Radiator with no air vent?

mbowes80
mbowes80 Member Posts: 3

We have a radiator that gets somewhat warm, but not as hot as others, doing a somewhat subpar job of heating up the room. One of the steps I was going to take to try to remedy this was to replace the air vent … upon inspection, from what I can tell, both locations where an air vent might be have plugs in them.

I'm wondering if I'm missing something, or if there's any use case for a radiator to be completely without an air vent? Or is this just an obvious mistake?

I appreciate any input!

20250316_103622-EDIT.jpg

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,007

    You are missing something: the trap on the outlet from the radiator just to the right of your feet in the pictures.

    That trap is the way air — and condensate — get out of the radiator so steam can get in. The pipe going down through the floor should connect to a dry return near the overhead in the basement, and that, in turn, should go to a vent somewhere near the boiler.

    If that trap is failed closed — which happens — the radiator won't heat. It also won't heat if the pipe in the basement isn't connected to a dry return.

    So that's what you want to go after. Check first the piping in the basement, and if that looks at least plausible the odd are on the trap. Replacement innards are readily available — if you tell us what markings there are on the cover we can help find them.

    You neither need nor want a vent!

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mbowes80mattmia2IronmanEdTheHeaterMan
  • Pumpguy
    Pumpguy Member Posts: 751

    The trap on the radiator outlet tells me you have a two pipe system. Typically, the radiator vents you describe are found on one pipe systems.

    As @Jamie Hall advises, problem is most likely the trap on this radiator has failed closed.

    If you have similar traps on the outlet of your other radiators, those too should not have radiator vents.

    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
    Mad Dog_2Long Beach Edmbowes80Neild5EdTheHeaterMan
  • mbowes80
    mbowes80 Member Posts: 3

    Thank you, @Pumpguy and @Jamie Hall - I'm aware of the traps, as I've replaced cage units in them before, but I didn't realize they de-necessitate the air vents. I do see that in the basement, on the returns, there are Maid-O-Mist air valves which perhaps do this air venting.

    There are a few radiators in the system that have air vents … what are the consequences of having them there when they are not needed?

    Appreciate your insight!

  • Jamie Hall
    Jamie Hall Member Posts: 26,007

    Depends on the system. On most two pipe systems odd air vents in odd places do no harm — though they often reflect bad traps somewhere in the past. On some vapour systems, however, they can defeat some of the ways in which the system is designed to maintain very low pressure differentials which they depend on for proper opeation.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mbowes80
  • mbowes80
    mbowes80 Member Posts: 3

    As a happy ending to the story, I changed out the cage unit in the steam trap (which I had done before) and the radiator is now piping hot. Thanks for all of the insight, experts!