Cast iron radiator output tables are wrong?
jesmed1
jesmed1 Posts: 1,631
edited March 2025 in Oil Heating
I have a heat produced-vs-heat-radiated puzzle that I wonder if any pros have thoughts on.
We have 100-yr-old gravity conversion hot water heat, with original 3-column, 9-inch cast iron radiators. I've measured all the radiators and calculated their square footage in a spreadsheet, and have checked my numbers three times. Radiator total is 482 sq ft, and adding 15% for piping gives 554 sq ft total.
These radiators are supplied by a Weil McLain WGO-5 running at 1.18 gph input (1.0 gph nozzle at 140 psi), which is 165,200 BTU/hr input.
Boiler is running at 82% dry gas efficiency, minus 7% latent heat of vapor loss, so 75% overall combustion efficiency. Then the net output after combustion loss is 75% of above, or 123,900 BTU/hr. Let's call it 124,000 BTU/hr.
At steady state, when the boiler has run for over an hour and supply water has stabilized at 160 degrees, return water has stabilized at 140 degrees, so average water temp is 150.
At 150 avg water temp, the standard radiator charts say cast iron rads output 110 BTU/sq ft. So our rads (plus 15% addition for pipes) should be outputting:
554 sq ft x 110 BTU/sq ft = 60,940 BTU/hr, at steady state.
But based on boiler input and known efficiency, the boiler is outputting about 124,000 BTU/hr into the supply water, again at steady state.
This is a factor of 2 off. For steady state, the rads and pipes must be emitting the same BTU/hr being imput from the boiler. I could see being off by 20%. But I can't explain being off by 100%.
One possible explanation is that our gravity conversion pipes are so large that we have as much pipe surface area as radiator surface area, or almost 500 sq ft of pipe EDR, which I find hard to believe. If that were the case, boiler mfr's would be adding a pickup factor of 100%, not 15%.
So the only other explanation I can come up with is that the radiator tables for BTU output of cast iron rads is off by roughly a factor of 2, and that at 150 degrees avg water temp, our rads are outputting about 220 BTU/sq ft, instead of the 110 BTU/sq ft given in the tables. Is it possible the tables are conservative by a factor of 2?
BTW, I used the table in the pdf below.
«1
  • delcrossv
    delcrossv Posts: 2,204
    edited March 2025
    Like you, I doubt your pipes are kicking out 60k btu. Must be a math problem.
  • jesmed1
    edited March 2025
    I know the abbreviation EDR is commonly applied to steam boilers, but the principle is the same for hot water. You add up your radiator square footage per the tables, look up the BTU/hr from the hot water table, and calculate your predicted BTU output totals. Take a look at the pdf I linked above. It's all for hot water radiators.
    I've tripled-checked and quadruple-checked the math. If there's a 2x math error, my 40 years of working as a mechanical engineer are failing me.
  • Ironman
    Ironman Posts: 7,975
    Could you be overlooking the fact the tables are btus per hour? Meaning that your boiler would have to run for a solid hour without shutting off to confirm its output?
    Bob Boan
  • jesmed1
    edited March 2025
    I know the boiler input in BTU/hr based on known oil input rate of 1.18 gph for a 1.0 gph nozzle running at 140 psi. And I've confirmed that input flow rate indirectly by taking boiler run time data from our ecobee smart thermostats, converting the run time to hours, calculating the expected oil consumption over months, and comparing that result to known oil delivery amounts. And there's perfect correlation to within 3% accuracy. So there's no doubt the boiler input rate is 1.18 gph, or about 165,000 BTU/hr.
    I also know our dry gas efficiency (82%) and latent heat of vapor loss (about 7%, standard for oil), so total combustion efficiency is 75%. Then when the boiler is running at steady state, there is some jacket loss, but a few percent at most. So the boiler is still outputting pretty close to 75% of input as hot water. There may be a few percents off, but not a factor of 2 off. So even if I assumed 70%, or even 65%, efficiency at that point, there would still be almost a factor of 2 missing somewhere.
    I've even confirmed the net output by known delta T across the boiler (20 deg), flow rate from the Taco 007 curve and our estimated head loss to get an estimated gpm (12 gpm), and when you plug those numbers into the delta T equation, you get 12 gpm x 20F x 8.3 lb/gal x 60 min/hr = 120,000 BTU/hr, which is almost exactly what I calculated the boiler net output to be based on known input and efficiency.
    Which is twice the BTU/hr output of my cast iron radiators based on what the tables say.
    edited March 2025
    The relevant question up there is what fraction of an hour does your boiler run? And I don't find the answer to that… the radiation does not cool off instantly when the boiler shuts off — it it ever does — so if, for example, we have radiation putting out 60,000 BTUh for an hour, and the boiler feeding them hot water at a rate of 120,000 BTUh, but only for 30 minutes…
  • ChrisJ
    ChrisJ Posts: 17,763
    edited March 2025
    I always interpreted the spec on radiators to be what they can do continuously. If they start at room temp and you dump energy into them for 15-30 minutes and then stop and let them cool off that's not the same at all.
    You're adding a lot just bringing their mass up to temp. That part isn't in the spec.
  • jesmed1
    edited March 2025
    Sorry, I didn't explain this very well.
    I'm talking about the thermal "steady state" that the boiler reaches after long (1+ hours) runs, when the water temperature has stopped climbing. At this point, the supply water temp stabilizes at 160 F, and the return stabilizes at 140 F. This represents the "balance point" at which the radiators and pipes are emitting BTU's at exactly the same rate as the boiler is outputting BTU's into the water. At that steady state, the boiler could run all day, and the supply water would remain at 160, and the return would remain at 140. I've stood at the boiler and monitored those temps at steady state, and they don't change no matter how long the boiler runs after the supply water hits 160. So the boiler cannot heat the supply water above 160, because at that supply temp, the radiators and pipes are emitting BTU's as fast as the boiler can output them.
    So I know that, at that average water temp, the emitters are outputting exactly as many BTU's as the boiler is dumping into the water. The boiler is dumping about 120,000 BTU's/hr into the water, based on known BTU input rate and known steady-state combustion efficiency. And as I mentioned, I've confirmed that BTU output rate by knowing the delta T across the boiler and the estimated gpm based on the 007 pump curve. So I'm quite confident the boiler is outputting about 120,000 BTU/hr, steady state, into the water stream.
    So, at that steady-state condition, when the average water temp is now 150, and not changing, the rads and pipes must be emitting those same 120,000 BTU's/hr at that average 150 water temp. But the cast iron radiator tables say the rads should be emitting only about 60,000 BTU's/hr at that average water temp. That is a factor of 2 missing somewhere.
    A BTU is a measure of energy so to make it a measure of power you have to add time to it. It is just changing it from a quantity to a rate of change of quantity.
  • Grallert
    Grallert Posts: 1,237
    jesmed1delcrossv
    The ambient air temp will change the output but since it is linear and we are talking maybe a dozen degrees in about 500 the effect is small. Something that can cause a stack effect to pull air over a radiator will change the output significantly.
    It is very possible that your assuming the average is the mid point between the supply and return temp is very wrong.
  • jesmed1
    So my suspicion here is that the cast iron radiator tables significantly understate the BTU/sq ft emission rate for a given average water temp, because they know homeowners are going to put enclosures over them, dry their laundry on them, or whatever.
    If that's the case, then it appears they've sandbagged the numbers quite significantly. In my case, my un-enclosed radiators appears to be emitting around 220 BTU/hr/sq ft at 150 degrees avg water temp, which is almost exactly twice the 110 BTU/hr/sq ft published number.
    I'm not completely convinced that the standardized radiator types are as standardized as has been claimed either.
  • jesmed1
    edited March 2025
    Ah, interesting that you mentioned this. So let's assume the impossible "best case," in which all the radiators have 160 degree water, the same temperature I'm measuring coming right out of the boiler.
    In that case, the tables say the rads should be emitting 130 BTU/hr/sq ft, which works out to about 72,000 BTU/hr for both the rads and a 15% pipe factor. That is still 52,000 BTU/hr short of the 124,000 BTU/hr the boiler is putting into the supply water. So now it's not a factor of 2 wrong, it's "only" a factor of 1.7 wrong, or still 70% too low.
    I suspect we're in the same territory as the magical 33% steam pickup factor, where the steam boiler mfrs derate their steam boilers by 33% to account for unknown installation conditions. But in this case, it looks like the cast iron radiator table people have "derated" the cast iron radiator BTU tables by 50% or so, perhaps for similar reasons (people putting enclosures over rads, etc).
    pecmsg Posts: 7,634
    somehow I’d trust the #’s from 100+ years ago as apposed to todays rocket scientists?
    jesmed1EdTheHeaterManSteamheadPerryHolzman
  • jesmed1
    edited March 2025
    I'm always willing to be proven wrong, but someone once said "numbers don't lie." Those 124,000 BTU's/hr are going somewhere…if you have a better theory where they're going, I'm all ears. 😉
    pecmsg Posts: 7,634
    edited March 2025
    Do HW Radiators get measured by EDR or BTU’s @ X*F ?
    If measuring steam temperatures then that radiator has 212-220* steam.
    If HW then 180 or less.
  • jesmed1
    That could well be. But for my case, I measured the triangular faces of my radiator columns and calculated the resulting surface area, and it came surprisingly close to the published area numbers. So while those might vary depending on radiator config, I'd guess the published numbers are within 10% of my actual radiator areas. Which still leaves the BTU/hr/sq ft published numbers as the most suspect.
  • jesmed1
    edited March 2025
    Yes, I probably shouldn't have used the "EDR" in my first post. I'm getting brainwashed by all the steam people. 😃 I've edited that post to remove the incorrect EDR reference.
    I should have just said "square feet." So my radiator square footage total is 482 square feet, and then I added a 15% piping factor of 72 feet to get a total of 554 square feet of radiation including pipes.
    Then it's just a matter of looking at the hot water radiator tables, and finding the BTU/hr/sq ft for a given average water temp. In my case the tables say 110 BTU/hr/sq ft for 150 deg avg water temp.
    So 554 x 110 = 60,940 BTU/hr being emitted according to the tables, which I'm saying appears to be low by a factor of 2.
    EdTheHeaterMan Posts: 12,951
    Does the burner ever reach the limit and shut off while the thermostat is calling for heat. The Ecobee run time is for the circulator pump run time, it may not be for the burner run time if the burner cycles at 160° off of the high limit.
    First off — EDR is, correctly interpreted, as equivalent direct radiation (hence EDR) in square feet. You can either actually measure the square feet in some manner — or you can assume that the manufacturer or rating agency did that for you. Take your pick. It really doesn't matter (for once…).
    Second, the relationship between EDR and power output is more or less linear, as has been noted. You can use the tables, as was done above, or you can figure it closely enough — it's about 1.7 times the difference between the radiator surface temperature and the ambient air temperature, in BTUh/sq.ft. If the surface temperature of the radiator is steady at 160 F, which it will be after a long run, and that is the temperature of the whole raidator, it should be dissipating around 160 BTUh.
    Which, for the above discussion, would work out to around 80,000 BTUh total power output.
    Now the gross power input to the boiler is stated to be around 162,000 BTUh. The net output, then, should be around 120,000 BTUh. If the burner is firing constantly, that implies a missing 40,000 BTUh somewhere. If we throw in the piping power output, which may be considerable, that could easily account for half of that.
    Now I'm not about to doubt the OP's numbers here. I am sure that he has very accurate thermometers for the actual circulating water temperature and that he has very accurate measurements for the actual EDR of the radiators.
    But perhaps before the manufacturer's data, validated over the last century and a half or so of practice, gets thrown under the bus, more research on all inputs and losses might be prudent.
  • jesmed1
    Thanks Ed, we never hit high limit, because the combination of cold start, high water volume, and massive radiation means even these 3x oversized boilers can't ever hit the high limit. They max out at 160!
    And they only ever get to 160 during morning recovery from a 3 degree setback, when they run about 80 minutes. Before I programmed in the setback, they only ran maybe 45-50 minutes max, with even lower max temps.
    @jesmed1 Said: "Thanks Ed, we never hit high limit"
    I thought you said that somewhere before, but I wanted to double check, because burner run time is often different than thermostat run time, especially on over sized equipment like yours.
    So If your equipment is so oversized, then how does it not shut off by the limit? I know that you have a large water volume system, I just don't understand how that oversized boiler does not go above 160° on those long calls for heat in the morning. Baffles the mind 🤯
  • DCContrarian
    DCContrarian Posts: 1,588
    @jesmed1 : "And I've confirmed that input flow rate indirectly by taking boiler run time data from our ecobee smart thermostats, converting the run time to hours, calculating the expected oil consumption over months, and comparing that result to known oil delivery amounts. And there's perfect correlation to within 3% accuracy. So there's no doubt the boiler input rate is 1.18 gph, or about 165,000 BTU/hr."
    I wouldn't expect the boiler run time to be the same as the burner run time. Especially since the output capacity of the radiators is far less than the output of the burner, I'd expect the burner to be cycling on and off even when the thermostat is calling continuously.
    If the radiator capacity was greater than the burner output, then I'd expect the burner run time to be close to the thermostat on time, the only time the burner shuts off is when the circulator shuts down.
    I don't have any answers, just pointing that out.
  • jesmed1
    @Jamie Hall said:
    " If the surface temperature of the radiator is steady at 160 F, which it will be after a long run, and that is the temperature of the whole raidator, it should be dissipating around 160 BTUh."
    Thank you, Jamie. I can measure a radiator surface temp tomorrow morning at steady state. I'm guessing I'll find average surface temps around maybe 140, as there will naturally be a gradient across the cast iron from the average 150 or so water temps inside. If that is the case, then using your 1.7 multiplier gives about 120 BTU/hr, assuming a room temp of 70. So that does get us a bit higher.
    Then 120 x 482 (radiator area only) = 57,840 BTU/hr
    And we have about 200 linear feet of pipe, averaging maybe 2" diameter, which would lose 104 BTU/hr/lin ft at 150 avg temp, so say the pipe loss is 104 x 200 = 20,800 BTU/hr.
    That puts us up to 57,840 + 20,800 = 78,640 BTU/hr. So we are still around 50,000 BTU/hr short.
    @DCContrarian and I had the same idea. I wonder if he is as smart as me?🤪
    DCContrarian
    Ah. I see a potential problem. The run time is being taken from the thermostats, not the burners.
    Go measure the actual burning run time.
  • jesmed1
    And I will never know as much about heating systems as you both have in your little pinkies.
    But here's the truth.
    Even with 3x oversized boilers, we NEVER HIT THE HIGH LIMIT. EVER! So the ecobee run time is ALWAYS the actual burner run time.
    Why?
    Because:
    1. Even though the boilers are 3x oversized for heat loss, they're somewhat downfired. So they "only" have about 165MBTU input and about 124MBTU net output after combustion losses.
    2. We have big gravity conversion pipes, mostly 2-3 inch, and big old cast iron rads. I figure we have about 150 gallons of water in one boiler, one set of pipes, and one set of rads.
    3. We have a massive amount of radiation. As I've shown, the boiler outputs about 124,000 BTU/hr net into the water, and reaches steady state at 160 F supply water temp, at which point the rads and pipes are losing heat as fast as the boiler can put it out. So the boiler could run 24/7 and not be able to get above 160 supply temp.
  • jesmed1
    See answers above. I will repeat for the nth time that the boiler NEVER HITS HIGH LIMIT, EVER.
    I've literally studied these boilers for hundreds of hours (sad, I know). I've even added up all the ecobee run times for an entire year, calculated the total call for heat hours, multiplied by the expected 1.18 gph input rate based on nozzle size (1.0) and pressure (140 psi) and calculated an expected total oil usage, and it came to within 3% of our actual oil usage for the entire season, based on known tank levels before and after, and known delivery quantities.
    So I can state with absolute certainty that the BURNERS NEVER SHUT OFF during a call for heat.
    @jesmed1 Said:"So the boiler could run 24/7 and not be able to get above 160 supply temp"
    The rooms would increase in temperature it you ran the boiler 24/7. As the room temperatures increased, the boiler temperature would also increase. that is because the higher air temperature around the radiator would remove less heat compared to the water temperature. So If you allowed the room temperature to get as high as 90° then your average radiator temperature may increase to 170° with a supply water temperature of 180°
    So don't do that, you will use too much oil on this experiment and the other condo owner might not like you anymore when their decorative candles start to melt.
    jesmed1
  • jesmed1
    But don't let the high limit thing distract you. It's not relevant.
    What matters is that, in the morning when the boiler has run continuously for over an hour and the supply temp has finally crept up to 160, I can stand there with an IR thermometer on black tape on the supply line, with the boiler firing continuously, as I can hear and see through the inspection port.
    So while the boiler is still firing continuously and the supply temp finally pegs out at 160 after 1+ hours running, I can guarantee you that:
    1. The boiler is still running, has been running, and could continue running until next Sunday without ever hitting the high limit. Or until the air temp gets so hot that the rads can't reject the heat fast enough, and we have a China Syndrome. 😅
    2. The supply temp gets to 160, and does NOT climb any higher. The boiler is cranking out those 124,000 BTU/hr, but the pipes and rads are rejecting them just ast fast. So that's the actual "high limit."
  • jesmed1
    edited March 2025
    LOL, yes, I just admitted as much in my China Syndrome post before I saw yours…
    But the larger point is, that within reason, 160 degrees is the max the boiler can output, and at that point, the radiation catches up with it and drains the BTU's as fast as the boiler can make them.
    That's why this is a useful "steady state" point for analysis, because I know the system is in thermal equilibrium, with the emitter losing BTU's exactly as fast as the boiler is outputting them into the water stream, and as I stand there in front of the boiler, I know the burner is running continuously.
    edited March 2025
    @jesmed1, I just have one more question, I want to be absolutely sure that the thermostat clock and the burner run time is identical. are you absolutely sure that THE BURNER
    NEVER REACHES THE HIGH LIMIT?
    I don't think I can ask that any louder
    LOL!!!!!
    I hope this post really gets your goat!!!
  • jesmed1
    @EdTheHeaterMan I'll never know as much about heating as you do, and I'll definitely never be able to shout as loud. 😂
    EdTheHeaterManPC7060
    Are your efficiency calculations under these conditions? As the return water gets warmer more heat goes up the vent.
  • jesmed1
    edited March 2025
    Excellent question. For a rise of, say, 100 degrees in stack temp, we lose about 2.5% dry gas efficiency according to the combustion efficiency charts, so let's call it 3% more dry gas loss, assuming our gross stack temp goes from 400 to 500. And maybe our latent heat of vapor loss goes up too, so let's say 5% loss in total combustion efficiency. That knocks us down from 75% to 70%, so instead of about 124,000 BTU net, we're down to 115,000 BTU net out. That's entirely possible.
    But it's still nowhere near the 40,000 or so BTU's we're still "missing…"
    hot_rod Posts: 28,708
    The heat emitters are dictiting the operating condition of the boiler. So at 160 thermal equilibrium
    point the radiators are outputting the boilers maximum. Now that could be your piping is as much radiator output as the radiators themself.
    Idronics 15 talks about equilibrium and how to predict it.
    jesmed1
  • jesmed1
    edited March 2025
    @hot_rod Thanks for that. Interesting that the text in your final screen shot talks about the mismatch between "legacy" (pre-1980) systems that were designed for high water temps, so aren't a good match for mod-cons.
    Ironically, our even older "legacy" system here (circa 1930) would be ideal for a mod-con, because we have so much radiation that we could probably heat the entire building with sub-120 degree water.
    What's old becomes new again if you wait long enough. 😊
    PC7060
  • DCContrarian
    "I figure we have about 150 gallons of water in one boiler, one set of pipes, and one set of rads."
    "And they only ever get to 160 during morning recovery from a 3 degree setback, when they run about 80 minutes."
    OK, here's a theory:
    Let's say the water in the system cools to 65F during the setback. Heating 150 gallons from 65F to 160F takes 118,275 BTU, plus whatever the heat capacity of the radiators themselves is. So it takes the full capacity of the burner for almost an hour just to heat that water. Let's say the radiators really do put out 60K BTU/hr, but the heating load is actually somewhat less than that. So the heat runs for, say, 90 minutes until the radiators get hot enough to put out some heat and the house warms up to the set point. At that point the thermostat is satisfied and it shuts off the boiler.
    But you've got 150 gallons of 160-degree water, plus the radiators themselves, sitting inside the house. They're going to keep putting out heat. If the heating load is fairly low, it could be several hours before the house cools off enough to trigger the thermostat. By then, the water has cooled off, and the cycle repeats.
    This would explain why the burner never cycles, by the time the water gets warm enough for the burner to turn off the house has warmed enough for the thermostat to shut off.
    This article gives a technique for estimating your heating load based on fuel usage:
    https://www.greenbuildingadvisor.com/article/replacing-a-furnace-or-boiler
    It would be helpful to get an idea of the heating load and how it compares to the amount of radiation.
    hot_rod