Seeking your thoughts regarding a boiler/system upgrade for a small 1980s ranch.
Hugh Mason
Hugh Mason Member Posts: 41
I'm considering putting a purchase offer in on a 900sf mid-80s ranch that's heated with a boiler of similar vintage in what appears to operate a single loop with the whole house including the basement are controlled via a single thermostat in the living room . The basement is unfinished so there's excellent access to piping. The old boiler and close in piping looks pretty sketchy with one section of pipe having 3 valves in a row with two being redundant or more likely seized up. I suspect that 2 or 3 zones might add to comfort and would even consider a condensing boiler and perhaps larger/lower temp emitters if that would add to comfort.
So what do you think? Just throw in another 80% cast iron unit of appropriate output and refresh bits that need it? I'm in my early 70s so this is in all likelihood the last house I'll live in.
Thanks so much for your well earned advice.
Hugh
    Jamie Hall Member Posts: 27,359
    If it ain't broke, don't fix it.
    Does the present system work? Will your building inspector for the sale test it? He or she should…
    If it does need a new boiler, get it sized correctly to the load. I wouldn't spend the extra to save the 5 percent or so on what a mod/con might give you.
    Alan (California Radiant) Forbesmattmia2Mad Dog_2
  • jesmed1
    jesmed1 Member Posts: 1,474
    edited March 2025
    I am not a heating pro, just a homeowner/engineer. The very knowledgeable heating pros here will give you good advice. Meanwhile, a few questions and thoughts.
    One important factor is going to be your type of radiation. You say mid-80's construction, so I'm assuming baseboard radiators? How many linear feet? And where in the country are you, as your local climate will affect how much heat you need.
    We have two cast iron boilers in our 100-year-old 4-unit building with cast iron radiators in the Boston area, and the cast iron boilers work well with high-water-volume, high flow rate systems with big old pipes and cast iron radiators. But they can be problematic on systems with smaller water volumes and lower flow rates through smaller diameter pipes and baseboards. Especially if you split one relatively small zone (900 sq ft) into even smaller zones. The boiler heats the relatively small volume/low flow rate of water very quickly, then short-cycles on the high limit, resulting in inefficient operation.
    With 900 square feet, you're unlikely to need more than, say 30,000 BTU/hr depending on where you are and how much insulation/air sealing you have. That already puts you in the very low end of cast iron natural gas boilers. And if you are going to split zones, you may want to reduce the output even further. So I'm guessing the heating pros may recommend a modulating condensing boiler that can reduce output further for smaller zones.
    But meanwhile, if you can answer the questions about your radiation type, linear footage, and your location, that will help them give you better answers.
    Mad Dog_2
  • Hugh Mason
    Thanks for the detailed reply. The house is in climate zone 5A. It's a modular with 2X4 walls and decent looking insulation in the attic. It has all new windows and doors. I can measure the lineal footage of baseboard this Tuesday when a get a chance at a second inspection. The purchase offer is due on Wednesday so I'm working to line all my ducks up. The basement walls are uninsulated but I plan to rectify that if I go ahead with the purchase.
  • jesmed1
    I think the short answer is that the house is so small and the pipes easily accessible, so any problems with the system as is now shouldn't be hard to rectify.
    Once you get in there and assess how the existing system is working, then you can make better informed decisions about where to go from here.
    EBEBRATT-Ed Member Posts: 20,165
    I had a 1000 sq ft ranch that was like a seive and 50,000 btu with 90 feet of baseboard it what it needed. Yours is certainly better insulated and better windows so 40,000 is probably a decent guess.
    That being said there is no need to install a larger boiler than the radiation will need.
    If it was me, I would use a standard CI boiler and either keep your water tank or install an indirect off the boiler.
    If you have an outside chimney which I suspect you probably need a stainless steel liner. A good chimney sweep can do this. You might call one and get a #.
    Look up the cost of a new 40,000-50,000 btu CI boiler on line and multiply the cost x4 and you will be in the ballpark.
    Peerless or Weil McLain are good choices. Supply House.com has the #s
    The biggest obstacle is a good contractor, unfortunately many of them suck.
    When your ready post your location or check "find a contractor" on this site. We may know someone who can help.
    LRCCBJ
  • Hugh Mason
    Perhaps I'm interpreting this wrong when you mentioned "Look up the cost of a new 40,000-50,000 btu CI boiler on line and multiply the cost x4 and you will be in the ballpark." Should I take that to mean to install a new cast Iron boiler ought to cost 4 times the cost of the boiler alone? It's not quite a plug and play operation but jeepers that seems spendy. It appears that many of the better regarded CI boilers are about as expensive as a small Lockinvar mod-con that would purr through the shoulder seasons with a good deal of efficiency.
    hot_rod
    pecmsg Member Posts: 7,053
    I wouldn’t use the home inspector for evaluating the boiler. Have your tech look at it.
    yes 3 or 4 time the onLine cost for install.
    Get into the trade and see what has to be done!
    hot_rod Member Posts: 27,446
    You are wise to consider a mod con. The modulation alone is worth any small price increase. And as you noticed CI boilers are not always less $$.
    The more you can condense it the better the efficiency. If you plan on zoning it makes even better sense to have a mod boiler.
    In my area labor rates can run from 50- 300 bucks an hour, so that is a big part of the cost.
    We did this issue to help people make decisions for low temperature operation and conversions.
    https://idronics.caleffi.com/sites/default/files/magazine/file/Idronics_i35_0125-compress.pdf
  • Hugh Mason
    Thanks for the link Bob,
    Zoning the system seems like it could potentially increase the comfort of the place but then again I've not lived in it yet. With some luck I'll get to spend a bit of chilly spring in the place to get a feel for how it currently heats.
  • Hot_water_fan
    Hot_water_fan Member Posts: 2,241
    I’d consider this the 50th highest priority thing for a new house. Get it inspected and then don’t think about it.
  • Hugh Mason
    Yes, but I've already looked at the 49 that rank above this;)
    HVACNUTHot_water_fanjesmed1
  • jesmed1
    Most home buyers never make it past number 3. 😅
  • LRCCBJ
    LRCCBJ Member Posts: 1,043
    edited March 2025
    The only way it increases the comfort is if the installed radiation is wildly in error as compared to the heatloss of the individual space. This is highly unlikely.
    I'll tell you a story of one of my houses where, at a younger age, I decided to separate the single thermostat and zone on the first floor in a 100 year old Dutch Colonial (1900 square feet) into NINE Zones. It was not as difficult as it sounds as all the rooms had the 3/4" piping extend directly to the basement so putting nine zone valves down there together with 1" copper for the mains was not a massive effort. All the asbestos clad 2" iron came out and the 1" copper was installed over the course of about two years when I had the time. Did one half the building at a time.
    The interesting thing about this story is that NONE of the zones on a given floor could be controlled greater than about 6°F. The energy from the highest zone would migrate over to the lower zones to the point where the lower zones would never call. The only way to increase the 6°F was to keep all the doors closed at all times………..which is possible in a 100 year old Dutch Colonial (because they all had doors)……………likely impossible in newer more open buildings.
    I will say that the project eliminated the excessive overtemperature on the second floor. This was clearly a benefit because the house only had one zone previously.
    So, your thoughts about increasing comfort with zoning is an exercise in futility on a building with one floor with a reasonably high expense if a contractor has to do it.
    If you have a room that you wish to reduce the output, just close the damper on the baseboard…………….or put some wood beneath the baseboard to reduce airflow through it………………costs you NOTHING.
    Regarding a new boiler:
    You are wise to consider NOTHING. If the boiler is not leaking water……………do NOT replace it. It may be fine for another 20 years.
    I bought a rental house in 1986 with a Utica OBT. The boiler had to be at least 20 years old at that point. I sold that house last year and the OBT was still operating perfectly fine………….together with it's tankless coil which I NEVER replaced in 38 years. It has a 275 outdoor tank running 2 pipe with a top feed with insulated lines to and from the tank into the building. I did replace the tank once…………with another used tank. When I sold it, I promised the new owner a new Honeywell 7224 control (since the L8124 was 30 years old). Put that in for him in about one hour.
    jesmed1delcrossv
    I would definitely zone the basement if you finish that.
    If you use panel radiators you can easily add TRVs for some temperature control, room by room
    If you only have 900 square feet of house I would only zone the basement and the house 2 zones.
    Money wasted on extra zone valve, pumps etc will be a waste with a small house
    Yes 3-4x the boiler cost. You probably have to :
    Reline the chimney
    Permits
    wiring
    start up and test
    remove old boiler
    install new
    material
    labor
    sales tax
    Flush and fill
    Truck
    Truck Insurance
    Liability Insurance
    Licenses
    etc etc etc
  • Hugh Mason
    edited March 2025
    I'm just back from a second look at the house. There are ~ 51' of upstairs emitter length and 27' downstairs if I found all the baseboards. The boiler is a 75,000 BTU input Utica that was install about 35 years ago. There's a surprising amount of corrosion on most of the valves considering how dry the basement seems to be and always has been. The boiler blipped on for a very short bit while we were there and I can't imagine it ever running hard. I'm especially impressed with the drip catching can that's rusted out;)
    Utica boiler placard.jpg Bottom of boiler.jpg Boiler pump.jpg Boiler drip can.jpg Boiler valves.jpg
    HVACNUT Member Posts: 7,436
    You could stay simple with an upgrade of what you have now. Something like the Weil McLain CGa-25.
    38K net BTU. Still more than you need but you won't find much smaller with an atmospheric gas boiler. I'm not partial to WM. Just an example. The 21st century version of your boiler gets a vent damper, Rollout and Spill switches for safety, and spark ignition. Not a lot to go wrong. Definitely cut all piping high and repipe. It looks like a split return at the boiler. Where does the supply split?
  • Hugh Mason
    "Where does the supply split? " In my haste I really didn't look over the pipe routing but would expect it splits between the up and downstairs. Thanks for the advice.
    mattmia2 Member Posts: 16,746
    It would have been less work to fix that packing than to rig up that soup can.
  • Hugh Mason
    Yes but that might have stifled the owner's creativity;)
    neilc
    With your baseboard footage of 78 feet the baseboard will output about 550BTU/ foot of baseboard so you need a boiler out put of around 50,000btu including the piping and pick up factor of 15%.
    Your old boiler is oversized. But not by a huge amount. This was common back in the day as smaller boiler were not as readily available.
    Boilers that output around 50k are more available.
    A heat loss would be more accurate but will probably not change the boiler size
  • Hugh Mason
    Thanks Ed. I understand your point that 78 feet of baseboard "could" output 50,000BTUs but feel like that in no way means that it needs to do so. Right now the basement is completely uninsulated and that would change drastically in short order. There were new windows installed since manufacture and the house appears to be quite tight. I'm told that the average utility bill has been $65/month for gas and electric but haven't seen that broken down by therms and kilowatts. If one direct vented a mod-con there would be no need to line the chimney.
    Its nice to have the extra emitters, but sizing to the baseboard will give 55.5 BTU per sq ft. It does make for good condensing on a mod con.
  • delcrossv
    delcrossv Member Posts: 2,203
    edited March 2025
    I'd be more concerned with the frozen valves and leaky air scoop than the boiler.
    If you're only paying $65/mo for both gas and electric, a mod con's additional cost and maintenance will probably never be a break even for you.
    What's you're aquastat set at? 180?
    Hugh MasonHVACNUT
  • Hugh Mason
    edited March 2025
    I agree that the frozen valves and leaky air scoop are troubling and will deal with them. My purchase offer will be considered at 2:00 today and then the real fun may begin. I've never actually seen the utility bills and am relying on the sells word on this. My realtor wasn't helpful in getting actual data. I failed to check what the aquastat is set to.
    If the boiler itself isn't leaking just clean it and fix the leaking piping, no reason to replace it until it leaks.
    delcrossv
    Actually the price of mod cons is in many cases less than a cast boiler. This Nobel is a larger BTU output and has many, many more control functions that the cast. It modulates and can run into the 90% efficiency, something the cast cannot accomplish
    The pricing issue is not much of an argument.
    ore comparing cast to high efficiency mod cons.
    Hugh Mason
  • Hugh Mason
    edited March 2025
    Thanks Bob! Do you prefer the Noble over the Knight?
    There's also an $850 tax credit/utility credit that goes with upgrading to high efficiency boiler which takes a bit of sting out of the upgrade.
    The Knight has a bit larger, nicer HX, and a handful of additional control features.
    The Nobel does have a nice outdoor reset function and the SH space heating limit function, so you can lock that 110 down to 11,000 btu/hr as I recall. That is really all you need for a basic residential system.
    I have the Knight 55,000 and it goes down to 8,000 btu/hr.
    This is the Nobel control menu.
    Hugh Mason
  • fwmech
    fwmech Member Posts: 15
    Hi Bob,
    I'm new to the condensing boiler scene. I found this thread while searching for info on replacing a conventional boiler with a condensing boiler while keeping the high temp baseboard emitters.
    Am I understanding your last post that to make this work, you set the boiler to limit it's BTU output, and I assume run a higher gpm circulator, to keep the boiler condensing and the baseboards putting out a lower more even temperature?
    I'd love to learn more so I can start saving my customers money. Thanks for any help or point me in the right direction.
    Correct, only a small fraction of heating season should you need full BTU output, or highest temperature.
    So with a mod con you can limit BTU output, run as low as temperature as possible and enable outdoor reset. ODR increases efficiency.
    If the system is zoned, the modulation is a big feature.
    Mad Dog_2GGross
  • fwmech
    Thank you, Bob that really helps. I have two jobs coming up, one is a mod con combi to baseboards on four zones and the other is a mod con with an indirect water heater to baseboards on two zones.
    I think I'll keep it simple and pipe them according to Lochinvar's manuals and the results from a heat loss calculation for desired BTU rating and pump gpm.
    I really appreciate your help!
    Mark
  • TheUpNorthState88
    TheUpNorthState88 Member Posts: 114
    Have the boiler serviced and see how it operates this coming heating season. Unless the boiler is experiencing issues, I would leave well enough alone. Full disclosure, I am not a heating professional, just a homeowner with a knack for these topics. My boiler is 88 years old. So I am not the poster child for replacing things simply for being “old.”
    Lifelong Michigander
    -Willie
    efficiency snd comfort go up with a mod con, properly installed and adjusted
    The ODR allows longer, in dome case continuous circulation. So less in/ off cycling and the heat output matching the heat loss near perfectly. Use all the cintrol features!
    Add to that the fact it will condense some of the season for 90% plus operation
    None of that is possible with a non condensing boiler. It is only correctly sized for design conditions, less than 10% of the heating season, typically