most high yield measure to improve indoor air quality
Hi there,
I'd like to improve my indoor air quality, IAQ, but not sure where to start. I have searched the forum, it seems like HRV is better than ERV for improving air quality; is that better than air purifer (whole-house)?
If I have to pick one, what is the single most effective way to improve indoor air quality?
Subjectively, the air feels very stale in my house (my Airthings sensor does occasionally show increased CO2 when the room is occupied for a while, and also low humidity during winter time). The indoor air feels stale both during summer (normal humidity 40-60%, with AC turned on) and winter (my humidity plummets to high 20s, low 30s, heating is via Steam).
Other info:
I'm in Zone 7a. Single family house, 5000 sqf, 3 stories.
AC with 2 handlers (one for 1st floor, other for 2nd/3rd floor)
Heating is mainly Steam (single pipe)
Radon mitigation installed
Whole house humidifier (installed but I don't use as it uses a lot of water and does not raise the humidity much).
Please advise (I tried looking for contractors but it seems like the list is mostly for heating/plubming/steam not so much for HVAC-related). Thanks in advance
  • delcrossv
    delcrossv Member Posts: 2,183
    edited November 2024
    Best thing I did for IAQ was install an electrostatic air cleaner. And not one of those little guys with a 4 inch collector. But a real one, with integral wash. My system is 2 tons so my CFM is lower (which makes it work better)
    Universal set me up: Stainless steel case, programmed an eprom so the anodes would de-energize on the wash cycle and system blower would shut off, 7 day clock control for wash etc. Still working after 20 years.
    https://compression-systems.uapc.com/viewitems/precipitators/ial-deluxe-precipitators-4-ton-through-5-ton-units
  • delcrossv
    Also, those Aprilaire drip humidifiers are pretty useless. Went with Dri-Steem, (but they do use a good deal of electricity, and require annual descaling.
    https://www.dristeem.com/products/steam-generation/vapormist-electric-humidifier/
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,892
    Hi, I'd start with testing to see if there is anything off about the indoor air. I'd then do a blower door test to see how tight the shell of the house is. If leaky, fix the big, easy leaks. After that, look at an HRV (maybe ERV) assuming you have good outdoor air to pull from. This might be useful also. https://www.haywardscore.com/
    Yours, Larry
    HVACNUT
  • DCContrarian
    DCContrarian Member Posts: 1,138
    "Subjectively, the air feels very stale in my house (my Airthings sensor does occasionally show increased CO2 when the room is occupied for a while, and also low humidity during winter time)."
    Before doing anything you need to find out what is going on. What's making the air feel stale?
    Low winter humidity is associated with high levels of air leakage.
    delcrossv
    Jamie Hall Member Posts: 26,155
    There really are two aspects to this kind of problem.
    The first — and by far the most important in my view — is to ask what the outdoor air quality is like. This view of mine stems, perhaps, from being able to remember the reactions to the first "we have to save energy" panic of the '70s. Everyone and their uncle went around tightening up the envelope of their houses/schools/offices/whatever and, to no one's surprise, indoor air quality plummeted.
    So my first thought is this: if the outdoor air quality is better, and acceptable (it may not be in some locations), bring as much of it in as you can while maintaining some energy efficiency. This means HRVs, as ERVs sometimes — not always — return contaminants to the house along with heat. The recommended air changes per hour can be found here:
    Air Change Rates in typical Rooms and Buildings
    Residences are listed as 1 to 2 air changes per hour. So that's the place to start. A blower door test can give you a very rough estimate.
    Now the next thing is to consider what is needed to feel comfortable, and their really are only two parameters to consider — the air temperature and the relative humidity. Both are somewhat affected by the individual; some folks don't mind relatively low temperatures in the winter (or high in the summer) and some do. Similarly, some folks don't mind drier air in the winter and moister in the summer, but some do. Any time air is warmed the relative humidity will decrease (it doesn't matter what kind of heating system is used), and so, particularly in colder weather and colder climates adding humidity may be needed. This can be spot humidifiers — for instance, in a bedroom — or whole house units. The one caution is to make sure that it doesn't get so high that condensation occurs on walls and windows — not uncommon in colder climates.
    The last point is what else is in the air to reduce the air quality? In a way, this goes back to the first point — if you have enough air changes per hour, and the outdoor air quality is reasonable, you won't have a problem. But what about if you don't have enough air changes, or the air quality outside is bad? Then you have to figure out what is in the air that is reducing quality, and attack that. Some things are easy enough — dust, for instance, and some bacteria can be reduced to acceptable levels with high quality filtration. Other bacteria and virus, and some airborne moulds, can be reduced with ultraviolet sterilization after high quality filtration. Some other problems, however, cannot: objectionable gasses. This would include carbon dioxide, of course, but also includes most odours. There are ways to handle these — submarines and space stations do work, after all — but the best possible way to handle them is… outside air.
    SuperTech
  • jimmyenz17
    jimmyenz17 Member Posts: 17
    Thank you all!
    @delcrossv , that was the first I've heard of an electrostatic air cleaner! there goes another 5 hours of me going down the rabbit hole!
    @Jamie Hall , @DCContrarian, @Larry Weingarten , I had a blower door test done in 2022, the report says:
    "air leakage is 9733 CFM50 which is equal to 0.58 Air Changes per Hour (ACH)"
    At that time, the house was very drafty. I insulated the attic and ceiling of the additions and a few walls. This all helped with heat retention and the house is no longer drafty on the first floor.
    The insulating company told me post-insulation blower test is not necessary, which in retrospect I should have insisted upon. Anyway, I assume my ACH is lower now.
    As far as outdoor air quality, I live in Verona, NJ, is there an online tool that shows average air quality per year in various areas? Aside from the Canadian wild fire (for 2 weeks we smelled smoke), the outdoor air subjectively feels good but not sure what is the actual report.
    By the way, I have a whole-house, giant fan on the 3rd floor to ventilate the house, however, everytime I turn it on, I think it creates so much negative pressure, that air from wall cracks/crawl space etc gets in the house and air quality feels worst. It's sometimes better when I keep the windows open and run that giant fan but it's too cumbersome to open multiple windows all around the house, I just won't remember to do it.
    My gut feeling tells me that more ventilation is all I need (ERV/HRV), and if more ventilation still does not solve the problem then I'll invest in a detailed air quality testing.
    Unfortunately, after doing a deep dive, I realize how complex a proper ventilation (HRV/ERV) set up is.
    I do not see any HVAC company specializing doing ERV/HRV in NJ, but found this guy on youtube who seems very knowledgable. I was thinking maybe hiring him as a consultant to guide my local HVAC guy to design a proper ventilatilon? I don't know, please let me know if you have any more advice for me.
    these are some his videos that i found very interesting:
    search this in youtube (i'm not sure if attaching link is allowed here):
    "Airtight Home Ventilation: Where to Place ERV Exhaust and Supply Grilles (HVAC Training)"
    and
    "Home Ventilation's 5 Factors: How to Plan a Healthy Home:"
    Thank you all
  • jimmyenz17
    this was a pic from the report by the way
    Less than 0.5 air changes per hour? Your very first step is to bring in more outside air. A HRV will reduce the bite on the energy bill, but one way or another … remember the recommendation for a residence is one to two air changes per hour.
    So that's cheapest. Now if that isn't feasible, or you are chasing energy efficiency, you can also get the required air changes by passing the exhaust/return air in a closed or partly closed system through systems to improve the air quality. To do that, you need to determine exactly what is in the air (or what is missing) degrading the air quality. Humidity is one such — a whole house humidifier capable of maintain around 50% RH in the wintertime, for instance. Electrostatic filters are excellent — if they are also whole house and maintained. HEPA filters can help with dust and some moulds (allergen problems, such as pets, are in this group). However, as I said earlier, for some things which are airbourne gasses — CO2, most odours, and a host of remarkably unhelpful minor chemicals — cannot be removed by anything short of dedicated scrubbers, and are best managed simply by bringing in enough outside air.
    delcrossv
  • clammy
    clammy Member Posts: 3,227
    Maybe possibly seal up the whole house ventilator. They suck the heat and humidity right out of the house in the winter and in alot of cases help cause a chimney effect between 1 and 2 nd floors . They also do bout the same in the summer being high temp goes to low . I sealed my pull down attic stair ions ago and gone was the draft which left my basementa little cool and in doing so lowered my gas bill and in the summer w it sealed the top of my basement stairs is not as hot as it was . With it sealed i did see a decent drop in gas and electric usage and comfort level was much better. Every air based system deserves at a min a hepa filter system . One step better would be a electronic air filter theres a few out there some better then others honeywell makes them as for the quality now a days who knows but when maintained properly they do what they say they do . I say this having replaced air handlers equipped w them from the late 60 s where they still worked and was amazed at how clean the evaporators and blowers where ,it was at that point i said ok they do work . As for erv /hrv take a look at fantech they have just about any type of timer / sensor set up to configure a system to your project . Just remember to do all ya home work before you leap and research all the pluses and minuses to all the different system layouts. A dedicated system has alot going for it and w multi supplies and returns offers the best performance over dilution using existing duct work and a shorter erv/hrv run time and heat /cool loses due to duct loses . There alot to consider no doubt . A few extech humidity /temp loggers and a 1/2 way decent Co2 logger and possibly another blower test before you leap . I would seal up the vententalor, infiltration from unconditioned attic to conditioned space always sucking energy. A simple box made of r-10 high density polystyrene constructed properly it can be taped w a reinforced scrim tap and placed over your ventilator set up depending upon how its set up . Most erv/hrv come w some sort of semi pos filter so having a filter box made could be a smart idea especially w the fresh air inlet /seperate note good practice to install them in conditioned space
    Aprilaire also makes a combo electronic/hepa filter set up they work fine except the replacement filter is more then there standard hepa replacement media by bout twice the cost and the wires and frame that holds them are a bit cheesy and easily break . They do do a great job again as long as they are maintained .
    peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    ethicalpaul Member Posts: 7,733
    edited March 26
    Well howdy neighbor (Cedar Grove here)! I was gonna say, .58 air changes per hour and then after that you sealed up drafts, that's not very much fresh air!
    But I guess the recommended isn't much different than that…I thought it was a lot more than that
    https://www.accuweather.com/en/us/verona-township/07044/air-quality-index/339553
    pecmsg Member Posts: 6,276
    whole house dehumidifier with filtered outside air hook up.
    the filtered outside will maintain positive pressure inside.
    Larry Weingarten
    True. In fact, they will often lower it, as the moisture content of the outside air they are bringing in is less than that of the indoor air they are exhausting.
    That, however, isn't the point. The point is that in most modern or recently built houses, as a result of tight construction, the inherent indoor air quality is poor — even before you consider the effect of various materials with which the house is built. Pretty much anything one can do to lower the concentration of airborne contaminants — including a variety of unfortunate gasses, never mind assorted virus and bacteria and mounds and… the list goes on. None of the gasses can be removed by filtration or UV or have you, and removal of other contaminants by filtration and UV can be done — but isn't either easy or cheap.
    In many areas (there are exceptions, of course), the outside air quality is considerably better. If you can swap the rather nasty indoor air for the rather more pleasant outside air, all to the good. If you can do so and recover some of the sensible heat with an HRV, so much the better.
