Off grid heating/ac minisplit efficiency

i am building a 2000 sq ft cabin off grid, relying on solar (with batteries), lp generator, and heated floor by on demand boiler. What is the most efficient way to cool the cabin in the summer? Minisplit?

Comments

  • ChrisJ
    ChrisJ Member Posts: 16,684

    Where is this cabin located? What's the typical humidity there?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Member Posts: 6,033

    Open windows?

    Depending on the heat load 1 to 3_Tons of cooling will be needed. can the solar handle that kind of start-up load?

    kcopp
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,823

    Hi, Have you looked at the passive stuff, like white or reflective roofing, low E glass, and good shading to keep summer sun out?

    Yours, Larry

  • pecmsg
    pecmsg Member Posts: 6,033

    window up high that open

    Same low.

    Larry Weingarten
  • Kaos
    Kaos Member Posts: 620

    Mini splits don't have the inrush of typical AC unit as all the bits are inverter controlled. They do ramp up to near full power when doing periodic oil recovery but as long as you size for max power, you should be fine.

    One thing to watch in off grid is power quality especially in remote areas with lighting. Make sure you have surge protection on your main panel and the AC itself.

    For off grid, you want heat that is guaranteed to work 100%. Generators have a nasty habit of not starting when you are not there, so can't be relied on for power for heat (your boiler and pumps need surprising amounts of power once you calculate it). Best to install a pilot operated heat source such as a through the wall vented heater that can keep your place from freezing even with power out.

    GGross
  • JUGHNE
    JUGHNE Member Posts: 11,401

    Minisplits want clean AC power with good Hertz control.

    As do modern boilers that have a fair amount of electronics inside.

  • ChrisJ
    ChrisJ Member Posts: 16,684

    Anything with electronics inside is going to run on DC, why would it care about frequency or anything else?

    That said I'm still waiting to hear where they are, maybe a swamp cooler will work.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Member Posts: 6,033

    the computers that control everything require a clean sign wave.

  • ChrisJ
    ChrisJ Member Posts: 16,684

    The PCs I build certainly don't seem to.

    Why would something that's runs 100% on DC need anything special as far as the AC side?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Larry Weingarten
    Larry Weingarten Member Posts: 3,823

    Hi, My experience with off grid stuff has been clear that pure sine wave power is needed for electronics. Even modified sine wave is considered to be "dirty power" and makes electronics get all glitchy. Even LEDs have problems with anything but clean power.
    Yours, Larry

  • ChrisJ
    ChrisJ Member Posts: 16,684

    LEDs I could see because I do not believe they have actual power supplies in them like anything computerized would.

    I don't know .

    @mattmia2 have you seen SMPS have issues with AC power quality? If so, why?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Member Posts: 6,033

    AI Overview

    image-539bb42db00ff-246e.png image-3402b8349650b8-238a.png image-a7d4ed6c4173e-3c78.png

    +4Clean sine wave power, often referred to as "pure sine wave," is a smooth, continuous waveform that closely resembles the power supplied by utility companies. It's produced by pure sine wave inverters and is ideal for powering sensitive electronic devices because it minimizes interference and damage. 

  • Jamie Hall
    Jamie Hall Member Posts: 25,995

    The power requirement has to do with the power supply in the widget, whatever that is. If that power supply can cope with off-frequency components — spikes or harmonics — then no problem, and some types of power supplies can. Oddly enough what little observation I've done suggests that either the power supply is actually charging a battery which in turn runs the item — such as a laptop computer or (shudder) a Nest, for example — or inherently doesn't care, such as LED lights, or is in high end enough equipment to afford very high frequency switching power supplies (a lot of current high end high fidelity things) or supplies with hefty capacitors and chokes. Otherwise the high frequency grundge on the input power gets through to the computer and confuses it…

    Once in a while really grundgy power can have enough high frequency harmonics to overheat a transformer — but that seems to be rare.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,823

    Hmm, "Grundge Power"… @Jamie Hall , you might have come up with the inspired name for a band! 🙀🎶

    Yours, Larry

  • ChrisJ
    ChrisJ Member Posts: 16,684

    No SMPS runs it's transformer at 60hz. It rectifies it and runs it through a high frequency oscillator. That's kinda my point.

    And any modern computer or even cell phone charger is usually a SMPS not a linear supply.

    But maybe there's something I'm missing. It's quite possible, that's why I'm asking. So far personally I've never experienced this with any of my equipment.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • pecmsg
    pecmsg Member Posts: 6,033

    li have Walk In freezers that work fine on a generator. Use an intelatraul controller and it won’t work.

  • ChrisJ
    ChrisJ Member Posts: 16,684

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ChrisJ
    ChrisJ Member Posts: 16,684

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Kaos
    Kaos Member Posts: 620

    Minisplits all have power factor correction on the input, not just a simple rectifier. The power factor correction ic needs to sync up to the grid and expects a reasonable sine wave to run properly. Some have better control and will run with noisy power, not all.

    Most modern PV inverters are sine wave. The ones I've put a scope on (Outback and Schneider SW) had very clean output. Can't say the same thing about generators though.

    Since AC runs mostly during the day in the summer and usually when there is a lot of sun, the minsplit will be running of the PV inverter. I don't see power quality being an issue as long as the inverter has sufficient output.

    ChrisJLarry Weingartenpecmsg