote down the install date on the capacitor, but the manufacturer date states 10/11/2021
@loamyroots11 said: "Hmm it was hard to tell if the compressor was humming with the condenser fan running. I just pulled both capacitors from the system."
I have had the same problem… to rule out or confirm the compressor hummmm, I would usually disconnect the fan motor to eliminate that noise. the you can hear the compressor start or just hummm.
Of course, I can't let this one go. Many times when a control or compressor humms… it is because they forgot the words. If you put the appropriate sheet music on the floor near the compressor, the humming may stop.
2 -
Should I place both capacitors back before checking the resistance of the compressor windings or does it not make a difference?
doesn't matter because the conductivity of the caps at dc is much less than a good winding but better if they're disconnected
Checking resistance (measuring Ohms) is always done with the item you're testing disconnected form anything else. If you have other stuff connected you will be measuring the resistance of all the connected items based on how they are connected (Parallel or in Series), and you don't want to know anything about the other stuff when measuring the windings of a compressor. You just want to measure the compressor motor's windings only
Hmm does it make sense that the resistance is zero?
I opened up the zip-ties and cleaned up the rat's nest - no obvious burnt wires that I noticed.
I tested the resistance across the black wire on T1 [C] and the red wire [R] and got 0 or 1 ohm of resistance.
The resistance across black [C] and brown [S] was also 0 of resistance. However, if I tested the resistance using the other black [C] Wie and the other brown [S] (I believe of the fan), the resistance was around 46 ohms.
If i were to guess what the dc resistance of a ~5 hp induction motor was i would guess a couple ohms, but i wouldn't be surprised of it was close to 0.
That means something is going to happen when you connect power to it, either it will run, it will just hum, or it will trip the overload or the breaker. possibly more than one thing.
It should be 0 or near resistance between Red to Black, Red to Brown, Black to Brown. Now check each lead to ground. If its not grounded, then...
Put everything back the way it originally was . Start the condenser for a minute. Disconnect power and immediately check the windings again. You'll likely find them open. Do you have an ammeter with a min/max function to check amps on start? Is it near LRA Locked Rotor Amps?
Checking each lead to ground reads as Open Loop.
I put everything back together, started the condenser for a minute, disconnected the compressor, and received similar readings of the compressor windings - approximately 1 ohm between C-R, 1 ohm between C-S, and about 1.5 ohms between R-S.
I was able to borrow an ammeter today. It doesn't have a min/max function, so I just paid close attention to the numbers after turning the unit on.
Upon startup, the black (common) wire to the compressor registered a max of 33 amps and after running for awhile was reporting 9 amps.
The label on the unit says LRA of 104 and RLA of 19.8, however I'm guessing with the hard start kit in place it's lowering both amperages?
So based on all of this, the compressor is fine? Would it still be helpful to disconnect a leg to the fan to hear wha the compressor is doing on startup?
Another unit made by a mystery company. Evcon leads you to Coleman which leads you to Johnson Controls.
Disconnect the 3 wire from the compressor. Measure resistance from common to start write it down. Then do common to run and write it down. Then do start to run.
The resistance from common to start + common to run should = start to run, (it might vary slightly)
Them measure start to ground , run to ground and common to ground you shouldn't get any reading.
If that comes out ok that means you have a motor and the compressor should run.
The start capacitor is in the same enclosure as the start cap you change the both of them at the same time. Look on the compressor it may be marked with the correct value of the run cap. Same for the fan.
The start relay and cap you may not know the value unless it is marked. I found the manual but couldn't find a parts list so the hard start kit and the value of the run cap I can't help with
Here is the resistance throughout the compressor:
Common + Run = 0.5 ohms
Common + Start = 1.4 ohms
Run + Start = 2.0 ohmsI didn't get any readings of resistance (open loop) from any of the compressor's terminals to ground.
Did you have a typo earlier and mean to say "The start capacitor is in the same enclosure as the run capacitor, and you change both of them at the same time."?
If so, doesn't the earlier capacitance readings of both the start and run capacitor mean that they are both functioning well?
I took off the cover to the unit and the fan says it has a capacitance of 5 uF and the compressor states 55 uF, so it seems the Turbo 200 is wired properly.
With all this testing and operating, it sounds like the compressor should be operating properly. So my next query is do the temperatures on the copper pipes change? The larger pipe with the insulation on it should get colder and the smaller one should be a little warmer. That is the real test… is the system cooling the rooms? Is the outdoor fan blowing warmer air? If not, then you may be looking for a refrigerant problem in the electrical system, when a set of gauges and some temperature probes will find the problem much faster.
And Yes… the fan disconnected for a minute or two will allow you to hear what the compressor sounds like on start up. But that will not tell you if the system is low on refrigerant.
Yeah I've started to suspect that after our electrical workup has been coming back clean. Temperature outside is 65 degrees right now, but I ran it for a few minutes and it seemed like both pipes were roughly the same temperature. I'll go check again and throw a temperature probe on it. Unfortunately don't have gauges, but if that's ultimately what we'll need then it looks like I need to hang up my hat at this point and give someone a call to come out.
The outdoor fan continues to blow cool air, while the vents inside the home seem to be room temp (or very slightly cooler just because the air is moving).
It's interesting that before the recent heat wave, it was operating (though unsure of how effectively). I do recall seeing the larger pipe sweating and the room did cool. Perhaps there's been a slow leak and with the recent increase in usage it leaked the remaining refrigerant.
Yeah both pipes are ambient temperature and similar to one another.
I did go up to the attic to check out the evaporator coil in the air handler. I could hear refrigerant flowing through the lines and there was a little bit of sweating of the smaller uninsulated copper line coming into the air handler. In addition, there is sweating inside of the air handler unit over the evaporator coil.
is part of the coil frosted and part warm or just part wet and part dry and corroded aluminum?
I think your low on charge but this must be confirmed.
- Looks like the drops of water on the small distributor tubes are freezing
- Distributor tubes have corrosion on top which could be where the leak is
- Outdoor fan should be blowing hot air
- suction line (larger line should be cold and sweating if humid should be 40-45 deg colder could be low on refrigerant.
- Liquid line (smaller line ) should be warm Say 90 deg colder could be loss of refrigerant
Those locking caps on the access valves don't usually make the same sort of metal to metal seal that the normal flare caps do either, those could be the source of the leak too. They usually just use an o-ring which is rarely a perfect seal.
Would it be worth it to purchase my own set of gauges to test refrigerant levels or just hire out to also perform leak test and determine whether the leak is repairable?
You can get gauges at harbor freight but if you have a leak you would need refrigerant, vacuum pump and a recovery tank so your better off getting someone. Gauges will not tell you how much charge you have but only help to find the problem. You need superheat & sub cooling air temp in and out of the AHU and maybe a wet bulb temp.
Since the EPA 608 requirement has been in force no individual householder has ever been criminally charged for maintaining, charging or otherwise working with refrigerants, illegal or otherwise, in their own home or business.
So, I guess the Refrigerant police are understaffed.
Working on the refrigeration side of an air conditioning system is not job for DIY's. You can create more problems not to mention you can get seriously injured. As someone just posted recently of a technician losing most of his fingers.
I spent a lot of time and money at school to learn how to install and service systems properly and 30 plus years of road experience. I see young techs with experience make mistakes so I would not recommend a homeowner. Matter of fact if I knew you put gauges on the system I wouldn't even touch the system.
1