Restoring One Pipe -- finally
cgutha
cgutha Member Posts: 119
HI Everyone, I am finally restoring the boiler.
In a "Whole house" heating update, insulating the house came first. Who would have thought it would take this long? Most of the house is now insulated, new electrical and plumbing installed. It is winter, so I am doing basement things: water heater, now boiler.
The boiler is a Weil-McLain EGH-85. 350k input, 280k DOE output. At a design temperature of -30, The new heat load of the building is 240k BTUH. So, I am redistributing and removing the radiators according to calculated need. Given the fact that this year we saw -39 degrees, I am not worried about being oversized. I am reusing the 3" main but will only have 14 risers.
Originally, I had two mains, 3" took care of the East half of the house, and 2" the west half. They met on the other side of the house and came back in a wet return. I thought I had a picture of the loop where the two connected
but it is behind the wash machine. The return line is dry here but drops down to go under the floor at the stairway. Then went into a condensate tank, with pump.
Because my heat load has decreased, I can now send all the steam through the 3" main, reduce it at this junction, then continue around the house in a 2" main (change slope and direction of flow). This will allow the end of the main to be a few feet from the boiler. I will take pictures when I get that far.
The right section of the boiler leaked, and all the burners were rusted / unusable. The section is now replaced, and the new burners are in a box in the corner. I did a pressure test and decided to replace all the ropes and sealing rings. That is what I am doing today. I probably should have boiled (chemically clean) all the sections but did not. There is a lot of calcium buildup and rust.
The near boiler piping was welded, and not quite right. I am moving the boiler and have modified the header to make a dropped header — threaded. I will send pictures when I get it assembled. Now I have two more sections to clean and put together. then the left section is ready to connect to the right section.
delcrossv
«1
    Steamhead Member Posts: 17,767
    This is in Velva?
    Consulting
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,096
    Velveeta? Wisconsin? Ha ha..Mad Dog
    Velva, ND. If that's the place I'm thinking of, I looked at that some years ago for a former owner.
    Consulting
    Mad Dog_2
  • cgutha
    edited March 23
    Yes, Velva ND. and you were here. You recognize the wash machine. it is still there. 3 phase, 3 hp belt drive, overhead shaft.
    Mad Dog_2
  • cgutha
    edited March 23
    The original coal boiler is still there, and some of the parts are still cluttering a corner somewhere. Part of me wants to remove it for the space, another part says keep it for a potential museum piece. most of the auxiliary equipment and piping has been removed. The old water tank leaked; I am waiting for help to truck it off.
    The bricking is crumbling, but there is enough left that I can tell the original water level of the system.
    Obviously, a wet return traveling under the basement floor returns condensate at a temperature around 65 degrees. I suspect that continuously adding 65-degree water to a cast iron boiler has something to do with the metal fatigue of the inlet section. I plan to eliminate that problem by employing dry return. With the change in the main, the main now ends a short distance from the boiler. thus I will try to maintain 212-degree saturated water at the Hartford loop.
    Or, if the return has to stay buried, insulate it. We generally do.
    And I bet a steam or gas engine originally drove those lineshafts.
    Consulting
  • cgutha
    Now for the near boiler piping: 24 inches from the water line, can it be taller than this? how tall is too tall?
    ethicalpaul Member Posts: 7,623
    It can be taller. There is no "too tall" for a header but there is "unnecessarily tall".
    If the water is reasonable quality, it won't even splash above the boiler anyway.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,916
    It's not just a matter of how high the water splashes; it's how far the droplets get carried by the high velocity steam column. That's why they call it carryover.
    edited March 25
    The velocity isn't high enough to carry them over, if the size and number of the supplies is anywhere at all close to manufacturer's specification.
    But lots of people sure think it is, even though they have never seen it.
    And just for fun, let's say the velocity is high enough. The drops don't stay suspended. They eventually hit a pipe wall and stick to it.
  • Hap_Hazzard
    There's something called entrainment where the droplets stay in the steam train until they're physically separated from it, such as going around a bend and hitting a pipe wall. That's the idea behind the header. But how much separation occurs depends on the velocity at the point of separation and the size of the droplets.
    Have you ever put a sight glass on your equalizer to see how much water is coming back to the boiler from the header? If you haven't, that's going to be my next project.
    edited March 25
    entrainment is another myth that people think exists yet no one has ever seen. I'm not saying it could never happen, but it never happens in residential steam. The drops fall out and hit a wall, with or without drop header. Residential steam isn't very fast. The bigger the boiler, the bigger the pipes so the speed is limited.
    "That's the idea behind the header." Not to be arrogant, but who are you talking to here? 😅
    There is no water coming back to the boiler from the header, unless the water quality is bad enough. See my videos.
    At startup there will be a very small amount sliding down the pipe wall but once everything is hot, the condensate in the header becomes steam again before it even has a chance to drip back to the boiler. The steam passing by re-vaporizes it.
  • Hap_Hazzard
    edited March 25
    Of course you can't see it. Are you going to tell me wind is a myth because no one has ever seen it? It's a real, measurable physical phenomenon. https://www.sciencedirect.com/topics/engineering/liquid-entrainment
    I've looked through your videos. I didn't see one that adresses this.
    Long Beach Ed
    edited March 25
    I'm saying if they are so small that they can't be seen, they don't affect anything.
    The examples on that page are very small tubes. At our speeds and size of pipe, there is no measurable effect.
    Note from your links: "In annular flow, liquid forms around the inside wall of the pipe and gas flows at a high velocity through the central core. It occurs for gas velocities greater than 20 ft/sec (6 m/sec)."
    This video shows the utter lack of carryover and entrainment:
  • Hap_Hazzard
    You wouldn't be able to see it there. The droplets are too small and moving too fast. I mean, I don't "see" any steam there either. Does that mean there's no steam there?
    come now.
  • Hap_Hazzard
    I'm sorry, but, "if I can't see it it isn't there" isn't a great argument.
    mattmia2delcrossvclammyLong Beach Ed
    edited March 26
    "Too fast to see" isn't that great either. This isn't a jet engine, it's a pot of boiling water. Your links regarding entrained mist are talking about much faster flows in much smaller pipes (and the ones referenced there are not invisible).
    Do people think these invisible droplets (if they are there) affect anything? Do people think that a few curvy pipes remove would them if the forces that entrained them are so strong? I know you put sight glasses on your boiler, but I can't remember if they are on the supplies.
    When I asked people what wet steam was in that thread some time ago, I don't recall anyone saying "it is droplets that are too fast and too small to see that apparently don't affect the water line". I know that people don't like it when some picture they have in their mind for years turns out to be different in reality but folks have to trust their eyes at some point.
    Here's what I think surging and carryover and wet steam actually are. It affects the waterline and steam "efficiency" (maybe) and is obviously not desirable:
    edited March 26
    Saturated steam —which is what we are dealing with — will always have liquid phase water droplets in it. They are constantly forming and evaporating. And no, usually you can't see them. They will coalesce on cooler surfaces, such as pipe walls.
    I agree with this—this was one of my definitions that I put in the poll on that thread. But almost nobody around here felt that was what "our" definition of wet steam was (I had made the statement that by definition, all of our steam is wet steam). (See the fourth choice in the poll here)
    So now I set that definition aside since I also agree that it isn't useful for residential steam since it's in fact ever-present and there's nothing we can do about it (we don't have super heaters on our boilers). But I think that's what @Hap_Hazzard is referring to (but I don't want to put words in his mouth)
  • cgutha
    edited March 29
    Wow. (And I am not even talking politics on Facebook.) If you wish to discuss super heat and steam engines, I recommend Steam Automobile Club of America | Steam Engines and More (can I do that?)
    I have a nine-foot ceiling in my basement, so 36 inches from the top of the boiler case to the center of the 'hook' that drops into the header is no problem. Which is about 46 inches from the water line.
    It looks like an eight-inch nipple between the takeoffs, and header will align my header with the condensate return port of the boiler. (Someone should have mentioned that in the boiler manual somewhere.)
    Dan mentioned in his 'Lost Art' book that we are shooting for dry steam to increase efficiency of transferring latent heat, so I am striving for dry steam.
    By the time the main wraps around the house, I only have about thirty inches to the water line. That is still above the required 28 inches. I have some changes to make, I will know more exactly later.
    by the way, the speed of the steam in the two-inch boiler risers, at maximum output is 44.6 feet per sec. lots of carry over.
    delcrossvHap_Hazzard
    30 inches, 28, 12 it’s all fine. On one pipe systems for sure, the waterline doesn’t rise at the end of the main
  • Hap_Hazzard
    Of course you can do that, @cgutha . It's your thread. Sorry I took it on a tangent, but some of us see the IOM rrecommendations as a maximum, while most of us see them as a minimum, and, when it comes to header height, if we're working with two 2" boiler risers and two 2" system risers, the amount of pipe it takes to get to the mains is the same, no matter where you put the header, so why not make it as high as reasonably posssible?
    I got a lot of help from the people on this site when I was designing my header. Here's a thread where I specifically asked how high my header should be:
  • ChrisJ
    ChrisJ Member Posts: 16,668
    The higher the header the more equalizer pipe you need.
    That's all I've got………
    Hap_Hazzard
  • Hap_Hazzard
  • cgutha
    I am reusing the old pipe. I eliminated the condensate return, so I have lots of extra pipe.
    Oh, I should mention that this project is not going to be quick. I am working on it alone after work and in between other engagements. If I run into a snag, such as "Where did that cast iron pipe come from? Why did I not remove it already?" and other miscellaneous items, such as "I should have ordered an 8-inch nipple not a six," or "It is Saturday afternoon, and I would rather chat on the computer than work downstairs where the coal dust still resides…"
    But I need to complete the project before June so I can get back to my other projects.
    Today I install the drop header. Then I need to cut it into the main. If I get further than that today, I will get another project out of my way that I am putting off.
  • cgutha
    Today, I plan to complete the near boiler piping and tie into the main and return. Pictures will be coming.
    I do have an important question that is running through my mind as I check the calculations, I made years ago.
    What happens inside the radiator as the steam displaces the air?
    Let's say I have a four-column radiator. The steam enters, and the vent is on the fourth column. Does the steam enter so fast that it pushes all the air out of the first three columns before the vent is satisfied and closes? (If so, then I have no further question, however, if it is partially filled with air, I do not understand the old coal system.)
    I understand the transfer of heat, the collapse of volume as steam condenses, the replenishing of steam and dispelling the condensate. But how much of the radiator still has air in it or is all the air displaced?
    Say I start an old coal boiler / system when it is thirty degrees outside. Enough steam enters the radiator to satisfy 33% design load. But when the temperature outside drops to minus thirty and the load is now 100%, If there is air in the radiator set to the required 33% load at the time, The radiator cannot meet the 100% load without breathing and resetting.
    Of course, if all the air is displaced, then the house will overheat when 33% is required and 100% is available. (Thus, the need for two pipe control.) I imagine that this is what happens. So, I conclude that all the air must be removed in all the columns. I need confirmation or further detailed explanation.
    In the old days, when coal was used to fire the boilers, The fire was lit and continued non-stop for months (maybe). My system was originally a coal fed system.
    Today's boilers cycle on and off requiring larger air vents on the main and risers. Thus, the non-coal, gas fired boilers "breath" where the old systems did not. The conversion from coal to gas requires larger vents. I found some of the vents, they need and will be replaced.
    As a boiler operator in an industry, I would control the variable boiler flame to match the load on the boiler thus maintaining pressure. Unfortunately, as electronics took over, manually controlling the flame became a thing of the past. I never could teach the electronics how to anticipate and match the load.
    Weil-McLain does not make a dual burner for residential.
    Thanks for answering my radiator air vet question.
    Jamie Hall Member Posts: 25,992
    Pretty much the air is pushed out of the radiator as it enters — the vent won't close until the steam makes it all the way through the radiator to the vent, so by that time… pretty much full of steam.
    You do mention control… and yes, two pipe is a lot easier to control as you can close, or partly close, the inlet to better match steam flow (and thus condensing) to required power. One pipe, as you note or imply, you can't. In most cases one works on a rather intricate interplay of venting rate and cycle time and one can get the balance pretty well. Thermostatically controlled VENTS can also be used — but it's important to remember that the boiler must cycle off and pressure drop to zero from time to time for them to gain control.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,763
    Just adding to Jamie's reply… Steam is lighter than air. When it enters a radiator it generally rises to the top nipples in each section and is carried to the low pressure point which is the air vent or return… It is condensing against the cool metal, so the condensate and condensing steam flows down the sections to the bottom of the radiator heating the iron.
  • cgutha
    "Steam is lighter than air."
    How could I have neglected that? Now it all makes sense.
    Well, I got the 3" (inlet end) of the main connected to the header. Now I need to align everything to make certain there is no stress on any pipes and double check that the slopes are correct.
    The Hartford loop is ready to install, and
    I found a two-inch pipe to complete the return end of main. (it needs to grow about seven feet)
    I will send pictures when this part is complete.
  • cgutha
    Two more questions:
    1. The Hartford Loop / return is recommended to be 1-1/2-inch pipe, is it ok to go larger? I have 2-inch on hand.
    2. What is the best way to supply makeup water? I seemed to have missed that chapter. My experience is with industrial systems, not one pipe, residential. The old setup had a condensate tank with pump. I have removed that. given all the mud when I disassembled it, it was obviously not treated. — I would prefer a float type valve, for when we lose electricity. I would prefer mixing it with the condensate return, before entering the boiler to lessen thermal shock. not certain i can do both.
    3. Oh, and a third question. What is the best way to clean the boiler. I did not give it a bath when it was apart, but there is scale, and rust — most of the mud is out.
    I hope to have the Hartford loop completed this weekend to send pictures.
    edited April 18
    The "float type valve" would be a McDonnell & Miller #47-2. But the newer electronic probe-type setups are more reliable….. is a backup generator under consideration here?
    That 2" pipe should be fine.
    How is the water quality out there- does it contain scale-causing elements?
    Consulting
  • cgutha
    I found a video. he manually opened a valve when the low water cut off tripped.
    ??? If the electricity is off, how is the gas valve staying open?
    Regardless of that, there's no way in hell that I would ever install a float-style LWCO if I had the choice, due to the additional maintenance and (in my opinion) the much higher chance of failure.
    My favorite place for makeup water is into the wet return, wherever is most convenient. Which is great for limiting thermal shock, even though I think thermal shock is not really a concern in residential steam.
    All agreed, @ethicalpaul . Particularly thermal shock! I pipe the feed into the cold return, too — but the only time you will get thermal shock in a steam boiler of pretty much any size is if you somehow manage to get the cold feed water in contact with metal which has NOT been in contact with boiler water. Now if your boiler has run low and you hit part of the firebox or tubes above the water line with cold water, yeah… it can get pretty spectacular. But otherwise? No. How do you think steam locomotives get their water? Now some of the later ones have feedwater heaters, but it's not for thermal shock — that's for efficiency. Otherwise — out of the tender, through the injector, and into the boiler.
    ethicalpaulLong Beach Ed
    this is how I do it too. I don’t mean I let the lwco trip it, but I mean I don’t have an auto feed, they lead to people ignoring their water usage.
  • Long Beach Ed
    edited April 19
    We still install and specify many McDonnell 47-2 float low water cutoffs and feeders on government spec and jobs where we know the boiler will receive maintenance and attention.
    Some clients just want the assurances of positive mechanical control and the positive test feature.
    If you install a 24 volt electronic cutoff, the power requirements will be minimal and could easily be provided by whatever backup system powers the gas valve. You'll also save enough money to buy groceries for a month.
  • cgutha
    A battery backup for the 24-volt control system is what I have in mind. for the most part, two hours should suffice, however, others in other areas have lost electricity for multiple days.
    I have completed the near boiler piping, header, tied into to the main, and the Hartford loop. The next step is to pressure test everything from the king valve to the return valve. (installed so I can blow down the boiler at 15 psig once a week) This test is supposed to take place before the piping, but I want to test all of it together.
    I found that I tightened the pipes to the dropped header too much. They are not moving. on the EGH, The near pipe plumbing has three connections, it looks like I am pulling the sections apart. I will test again tomorrow after allowing for more movement.
    pictures are coming after I clean the room and make it photo presentable.
    Oh, I am in favor of a standing pilot. any comments on that?
    and I also need recommendation on cleaning the cast iron boiler.
    edited April 23
    A battery backup is fine, but if you have a battery backup then you can use a probe LWCO (which you absolutely should) with auto-feeder (which is far less clear-cut). If power does fail, the gas valve will close—having a battery backup is not a reason to desire a mechanical autofeeder. If you have a long power failure, you'll know it and you can manually add water regardless, but your system shouldn't have leaks and will only use a gallon a month or so (or ideally less).
    Why do you want a standing pilot? Why not an electronic start with a flue damper so your heat isn't going up the chimney all day and night?
    They don't move. It's a myth that swing joints "swing". They rust tight and are a real pain to remove even a few years after installation. Anyone who has ever tried to re-use a fitting knows this. What the swing joints give you is some flex due to distance and leverage. If you are pulling sections apart then your pipe-fitting needs some improvement (I'm not judging here, it's not easy, that's why there's a whole trade for it).
    What part of cleaning are you asking about?
    Don't blow down the boiler once a week, that will just introduce a lot of unnecessary fresh water with oxygen into your boiler, causing even more mud production.
    Treat the water with 8-way to raise the pH and absolutely minimize leaks and other fresh water introduction and the water stays clean.
    See my blessedly short video about it here:
  • ChrisJ
    A reason for wanting a standing pilot could be to get away from issues with the controls.
    I have ZERO experience with them but I have seen pros commenting on how thermal couples have gone down hill and don't last nearly as long as they used to. If that's true, then going with a standing pilot is not going to gain you the reliability you think it is.
