Single pipe radiator
Howdy, Iโve got an old Moline two pipe system that has a retrofit single pipe radiator added on at some point. Once I got my system running correctly (Thanks to Danโs book!) the retrofit single pipe rad water hammers horribly and has been valved off ever since. It has a new working vent, etc.
Is there anyway to get this rad working on this system? Bigger vent?
Thanks
Bill
Comments
-
You have to consider how the condensate is being handled from the single pipe radiator. Usually a water loop or a trap could be used. You can't just dump the condensate back in the steam line as it is properly not sized for that.
Send a diagram of how this radiator was added. Andโฆ at what pressure is the boiler operating?
2 -
Iโll work on a diagram. As far as pressure goes. I have a large 0-15psi gauge on the header. It never registers pressure. The other radiators heat up quite fast, no complaints there.
0 -
What @Long Beach Ed said. Also check the pitch of all the piping from the main to the radiator.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
supply line (obviously)
0 -
radiator
0 -
from the tee it runs about 7 linear feet and only about 12inches vertical.
Unfortunately the supply is at best level for those 7 feet from the tee.
0 -
Need some pitch. The takeoff from the end of the main pretty much guarantees water in the lateral.
Is that main counterflow? If not, it needs to go to a drip or crossover trap- not a supply line.
If you're feeling frisky, repipe it as 2 pipe like the rest of the system. ๐
Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.2 -
@delcrossv, I was hoping there was some long lost ancient steam secret that would unlock my hopes.๐
1 -
-
-
-
-
bodge[bรคj]verb
- make or repair (something) badly or clumsily:"they were left in a half-finished house renovation when the company bodged improvement works" ยท "the door was bodged together from old planks"
Had to look this term up, but "unbodge" is clearly on point and should be part of the lexicon
Regards,
RTW
2
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 123 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements