    The white module mounted on bracket over tank is for bleeding any air trapped in the bracket. I supposed it could be used to relive pressure as well but would be a bit of a mess. The configuration shown in the previous post has two shutoffs to fully isolate the tanks and a valve at opposite end to allow water to be drained.

  • PC7060
    PC7060 Member Posts: 1,609
    edited March 30

    Eric, I agree with your approach. I kept my ceiling tank until I replaced the boiler. Still have the tank and the Thrush valve sitting around my shop as a space eating homage to the past. 😂

    EricPetersonAlan (California Radiant) Forbes
  • EricPeterson
    EricPeterson Member Posts: 270

    Here's an update and summary of figuring out the size of compression tank I need.
    First I had to estimate the # of gallons in my system, then use a tool for required tank size.

    Radiator Volume
    Since I have a mix of radiator types, I had to use different methods. I have:

    • free-standing column radiators (Kewaunee) of various sizes
    • baseboard radiators (Burnham: 7", Weil McLain: 9")
    • Radiant radiator (Burnham)

    For Burnham and Weil McLain I was able to find information from the manufacturers.
    Burnham baseboard data was only for 9" model so I had to interpolate to 7".

    For the old Kewaunee radiators, it's a two-step process:

    • Calculate the EDR
    • Convert the EDR to water volume

    For the EDR calculation I found a couple of sources (GreenBuildingAdvisor, ExpressRadiant) that provided the EDR based on the number of columns and the height. For the volume I used what seems to be a commonly accepted formula: 1.5 pints (0.1875 gallons) per square foot. So for example, our dining room radiator is 18" tall and has 24 sections, which worked out to:

    • EDR: 108 sq ft
    • Volume: 20.3 gallons

    Piping Volume
    This was based on visible configurations plus my recollection of how I added pipe for two additions, and split the original gravity piping into zones. I then used numbers from Table D (Page 42, Xylem Air Management
    Sizing And Installation Instructions
    ) for the volume per foot of all the different sizes.

    The final numbers work out to:

    • Radiators: 146.8
    • Piping: 56.9 (including boiler)
    • Total: 203.7 gallons.

    Compression Tank Sizing
    I used a couple of different sizing tools. Taco has a web version of a calculator. Xylem has a downloadable program called ESP-TANKS.
    These two tools provided very similar recommendations:

    • Taco: 44.66 gallon
    • Xylem: 44.60 gallon

    For these I used

    • Initial Temperature: 65
    • Max Temp: 170
    • Initial Fill Pressure: 18
    • Max Pressure In Tank: 28
    • System Volume: 204

    So bottom line, adding a second 24-gallon compression seems to be just the ticket. I'm prepping it now and will install it in the off-season.

    Thanks for all the comments and feedback. This was quite a lively topic.
    —Eric

    PC7060delcrossv
  • Intplm.
    Intplm. Member Posts: 2,588
  • Love your shop! Makes me feel better because I thought I had too many different brand battery chargers.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    PC7060
  • EricPeterson
    EricPeterson Member Posts: 270

    Haha - yeah I used to watch those reruns back in high school!

    My Airtrol does not have any slot for a screwdriver, just a fitting for a wrench to open / close the Airtrol for setting the water level.

    Honestly I've spent most of my time figuring out the root cause of the high PSI, then finding all the needed information to determine the size of the compression tank I need (calculating EDR, piping, water volume, sizing tools, etc). I then tried to summarize all this in my last post so that others in a similar situation could find everything in one place. I've not spent a lot of time thinking about how to pressurize my tank.

    That said, honestly I think my method is actually very simple and takes less time: isolate the tank, set the water level, pressurize, piece of cake. Or as K-9 said in Dr. Who, "radial segment of baked confection". Bob's you uncle.

    —Eric

  • mattmia2
    mattmia2 Member Posts: 12,280
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,872

    I could have told him "LOST". I just finished binge watching that, and I didn't remember most of it. Guess I was Lost the first time I watched it over 20 years ago :-)

  • Mark Eatherton
    Mark Eatherton Member Posts: 5,872

    One thing I forgot to mention is that if you keep the tank, you can NOT have any means of air elimination on your system, because it WILL get rid of the cushion in the tank. I don't remember if anyone else mentioned that, and if they did, ignore me. Whereas if you switch to a diaphragmatic type of tank, you MUST have an automatic air eliminator. We haven't even talked about proper, ideal system configuration as it pertains to your pumps location in relation to the expansion tank. That in and of itself will create "air problems" in your radiators. Look up "Pumping Away" for more information.

  • EricPeterson
    EricPeterson Member Posts: 270

    Funny. I’m just finishing watching Lost. Maybe it makes more sense the second time?

    —Eric

    Mark Eatherton
  • EricPeterson
    EricPeterson Member Posts: 270

    I assure you there are no other air eliminators in the system. Also all the components are connected per “pumping away” - boiler supply, air separator connected to water feed & compression tank, circulator. Pretty much by the book.

    —Eric

    delcrossvMark Eatherton
  • PC7060
    PC7060 Member Posts: 1,609
    edited April 4

    whaaaat? Isn’t 5 or more battery types “normal” these days? 🙄🥸😂

  • leonz
    leonz Member Posts: 1,465
    edited April 4

    Hello Eric,

    I am coming in to your discussion late but I wanted to make sure that you plumb in the new steel compression tank correctly for your heating system.

    If you have ordered a steel compression tank with end tapping's for a gauge glass all the better as you can be assured of the water in both tanks as the water levels will be equal when you fill them again.

    The piping for the first and second steel compression tank should be parallel to allow the proper orientation of the airtrol valves.

    Page 4 of the Bell & Gossett AIRTROL installation sheet illustrates how parallel steel compression tanks need to installed correctly with larger header pipes.

    The drawings on page four shows how the plumbing should be oriented with the new piping.

    According to the information on page 4 Bell &Gossett wants the trunk line feeding both steel compression tanks to be one size larger than the tapping in the Airtrol tank fitting so that means a one inch truck line is needed. I am not sure whether a 3/4" nipple to 3/4" to 1" bell reducer would be advisable to create the 1" riser that would meet a 1" elbow to create the header pipe to be used to connect to the two steel compression tanks in tandem.

    The one inch trunk line/horizontal header must be pitched up to both steel compression tanks. in your case with 2 tanks the tee and elbow must be pitched up to the ATF-12 Airtrol valves in both tanks.

    The instructions do not state what reducing fitting should be used to do this coming off the tee and elbow of the one inch header pipe, perhaps a 1" short nipple and a 1" inch to 3/4" reducing bell coming from the elbow and the tee in the header pipe would be the more ideal way to let the air bubbles migrate more swiftly to both steel compression tanks. The drawing on page 4 illustrates a 3/4" short pipe nipple coming from both the elbow and the two tees which are connected to unions that are connected to the airtrol valves but there is no mention of the ideal type of 1" to 3/4" reducer whether a bushing or bell fitting and pipe nipple is preferably used to connect to the short nipples to the unions and the next short nipple that meets the Airtrol valve.

    I do not know how to upload the page illustrating the diagrams showing how the piping is done for multiple steel compression tanks.

    I hope I have not made any mistakes in describing this to you and I would certainly appreciate any corrections made by the members.

  • EricPeterson
    EricPeterson Member Posts: 270

    @leonz - thanks for your concern. I am following the instructions per the B&G document you reference.

    The pipe from the boiler to the compression tank is already 1" and pitched 3/4" in 2 feet, then reduced to 3/4" to connect to the Airtrol fitting - so I believe I meet the requirements mentioned in that document.

    —Eric