Confused - Hydronic air handler VS heat pump VS heat pump plus furnance
  • Kaos
    Kaos Member Posts: 681
    edited March 16
    For the heat pump, I would ask for a cold climate unit. Something like this:
    https://mylinkdrive.com/viewPdf?srcUrl=http://s3.amazonaws.com/enter.mehvac.com/DAMRoot/Original/10007/M_SUBMITTAL_PAA-A24AA1_PUZ-HA24NHA1-R1_en_M1.pdf
    or the 38MURA high heat* version of this:
    https://www.shareddocs.com/hvac/docs/1010/Public/00/01-DLS-019-CA-01.pdf
    These will heat down to your design temp so you have the option of running either gas or electric when cold.
    Also make sure the furnce has an ECM blower. These are much quieter and use significantly less power. With the duel fuel setup, you don't need an expansive furnace as it should only ever run when very cold. A standard one or two stage unit is good enough.
    *high heat is important. There are two version and the other version does significantly less heat at 5F.
  • Toasted
    Toasted Member Posts: 34
    edited March 16
    @Kaos Awesome - I just spoke with an installer that's Diamond, and he just mentioned Intelli-heat. Wonder if I can get my hands on some 410a equipment. I have to confirm, but it sounded like his idea was to use the intelliheat just for the first floor and leave the second as a regular heat pump.
    ethicalpaul Member Posts: 7,766
    That is surprising because it seems that clean fill material would be desirable by someone
  • Toasted
    Definitely possible, and finding that person(s) is the way to reduce that cost.
  • Toasted
    Here's a part two to the question: I had an installer mention that if I go duel fuel, just to do it on the first floor since heat rises and no need to do it for the second floor system. Make sense?
  • ChrisJ
    ChrisJ Member Posts: 16,854
    If you agree with that logic why bother putting any heat at all on the second floor?
    Yes, you can make such layouts work, such as many have used a single wood stove on the first floor and heated an entire house. But the house tends to have large temperature differences and you need to make adjustments in how you live just to make the system function at all.
  • Kaos
    That is mostly correct espcially with doors open. One option is to look at the fuel burner as backup for polar vortex days. In that case the having it only on the main floor makes sense if it saves some cost. Just make sure the heat pump for the 2nd floor is sized properly to handle your 99% design load.
  • ChrisJ
    Duel fuel……..is that when you run the AC and the heat at the same time?
    pecmsg Member Posts: 6,295
  • DCContrarian
    DCContrarian Member Posts: 1,153
    I want to follow up on the early part of the discussion where we talked about the role of infiltration in indoor humidity.
    When it's cold out, the air outside will hold less moisture than the air inside the house. Infiltration will tend to take humidity out of the house. At the same time, the occupants of the house generate humidity through activities like bathing, cleaning, cooking, breathing and perspiration. The humidity level in the house will stabilize when the moisture lost through infiltration balances the humidity added through occupant behavior.
    This graph shows infiltration rate (on the x-axis, in CFM) versus equilibrium humidity (on the y-axis, in percent):
    It assumes an indoor temperature of 70F. The three lines are for outdoor temperatures of 0F, 20F and 40F, all at 50% relative humidity outdoors.
    Manual J assumes that occupants produce an average of 0.2 pints per hour, this chart assumes four occupants.
    Note that at very low infiltration rate — as in a very tight house — even in winter humidity can get uncomfortably high. The ideal infiltration rate seems to be around 40 CFM.
    Usually when infiltration is measured it's measured using a blower door test and expressed in air changes per hour. To convert that to CFM you need to know the volume of the house. Also, the blower door pressurizes the house, so you have to apply some sort of correction to account for the pressurization.
    Just to put these numbers in context, 40 CFM is 2400 cubic feet per hour. A 3,000 square foot house with 8' ceilings is 24,000 cubic feet in interior volume, so that's 0.1 air changes per hour. A very rough rule of thumb to convert from blower door scores to natural air changes is to divide by 20, so that would be equivalent to a blower door score of 2.0 ACH. In 20th century construction that would be pretty much unheard-of, but in modern construction that's a very achievable level of tightness.
  • Toasted
    Main floor is effectively open floor plan - living room, central cooridor with mudroom/half bath/hall, then kitchen and living connected. Second floor is three bed, two full bath, and a laundry room.
  • DCContrarian
    I'm a dual fuel skeptic. In order for it to make sense to switch between gas and electric depending on the outdoor temperature they have to be close in price anyway. If they weren't, one would just be cheaper all the time. But if they're close the amount of money saved by switching is going to be small, not enough to justify the added complexity and cost.
    The advantage a furnace has over a heat pump is that it produces hotter air, so it can output the same amount of heat with smaller ducts. This is a real advantage, especially in a retrofit where the ducting is already there, but in any house no one wants to give up space for ductwork unnecessarily. Usually when dual fuel is proposed what is envisioned is that gas is going to be used on the coldest days, regardless of relative prices, because the system as installed won't be able to meet the heating load using the heat pump.
    Sure, the heat pump can provide heat in mild weather, but you don't need that much heat anyway in mild weather so you're not saving that much money.
  • Hot_water_fan
    Hot_water_fan Member Posts: 2,199
    Dual fuel has a place DC, for the constraints. Ductwork is one. An electric panel is another as is cold climate performance. I agree that switching to save on costs is a bit of a loser. The prices change a lot and you have to be ON IT to know the current monthly price of each
  • DCContrarian
    Just to be clear we're talking about the same thing, when I say "dual fuel" I mean a system that can heat using either a heat pump or a furnace, not a furnace for heating and a heat pump for cooling.
    If the heat pump being installed can't heat the house by itself, it's kind of a sham dual fuel. You don't really have the choice of choosing your fuel, you have the choice only in warmer temperatures. And I think we both agree that the cost savings from that are minimal.
    Now, in a lot of cases installing a heat pump instead of just an air conditioner adds little or nothing to the total cost. So adding a heat pump instead of just an AC is a selling point, it's now a "dual fuel" system. But it's not like this is really doing the customer any favors.
  • Hot_water_fan
    edited March 21
    I think dual fuel includes cases where the heat pump alone can’t cover 100% of demand. In that situation, the furnace is competing against resistance backup too. But I see your point. I still think dual fuel has value for the constraints. That’s not a sham. Using a heat pump for 80% of outdoor temps, which is likely 95+% of total heat needed, is still substantial.
  • DCContrarian
    I did a detailed analysis for Boston, MA, you can see it here: https://docs.google.com/spreadsheets/d/1KmnOjq_MEQ2fNqj5AZvLSXHkNx3dwDPvn_SNBV2iHMA/edit?usp=sharing
    Look at the tab labeled "Analysis."
    The house in question would have an estimated annual heating bill of $2,037.47 if it was heated with a heat pump, with electrical resistance used when the heat pump lacked enough capacity.
    I ran three scenarios:
    1. Burning oil instead of using resistance heat for supplemental heat. This would save $10.47 per year.
    2. Burning oil below the breakeven temperature (10F). This would save $21.92 per year.
    3. Burning oil below 25F (picked arbitrarily as something that felt about right). This would save $9.51 per year.
    Now, every house is different and energy costs vary tremendously from region to region. But the takeaway that the savings from dual fuel are just miniscule is something that applies broadly.
    The reason is that you're only going to be considering dual fuel if the two fuels are reasonably close in cost. Boston is expensive, oil is expensive, so the breakeven temperature is pretty low there, 10F. But most places it's between 20F and 30F. And if the breakeven temperature is, say, 25F, electricity is going to be cheaper at 35F, but it's not going to be that much cheaper. And electricity is going to be more expensive at 15F, but it's not going to be that much more expensive. And the annual savings from switching fuels to chase the lowest cost is going to be less than the cost of a filter change.
    Now, if you live some place where the fuel costs are radically different — let's say your breakeven is 50F, or -25F — you're not even going to be thinking about dual fuel, you're just going to run the cheaper one all the time.
  • Hot_water_fan
    I disagree! I think if you want to go dual fuel for energy savings, sure, the savings are likely minor.
    But there are absolutely other great reasons for dual fuel.
  • DCContrarian
    "But there are absolutely other great reasons for dual fuel."
    The reasons given so far are for choosing gas over heat pump, not for dual fuel. What's a "great reason" for running a heat pump part of the time instead of gas all the time if it doesn't save any money?
  • Hot_water_fan
    edited March 21
    a few notes:
    1. Dual fuel can use fuels other than gas. Oil and propane can be particularly pricey, so savings could be better.
    2. sometimes people want a heat pump over just a furnace. Dual fuel can help accommodate them
    3. the price of AC + furnace can be the same as HP + furnace, so it’s an easy hedge against future fuel cost changes
    4. Dual fuel can enable a cheap furnace + cheap heat pump since the weaknesses cancel out.
    As to why dual fuel can make sense instead of exclusively heat pump:
    1. #4 from above
    2. Helps with constraints: generator capacity, electric service capacity, airflow capacity, etc
    3. Can provide low temp performance
    4. Can reduce low temp emissions
    5. can be an easier sell to installers, insurance, homebuyer, electric utilities, etc
    all that said, I have only a heat pump :).
  • DCContrarian
    I'm sorry, but you should know better. It's a myth that one kind of heating system dries the air more than another. It's a misconception that the heating system is what's responsible for the air getting dry. It's caused by infiltration of cold outdoor air.
    Hot_water_fanbburd
  • GW
    GW Member Posts: 5,065
    Hydronic air handler VS heat pump VS heat pump plus furnace
    Subtle pros and cons to every option. It's easy to get bogged down!
    "I'm sorry, but you should know better. It's a myth that one kind of heating system dries the air more than another. It's a misconception that the heating system is what's responsible for the air getting dry. It's caused by infiltration of cold outdoor air."
    »It is possible for the air system to induce more infiltration, though.
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    ChrisJ
  • TAG
    TAG Member Posts: 792
    Did I miss where this guy lives?
    I never understood the boiler running to two air handlers and nothing else .. this seemed to grow out of a "this old house" episode and it never made sense unless NOTHING else was possible. High cost with poor control when stacked up against the other possibilities.
    In the states where I live to get the rebates you have to get a heat pump and not a straight AC … even in NJ where I have natural gas and the NG is cheaper to use for heat. I have a heat pump that is never used.
    Seems like the homeowner has natural gas … you want to keep that. Adding a boiler to a house without one is expensive. The new equipment makes zoning easy but you need to get someone who knows what they are doing and that's the hardest part .. the number of trades people who still say put in two systems when one will work is surprisingly high.
  • Toasted
    You're on it - zone 5a east coast. I would like to keep the NG and that is the approach, but I am understanding that with Mitsu HH, intelliheat itsn't needed as we are temperate enough for the HH unit alone to provide adequate heating down to ~10-15F.
    Let's take a boiler out of the equation as we now know that really doesn't make sense. I still want two systems, one for first and basement, and one for second and attic. The idea is to duct the first with a handler in the basement and throw a minisplit in the basement in order not to combine air with first (Mitsu HH systems lets you mix and match ducted with mini split heads). I would then do the same approach with a handler in the attic and put a split in the attic.
    My three major questions include 1. Do I do a duel fuel (Intelliheat) or just go straight up traditional furnace and AC, 2. Do I go straight heat pump, and 3. How to size it because I had a Diamond installer tell me I need two 3-ton systems for each floor and we are talking 1,100 fully renovated/new. My load calc is getting me closer to 3 ton on first and 2.5 ton on second.
  • DCContrarian
    I'm going to repeat my contention that dual fuel never makes sense. Or rather, rarely and under very specific circumstances: electricity is much cheaper than any other heat source, but you are unable to use a heat pump for all of your heating needs because of some constraint, like existing ductwork or limited electrical capacity.
    Dual fuel is installed when the installer doesn't believe in heat pumps.
    Jamie Hall Member Posts: 26,200
    Just a few random observations..
    First, if you are going to install air conditioning, make it a heat pump (unless you are far enough south to never need heat). Why not? The cost difference is minimal.
    Second, each situation is different. If you are dealing with a house with poor or no ductwork — surprising how many of those there are — anything on the heat pump side of the game other than minisplits is probably not in the cards. But see the previous paragraph.
    Third, be very careful about costs. The cost and availability of energy sources (natural gas, LP, oil, electricity primarily) varies widely from place to place, and thus the economic viability of selecting one source, or a combination of sources, will be different. In Cedric's area, for instance, a heat pump always costs more to run, per BTUh delivered, than Cedric's big oil burner. There is no "break even" temperature. In other locations, a heat pump may well be less expensive to run even down to the lowest temperatures encountered.
    Then there are local political considerations. Is the cheapest source even available for new or retrofit? Is it permitted? Are there subsidies and, if so, what are their requirements? And so on.
  • Toasted
    @DCContrarian
    @Jamie Hall
    First, I am running steam on NG, so not sure whether or not a heat pump is going to be cheaper as I am undergoing insulating and sealing the home. Is there a way to back into that by using currently utility costs per killowatt hour and therm?
    Also, thank you both, as your comments overlap in a helpful way; meaning, I should decide whether or not I am going heatpump (all electricity) or NG heat plus condenser-based AC.
  • DCContrarian
    @Toasted : "First, I am running steam on NG, so not sure whether or not a heat pump is going to be cheaper as I am undergoing insulating and sealing the home. Is there a way to back into that by using currently utility costs per killowatt hour and therm?"
    To do an apples-to-apples comparison you take the unit cost of the fuel and multiply it by the efficiency of your heating device. What's tricky is that gas and electricity are sold in different units, gas is typically sold in therms which is 100,000 BTU. Electricity is sold in kWh which is 3412 BTU.
    The efficiency of a gas burner is going to be somewhere between 60% and 95%. It should have a label on it with input and output BTU/hr, that's the efficiency. Efficiency of a heat pump varies with temperature, it's typically around 100% in sub-zero weather and 500% or more in the 50's. Efficiency for heat pumps is expressed as coefficient of performance, or COP, which is the percent efficiency turned into a real number; i.e. 3.1 COP means 310% efficiency.
    The way I like to do it is to take the cost per therm and boiler efficiency, along with the cost of electricity, and calculate what the COP would have to be for both sources to cost the same, this is the break-even COP. Then look at the performance stats for the heat pump and figure out what temperature corresponds to that COP, that's the break-even temperature. Then look at historical weather data for the area to see how much time is spent above and below the break-even temperature.
  • Hot_water_fan
    A heat pump costs essentially the same as AC. I see no compelling reason to lock yourself into only 1 fuel. Prices change.
  • Bernie_the_Brewer
    Bernie_the_Brewer Member Posts: 17
    edited March 30
    Here is a calculator that performs the conversion that DCContrarian mentioned:
    https://siecje.github.io/heatpump-cost/
    Trying to keep Bernie burning!
  • Toasted
  • Toasted
    FYI all - now looking at Daikin Fit as they have what appears to be a solid duel fuel set up which utilizes all Daikin manufactured equipment.
  • TAG
    I'm in PA/NJ/SC …. Propane in the PA house because no natural gas is available — even with the high cost of electric in eastern PA the high end heat pumps are a bit cheaper to operate. I run a propane boiler to heat the domestic water and for the radiant heat for comfort in the winter. The heat pumps get used in the shoulder season when you need a little heat now and then. Turning on the floor would overheat the house at those times. This house has a properly sized Carrier Five Speed Infinity heat pump and the matching infinity gas furnace w/ properly sized three zones of ductwork. I went the extra mile and did the furnace vs just an air handler because we don't use the house full time and I wondered what would happen if it quickly got colder and we arrived and wanted it warmer in a hurry. I can't stress properly sized enough .. I paid a guy in FL to do a heat and cool load — he is a real pro and this house was rehabbed with spray foam. The heat pump properly sized ends up being too small to provide the full heat load. Just to complicate things … this is an odd property and the addition had no way to get ductwork installed … either for it as a separate system or as a stand alone. We had to use three minisplits … all single Mitsubishi. Why singles — more control and I have had nothing but problems with a three head system in another house.
    In my NJ house w/ natural gas the heat pump is never used …. I have the same Carrier 5 speed set up with zoned gas ducted furnace and there is no time the HP is cheaper to operate with our NG prices and high electric cost … the HP is multi times more costly to operate. The Carrier infinity system is fantastic and it has the best zoning add on in the business IMO.
    At my pace in SC I use a Rheem 2 speed set up and put a ceiling mini (Mitsubishi) in an upper bedroom with poor ducts for when it gets really hot … I have no gas of any kind in SC so you go with what you can.
    You having steam is an odd one because as you make the space more efficient the seam becomes oversized … now you need someone who really needs to understand if the steam can work.
    Make sure you understand these complex mini systems … IMO they have a host of issues and I have stayed away from them since I did a 3 head set up at a beach house. you must understand the sizing of them … how low they can go ( a huge problem) … they are expensive and any issue and the whole thing goes down
  • Toasted
    This is amazing and very helpful insight.
    Who is your gas/electric provider, and what is your cost per therm/kilowatt hour?
  • Toasted
    I have been doing some analysis:
    Electric: $0.25 p/kWh
    NG: $1.10 p/therm
    Based on this, it is more cost effective to go with a variable/modulating furnace and AC system than the heat pump.
    Currently leaning towards Amana given the solid warranty. I realize the quality of install and sizing via a Manual J are both the most critical. I'd welcome thoughts in support or against, with recommendations of other systems if against!
  • ILikeEmOlder
    ILikeEmOlder Member Posts: 54
    The best forced air dual-fuel setups I have seen are using inverter heat pumps in line with modulating furnaces, to meet the loads at everything from mild conditions to design temps.
    If you seal up and insulate the house well, even the smallest modulating furnaces are going to be oversized for most of the heating season.
    Gas and electric rates are similar in the Catskills, but Lord knows where they’ll be in the future. Your best insurance is to seal and insulate like a champ.
    Swinging hammers and fitting pipe…bringing the dream to life
  • DCContrarian
    At those rates I calculate your break-even COP at 6.3. That's pretty far from realistic.
  • TAG
    In PA — the electric is PECO and I'm paying around $2.20 for Propane .. my last look at the electric was around .20kw. In NJ it's PSE&G … about the same electric the last I looked. Not sure about the gas this year .. no way the heat pumps can match price per BTU
    The AMANA product has really improved and they are making nice products today … Goodman only mad very basic stuff years ago and now under the new ownership they have nicer stuff …especially with the AMANA nameplate. The warranty is as good as it gets out there.
    I went with the Carrier product because of previously using the products and they have the best zoning IMO. I also went with the 5 speed product because it fits into what I need and gets me all he rebates. Carrier uses a rotary compressor on the 5 speed and the full VS ..the same type that is in a mini split. My oldest one is now almost 10 years old — gets used for both AC and partial heat. The unit has never been touched.
    The nice thing about a fully modulation furnace is comfort (same with heat pump) — the unit matches what is needed be it heat or cooling. I also keep my units on all the time with the fan set on low — this way the units are always moving some air around … I do this even in the houses with radiant floor. That's why I love the zoning … the unit can adjust a colder spot or just make some part of the house warmer when you want.
    In the summer the Carrier 5 speed will sit on 1 or 2 most of the time … silently removing humidity. How the zoning works with constant fan … all zones are open and when a zone needs heat or cool the others close. With a VS or 5 speed … you just need to make sure that every zone can take 25% of capacity. That why oversizing is bad
  • TAG
    FYI - you have to look how the rebates are applied. In all cases for me the only way to get the max rebate was to install a heat pump. So even if you don't ever use it … that what you need. Remember — there is little difference between the two. The heat pump has a reversing value and the ability to defrost — that's about it. You want to make sure you get the proper thermostat — buy the one that goes with the unit (many times you have to). You don't want to limit the control using a generic control even if there is a way to "make it work"
    Toasted
  • Toasted
    Appreciate both your feedback. Now it's a matter of system design, specifically which manufacturer. Maybe I stick with Amana.