Single pipe radiator
Howdy, I’ve got an old Moline two pipe system that has a retrofit single pipe radiator added on at some point. Once I got my system running correctly (Thanks to Dan’s book!) the retrofit single pipe rad water hammers horribly and has been valved off ever since. It has a new working vent, etc.
Is there anyway to get this rad working on this system? Bigger vent?
Thanks
Bill
Comments
-
You have to consider how the condensate is being handled from the single pipe radiator. Usually a water loop or a trap could be used. You can't just dump the condensate back in the steam line as it is properly not sized for that.
Send a diagram of how this radiator was added. And… at what pressure is the boiler operating?
2 -
I’ll work on a diagram. As far as pressure goes. I have a large 0-15psi gauge on the header. It never registers pressure. The other radiators heat up quite fast, no complaints there.
0 -
What @Long Beach Ed said. Also check the pitch of all the piping from the main to the radiator.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2